event handler
Re: event handler
yes I have 2 contacts for the event handler, one is vassiliy-phone and another one vassiliy-backup-phone
Can it be an issue?
but they have different time periods, the second one is used in escalation file
Give me a sec And I'll send you logs
Can it be an issue?
Re: event handler
Great. Ummm, when does the escalation take priority? Escalations will suppress the standard notifications, could you post the escalation config as well?
Re: event handler
this is from /var/log/nagios/nagios.log
started from daemonizing
debug_level in nagios.cfg 32 OR 64 OR 2048 , if you need more let me know
I got email at HARD state but still no calls
[1398199867] Finished daemonizing... (New PID=40744)
[1398199897] HOST ALERT: test-condor-site;DOWN;SOFT;1;PING CRITICAL - Packet loss = 100%
[1398199897] GLOBAL HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;1;asteriks-host-phone-call
[1398199897] HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;1;asteriks-host-phone-call
[1398199897] SERVICE ALERT: test-condor-site;check-host-alive-or-not;CRITICAL;HARD;1;PING CRITICAL - Packet loss = 100%
[1398199967] HOST ALERT: test-condor-site;DOWN;SOFT;2;PING CRITICAL - Packet loss = 100%
[1398199967] GLOBAL HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;2;asteriks-host-phone-call
[1398199967] HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;2;asteriks-host-phone-call
[root@callme-dor-billing objects]# tail -f /var/log/nagios/nagios.log
[1398199867] Local time is Tue Apr 22 16:51:07 CLT 2014
[1398199867] LOG VERSION: 2.0
[1398200047] HOST ALERT: test-condor-site;DOWN;SOFT;3;PING CRITICAL - Packet loss = 100%
[1398200047] GLOBAL HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;3;asteriks-host-phone-call
[1398200047] HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;3;asteriks-host-phone-call
[1398200117] HOST ALERT: test-condor-site;DOWN;HARD;4;PING CRITICAL - Packet loss = 100%
[1398200117] HOST NOTIFICATION: vassiliy;test-condor-site;DOWN;notify-host-by-email;PING CRITICAL - Packet loss = 100%
[1398200118] HOST NOTIFICATION: vassiliy-phone;test-condor-site;DOWN;asteriks-host-phone-call;PING CRITICAL - Packet loss = 100%
[1398200118] GLOBAL HOST EVENT HANDLER: test-condor-site;DOWN;HARD;4;asteriks-host-phone-call
[1398200118] HOST EVENT HANDLER: test-condor-site;DOWN;HARD;4;asteriks-host-phone-call
Reason: code wraps save scroll wheels :)
Re: event handler
for me it looks like event handler is not called at all, but with 3 parameters it works. I completely lost
Re: event handler
I have 2 escalations file - one for emails another one for phone calls, again my boss wants to get 3 phone calls and only one email for the event, and on every escalation stage
first file hosts-escalation-phone.cfg
the second one is vi hosts-escalation.cfg
do not pay attention any other stage than the very first in escalations
thank you
define hostescalation{
host_name test-condor-site
hostgroup_name condor-site,elsalto-site,concert-site
contact_groups admins-onreserve-phone
first_notification 4
last_notification 6
notification_interval 3
escalation_period 24x7
escalation_options d
contact_groups chile-technicians, admins-onreserve-phone
first_notification 7
last_notification 9
contact_groups chile-managers,chile-technicians, admins-onreserve-phone
first_notification 10
last_notification 12
contact_groups calgary-managers,chile-managers,chile-technicians, admins-onreserve-phone
first_notification 13
last_notification 15
last_notification 4
notification_interval 0
escalation_options d,r
last_notification 7
last_notification 10
last_notification 13
}do not pay attention any other stage than the very first in escalations
thank you
Re: event handler
so the idea - the very first 3 notifications - go to admins (vassiliy, vassiliy-phone contacts)
the next 3 (from 4 to 6) - admins-oncall (vassiliy-oncall, vassiliy-backup-phone contacts )
the only difference between first group of contacts and second one - time periods
Re: event handler
It looks like you also have a global event handler enabled. Could you post your nagios.cfg in code wraps?vvz wrote:GLOBAL HOST EVENT HANDLER: test-condor-site;DOWN;SOFT;1;asteriks-host-phone-call
Lets also include a bit of debugging output in the event handler script. Add the following to the top of your script:
#!/bin/bash
echo "$1, $2, $3, $4" > /tmp/test.txtCode: Select all
cat /tmp/test.txtAll of your escalations look good as they will not take effect until the 4th notification.
Re: event handler
here it my main config
# NAGIOS.CFG - Sample Main Config File for Nagios 3.5.1
# Last Modified: 12-14-2008
# LOG FILE
# This is the main log file where service and host events are logged
# for historical purposes. This should be the first option specified
# in the config file!!!
log_file=/var/log/nagios/nagios.log
####################### COMMANDS #################################################
cfg_file=/etc/nagios/objects/commands.cfg
###################### TEMPLATES ##############################################
cfg_file=/etc/nagios/objects/templates/templates.cfg
###################### CONTACTS AND CONTACTGROUPS #################################
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-admins.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-admins-phone.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-admins-onreserve.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-admins-onreserve-phone.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-chile-managers.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-calgary-managers.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contactgroup-chile-technicians.cfg
cfg_file=/etc/nagios/objects/contacts_contactgroups/contacts.cfg
####################### TIMEPERIODS ################################################
cfg_file=/etc/nagios/objects/timeperiods/timeperiods.cfg
cfg_file=/etc/nagios/objects/timeperiods/second-quarter-timeperiod.cfg
#cfg_file=/etc/nagios/objects/timeperiods/third-quarter-timeperiod.cfg
#cfg_file=/etc/nagios/objects/timeperiods/forth-quarter-timeperiod.cfg
cfg_file=/etc/nagios/objects/timeperiods/vassiliy-onreserve-timeperiod.cfg
cfg_file=/etc/nagios/objects/timeperiods/mike-onreserve-timeperiod.cfg
#cfg_file=/etc/nagios/objects/timeperiods/vassiliy-vacations-timeperiod.cfg
#cfg_file=/etc/nagios/objects/timeperiods/mike-vacations-timeperiod.cfg
######################## CONDOR HOSTGROUP AND HOSTS ###############################
cfg_file=/etc/nagios/objects/hostgroups/hostgroup-condor-site.cfg
cfg_file=/etc/nagios/objects/hosts/smg2-condor-site.cfg
cfg_file=/etc/nagios/objects/hosts/smg1-condor-site.cfg
#cfg_file=/etc/nagios/objects/hosts/probe1-condor-site.cfg
cfg_file=/etc/nagios/objects/hosts/probe2-condor-site.cfg
cfg_file=/etc/nagios/objects/hosts/billing-condor-site.cfg
######################## CONCERT HOSTGROUP AND HOSTS ##############################
cfg_file=/etc/nagios/objects/hostgroups/hostgroup-concert-site.cfg
cfg_file=/etc/nagios/objects/hosts/billing-concert-nagios-server.cfg
cfg_file=/etc/nagios/objects/hosts/probe1-concert-site.cfg
cfg_file=/etc/nagios/objects/hosts/probe2-concert-site.cfg
######################## ELSALTO HOSTGROUP AND HOSTS #############################
cfg_file=/etc/nagios/objects/hostgroups/hostgroup-elsalto-site.cfg
cfg_file=/etc/nagios/objects/hosts/probe1-elsalto-site.cfg
cfg_file=/etc/nagios/objects/hosts/probe2-elsalto-site.cfg
####################### DEPENDENCIES ##############################################
### --- services --- ###
cfg_file=/etc/nagios/objects/dependencies/services/billing-concert-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/billing-condor-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/probe1-concert-site-dependencies.cfg
#cfg_file=/etc/nagios/objects/dependencies/services/probe1-condor-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/probe1-elsalto-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/probe2-concert-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/probe2-condor-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/probe2-elsalto-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/smg1-condor-site-dependencies.cfg
cfg_file=/etc/nagios/objects/dependencies/services/smg2-condor-site-dependencies.cfg
#cfg_file=/etc/nagios/objects/dependencies/services/test-dependencies.cfg
### --- hosts --- ####
cfg_file=/etc/nagios/objects/dependencies/hosts/billing-concert-site-hosts-dependencies.cfg
############################# ESCALATIONS ######################################
##### --- services --- ###
cfg_file=/etc/nagios/objects/escalations/services-escalation/currentload-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/dimm-condition-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/fans-condition-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/powersupply-condition-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/processors-condition-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/root-partition-usage-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/temperature-condition-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/total-processes-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/users-logged-in-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/services-escalation/zombies-service-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/hosts-escalation/hosts-escalation.cfg
cfg_file=/etc/nagios/objects/escalations/hosts-escalation/hosts-escalation-phone.cfg
########################### END OF CFG FILES #####################################
################# THIS CFG ONLY FOR TESTING ######################################
cfg_file=/etc/nagios/objects/hosts/test.cfg
# Definitions for monitoring the local (Linux) host
#cfg_file=/etc/nagios/objects/localhost.cfg
# Definitions for monitoring a Windows machine
#cfg_file=/etc/nagios/objects/windows.cfg
# Definitions for monitoring a router/switch
#cfg_file=/etc/nagios/objects/switch.cfg
# Definitions for monitoring a network printer
#cfg_file=/etc/nagios/objects/printer.cfg
# You can also tell Nagios to process all config files (with a .cfg
# extension) in a particular directory by using the cfg_dir
# directive as shown below:
#cfg_dir=/etc/nagios/servers
#cfg_dir=/etc/nagios/printers
#cfg_dir=/etc/nagios/switches
#cfg_dir=/etc/nagios/routers
cfg_dir=/etc/nagios/conf.d
#cfg_dir=/etc/nagios/objects
# OBJECT CACHE FILE
# This option determines where object definitions are cached when
# Nagios starts/restarts. The CGIs read object definitions from
# this cache file (rather than looking at the object config files
# directly) in order to prevent inconsistencies that can occur
# when the config files are modified after Nagios starts.
object_cache_file=/var/log/nagios/objects.cache
# PRE-CACHED OBJECT FILE
# This options determines the location of the precached object file.
# If you run Nagios with the -p command line option, it will preprocess
# your object configuration file(s) and write the cached config to this
# file. You can then start Nagios with the -u option to have it read
# object definitions from this precached file, rather than the standard
# object configuration files (see the cfg_file and cfg_dir options above).
# Using a precached object file can speed up the time needed to (re)start
# the Nagios process if you've got a large and/or complex configuration.
# Read the documentation section on optimizing Nagios to find our more
# about how this feature works.
precached_object_file=/var/log/nagios/objects.precache
# RESOURCE FILE
# This is an optional resource file that contains $USERx$ macro
# definitions. Multiple resource files can be specified by using
# multiple resource_file definitions. The CGIs will not attempt to
# read the contents of resource files, so information that is
# considered to be sensitive (usernames, passwords, etc) can be
# defined as macros in this file and restrictive permissions (600)
# can be placed on this file.
resource_file=/etc/nagios/private/resource.cfg
# STATUS FILE
# This is where the current status of all monitored services and
# hosts is stored. Its contents are read and processed by the CGIs.
# The contents of the status file are deleted every time Nagios
# restarts.
status_file=/var/log/nagios/status.dat
# STATUS FILE UPDATE INTERVAL
# This option determines the frequency (in seconds) that
# Nagios will periodically dump program, host, and
# service status data.
status_update_interval=10
# NAGIOS USER
# This determines the effective user that Nagios should run as.
nagios_user=nagios
# NAGIOS GROUP
# This determines the effective group that Nagios should run as.
nagios_group=nagios
# EXTERNAL COMMAND OPTION
# This option allows you to specify whether or not Nagios should check
# for external commands (in the command file defined below). By default
# Nagios will *not* check for external commands, just to be on the
# cautious side. If you want to be able to use the CGI command interface
# you will have to enable this.
# Values: 0 = disable commands, 1 = enable commands
check_external_commands=1
# EXTERNAL COMMAND CHECK INTERVAL
# This is the interval at which Nagios should check for external commands.
# This value works of the interval_length you specify later. If you leave
# that at its default value of 60 (seconds), a value of 1 here will cause
# Nagios to check for external commands every minute. If you specify a
# number followed by an "s" (i.e. 15s), this will be interpreted to mean
# actual seconds rather than a multiple of the interval_length variable.
# Note: In addition to reading the external command file at regularly
# scheduled intervals, Nagios will also check for external commands after
# event handlers are executed.
# NOTE: Setting this value to -1 causes Nagios to check the external
# command file as often as possible.
#command_check_interval=15s
command_check_interval=-1
# EXTERNAL COMMAND FILE
# This is the file that Nagios checks for external command requests.
# It is also where the command CGI will write commands that are submitted
# by users, so it must be writeable by the user that the web server
# is running as (usually 'nobody'). Permissions should be set at the
# directory level instead of on the file, as the file is deleted every
# time its contents are processed.
command_file=/var/spool/nagios/cmd/nagios.cmd
# EXTERNAL COMMAND BUFFER SLOTS
# This settings is used to tweak the number of items or "slots" that
# the Nagios daemon should allocate to the buffer that holds incoming
# external commands before they are processed. As external commands
# are processed by the daemon, they are removed from the buffer.
external_command_buffer_slots=4096
# LOCK FILE
# This is the lockfile that Nagios will use to store its PID number
# in when it is running in daemon mode.
lock_file=/var/run/nagios.pid
# TEMP FILE
# This is a temporary file that is used as scratch space when Nagios
# updates the status log, cleans the comment file, etc. This file
# is created, used, and deleted throughout the time that Nagios is
# running.
temp_file=/var/log/nagios/nagios.tmp
# TEMP PATH
# This is path where Nagios can create temp files for service and
# host check results, etc.
temp_path=/tmp
# EVENT BROKER OPTIONS
# Controls what (if any) data gets sent to the event broker.
# Values: 0 = Broker nothing
# -1 = Broker everything
# <other> = See documentation
event_broker_options=-1
# EVENT BROKER MODULE(S)
# This directive is used to specify an event broker module that should
# by loaded by Nagios at startup. Use multiple directives if you want
# to load more than one module. Arguments that should be passed to
# the module at startup are seperated from the module path by a space.
# WARNING !!! WARNING !!! WARNING !!! WARNING !!! WARNING !!! WARNING
# Do NOT overwrite modules while they are being used by Nagios or Nagios
# will crash in a fiery display of SEGFAULT glory. This is a bug/limitation
# either in dlopen(), the kernel, and/or the filesystem. And maybe Nagios...
# The correct/safe way of updating a module is by using one of these methods:
# 1. Shutdown Nagios, replace the module file, restart Nagios
# 2. Delete the original module file, move the new module file into place, restart Nagios
# Example:
# broker_module=<modulepath> [moduleargs]
#broker_module=/somewhere/module1.o
#broker_module=/somewhere/module2.o arg1 arg2=3 debug=0
# LOG ROTATION METHOD
# This is the log rotation method that Nagios should use to rotate
# the main log file. Values are as follows..
# n = None - don't rotate the log
# h = Hourly rotation (top of the hour)
# d = Daily rotation (midnight every day)
# w = Weekly rotation (midnight on Saturday evening)
# m = Monthly rotation (midnight last day of month)
log_rotation_method=d
# LOG ARCHIVE PATH
log_archive_path=/var/log/nagios/archives
# LOGGING OPTIONS
# If you want messages logged to the syslog facility, as well as the
# Nagios log file set this option to 1. If not, set it to 0.
use_syslog=1
# NOTIFICATION LOGGING OPTION
# If you don't want notifications to be logged, set this value to 0.
# If notifications should be logged, set the value to 1.
log_notifications=1
# SERVICE RETRY LOGGING OPTION
# to 0. If retries should be logged, set the value to 1.
log_service_retries=0
# HOST RETRY LOGGING OPTION
# 0. If retries should be logged, set the value to 1.
log_host_retries=1
# EVENT HANDLER LOGGING OPTION
# If you don't want host and service event handlers to be logged, set
# this value to 0. If event handlers should be logged, set the value
# to 1.
log_event_handlers=1
# INITIAL STATES LOGGING OPTION
# If you want Nagios to log all initial host and service states to
# the main log file (the first time the service or host is checked)
# you can enable this option by setting this value to 1. If you
# are not using an external application that does long term state
# statistics reporting, you do not need to enable this option. In
# this case, set the value to 0.
log_initial_states=0
# EXTERNAL COMMANDS LOGGING OPTION
# If you don't want Nagios to log external commands, set this value
# to 0. If external commands should be logged, set this value to 1.
# Note: This option does not include logging of passive service
# checks - see the option below for controlling whether or not
# passive checks are logged.
log_external_commands=1
# PASSIVE CHECKS LOGGING OPTION
# If you don't want Nagios to log passive host and service checks, set
# this value to 0. If passive checks should be logged, set
# this value to 1.
log_passive_checks=1
# GLOBAL HOST AND SERVICE EVENT HANDLERS
# These options allow you to specify a host and service event handler
# command that is to be run for every host or service state change.
# The global event handler is executed immediately prior to the event
# handler that you have optionally specified in each host or
# service definition. The command argument is the short name of a
# command definition that you define in your host configuration file.
# Read the HTML docs for more information.
global_host_event_handler=asteriks-host-phone-call
#global_service_event_handler=asteriks-service-phone-call
# SERVICE INTER-CHECK DELAY METHOD
# This is the method that Nagios should use when initially
# "spreading out" service checks when it starts monitoring. The
# default is to use smart delay calculation, which will try to
# space all service checks out evenly to minimize CPU load.
# Using the dumb setting will cause all checks to be scheduled
# at the same time (with no delay between them)! This is not a
# good thing for production, but is useful when testing the
# parallelization functionality.
# n = None - don't use any delay between checks
# d = Use a "dumb" delay of 1 second between checks
# s = Use "smart" inter-check delay calculation
# x.xx = Use an inter-check delay of x.xx seconds
# MAXIMUM SERVICE CHECK SPREAD
# This variable determines the timeframe (in minutes) from the
# program start time that an initial check of all services should
# be completed. Default is 30 minutes.
max_service_check_spread=30
# SERVICE CHECK INTERLEAVE FACTOR
# This variable determines how service checks are interleaved.
# Interleaving the service checks allows for a more even
# distribution of service checks and reduced load on remote
# hosts. Setting this value to 1 is equivalent to how versions
# of Nagios previous to 0.0.5 did service checks. Set this
# value to s (smart) for automatic calculation of the interleave
# factor unless you have a specific reason to change it.
# s = Use "smart" interleave factor calculation
# x = Use an interleave factor of x, where x is a
# number greater than or equal to 1.
service_interleave_factor=s
# HOST INTER-CHECK DELAY METHOD
# "spreading out" host checks when it starts monitoring. The
# space all host checks out evenly to minimize CPU load.
# MAXIMUM HOST CHECK SPREAD
# program start time that an initial check of all hosts should
max_host_check_spread=30
# MAXIMUM CONCURRENT SERVICE CHECKS
# This option allows you to specify the maximum number of
# service checks that can be run in parallel at any given time.
# Specifying a value of 1 for this variable essentially prevents
# any service checks from being parallelized. A value of 0
# will not restrict the number of concurrent checks that are
# being executed.
max_concurrent_checks=0
# HOST AND SERVICE CHECK REAPER FREQUENCY
# This is the frequency (in seconds!) that Nagios will process
# the results of host and service checks.
# MAX CHECK RESULT REAPER TIME
# This is the max amount of time (in seconds) that a single
# check result reaper event will be allowed to run before
# returning control back to Nagios so it can perform other
# duties.
max_check_result_reaper_time=30
# CHECK RESULT PATH
# This is directory where Nagios stores the results of host and
# service checks that have not yet been processed.
# Note: Make sure that only one instance of Nagios has access
# to this directory!
check_result_path=/var/log/nagios/spool/checkresults
# MAX CHECK RESULT FILE AGE
# This option determines the maximum age (in seconds) which check
# result files are considered to be valid. Files older than this
# threshold will be mercilessly deleted without further processing.
# CACHED HOST CHECK HORIZON
# This option determines the maximum amount of time (in seconds)
# that the state of a previous host check is considered current.
# Cached host states (from host checks that were performed more
# recently that the timeframe specified by this value) can immensely
# improve performance in regards to the host check logic.
# Too high of a value for this option may result in inaccurate host
# states being used by Nagios, while a lower value may result in a
# performance hit for host checks. Use a value of 0 to disable host
# check caching.
cached_host_check_horizon=15
# CACHED SERVICE CHECK HORIZON
# that the state of a previous service check is considered current.
# Cached service states (from service checks that were performed more
# improve performance in regards to predictive dependency checks.
# Use a value of 0 to disable service check caching.
cached_service_check_horizon=15
# ENABLE PREDICTIVE HOST DEPENDENCY CHECKS
# This option determines whether or not Nagios will attempt to execute
# checks of hosts when it predicts that future dependency logic test
# may be needed. These predictive checks can help ensure that your
# host dependency logic works well.
# Values:
# 0 = Disable predictive checks
# 1 = Enable predictive checks (default)
# ENABLE PREDICTIVE SERVICE DEPENDENCY CHECKS
# checks of service when it predicts that future dependency logic test
# service dependency logic works well.
# Values:
# SOFT STATE DEPENDENCIES
# This option determines whether or not Nagios will use soft state
# information when checking host and service dependencies. Normally
# Nagios will only use the latest hard host or service state when
# checking dependencies. If you want it to use the latest state (regardless
# of whether its a soft or hard state type), enable this option.
# Values:
# 0 = Don't use soft state dependencies (default)
# 1 = Use soft state dependencies
soft_state_dependencies=0
# TIME CHANGE ADJUSTMENT THRESHOLDS
# These options determine when Nagios will react to detected changes
# in system time (either forward or backwards).
#time_change_threshold=900
# AUTO-RESCHEDULING OPTION
# automatically reschedule active host and service checks to
# "smooth" them out over time. This can help balance the load on
# the monitoring server.
# WARNING: THIS IS AN EXPERIMENTAL FEATURE - IT CAN DEGRADE
# PERFORMANCE, RATHER THAN INCREASE IT, IF USED IMPROPERLY
auto_reschedule_checks=0
# AUTO-RESCHEDULING INTERVAL
# This option determines how often (in seconds) Nagios will
# attempt to automatically reschedule checks. This option only
# has an effect if the auto_reschedule_checks option is enabled.
# Default is 30 seconds.
auto_rescheduling_interval=30
# AUTO-RESCHEDULING WINDOW
# This option determines the "window" of time (in seconds) that
# Nagios will look at when automatically rescheduling checks.
# Only host and service checks that occur in the next X seconds
# (determined by this variable) will be rescheduled. This option
# only has an effect if the auto_reschedule_checks option is
# enabled. Default is 180 seconds (3 minutes).
auto_rescheduling_window=180
# SLEEP TIME
# This is the number of seconds to sleep between checking for system
# events and service checks that need to be run.
sleep_time=0.25
# TIMEOUT VALUES
# These options control how much time Nagios will allow various
# types of commands to execute before killing them off. Options
# are available for controlling maximum time allotted for
# service checks, host checks, event handlers, notifications, the
# ocsp command, and performance data commands. All values are in
# seconds.
service_check_timeout=60
host_check_timeout=30
event_handler_timeout=60
notification_timeout=60
ocsp_timeout=5
perfdata_timeout=5
# RETAIN STATE INFORMATION
# This setting determines whether or not Nagios will save state
# information for services and hosts before it shuts down. Upon
# startup Nagios will reload all saved service and host state
# information before starting to monitor. This is useful for
# maintaining long-term data on state statistics, etc, but will
# slow Nagios down a bit when it (re)starts. Since its only
# a one-time penalty, I think its well worth the additional
# startup delay.
retain_state_information=1
# STATE RETENTION FILE
# This is the file that Nagios should use to store host and
# service state information before it shuts down. The state
# information in this file is also read immediately prior to
# starting to monitor the network when Nagios is restarted.
# This file is used only if the retain_state_information
# variable is set to 1.
state_retention_file=/var/log/nagios/retention.dat
# RETENTION DATA UPDATE INTERVAL
# This setting determines how often (in minutes) that Nagios
# will automatically save retention data during normal operation.
# If you set this value to 0, Nagios will not save retention
# data at regular interval, but it will still save retention
# data before shutting down or restarting. If you have disabled
# state retention, this option has no effect.
retention_update_interval=60
# USE RETAINED PROGRAM STATE
# This setting determines whether or not Nagios will set
# program status variables based on the values saved in the
# retention file. If you want to use retained program status
# information, set this value to 1. If not, set this value
# to 0.
use_retained_program_state=1
# USE RETAINED SCHEDULING INFO
# This setting determines whether or not Nagios will retain
# the scheduling info (next check time) for hosts and services
# based on the values saved in the retention file. If you
# If you want to use retained scheduling info, set this
# value to 1. If not, set this value to 0.
# RETAINED ATTRIBUTE MASKS (ADVANCED FEATURE)
# The following variables are used to specify specific host and
# service attributes that should *not* be retained by Nagios during
# program restarts.
# The values of the masks are bitwise ANDs of values specified
# by the "MODATTR_" definitions found in include/common.h.
# For example, if you do not want the current enabled/disabled state
# of flap detection and event handlers for hosts to be retained, you
# would use a value of 24 for the host attribute mask...
# MODATTR_EVENT_HANDLER_ENABLED (8) + MODATTR_FLAP_DETECTION_ENABLED (16) = 24
# This mask determines what host attributes are not retained
# This mask determines what service attributes are not retained
# These two masks determine what process attributes are not retained.
# There are two masks, because some process attributes have host and service
# options. For example, you can disable active host checks, but leave active
# service checks enabled.
# These two masks determine what contact attributes are not retained.
# There are two masks, because some contact attributes have host and
# service options. For example, you can disable host notifications for
# a contact, but leave service notifications enabled for them.
# INTERVAL LENGTH
# This is the seconds per unit interval as used in the
# host/contact/service configuration files. Setting this to 60 means
# that each interval is one minute long (60 seconds). Other settings
# have not been tested much, so your mileage is likely to vary...
interval_length=60
# CHECK FOR UPDATES
# This option determines whether Nagios will automatically check to
# see if new updates (releases) are available. It is recommend that you
# enable this option to ensure that you stay on top of the latest critical
# patches to Nagios. Nagios is critical to you - make sure you keep it in
# good shape. Nagios will check once a day for new updates. Data collected
# by Nagios Enterprises from the update check is processed in accordance
# with our privacy policy - see http://api.nagios.org for details.
check_for_updates=0
# BARE UPDATE CHECK
# This option deterines what data Nagios will send to api.nagios.org when
# it checks for updates. By default, Nagios will send information on the
# current version of Nagios you have installed, as well as an indicator as
# to whether this was a new installation or not. Nagios Enterprises uses
# this data to determine the number of users running specific version of
# Nagios. Enable this option if you do not want this information to be sent.
bare_update_check=0
# AGGRESSIVE HOST CHECKING OPTION
# If you don't want to turn on aggressive host checking features, set
# this value to 0 (the default). Otherwise set this value to 1 to
# enable the aggressive check option. Read the docs for more info
# on what aggressive host check is or check out the source code in
# base/checks.c
# SERVICE CHECK EXECUTION OPTION
# This determines whether or not Nagios will actively execute
# service checks when it initially starts. If this option is
# disabled, checks are not actively made, but Nagios can still
# receive and process passive check results that come in. Unless
# you're implementing redundant hosts or have a special need for
# disabling the execution of service checks, leave this enabled!
# Values: 1 = enable checks, 0 = disable checks
execute_service_checks=1
# PASSIVE SERVICE CHECK ACCEPTANCE OPTION
# This determines whether or not Nagios will accept passive
# service checks results when it initially (re)starts.
# Values: 1 = accept passive checks, 0 = reject passive checks
# HOST CHECK EXECUTION OPTION
# host checks when it initially starts. If this option is
# disabling the execution of host checks, leave this enabled!
execute_host_checks=1
# PASSIVE HOST CHECK ACCEPTANCE OPTION
# host checks results when it initially (re)starts.
# NOTIFICATIONS OPTION
# This determines whether or not Nagios will sent out any host or
# service notifications when it is initially (re)started.
# Values: 1 = enable notifications, 0 = disable notifications
enable_notifications=1
# EVENT HANDLER USE OPTION
# This determines whether or not Nagios will run any host or
# service event handlers when it is initially (re)started. Unless
# you're implementing redundant hosts, leave this option enabled.
# Values: 1 = enable event handlers, 0 = disable event handlers
enable_event_handlers=1
# PROCESS PERFORMANCE DATA OPTION
# This determines whether or not Nagios will process performance
# data returned from service and host checks. If this option is
# enabled, host performance data will be processed using the
# host_perfdata_command (defined below) and service performance
# data will be processed using the service_perfdata_command (also
# defined below). Read the HTML docs for more information on
# performance data.
# Values: 1 = process performance data, 0 = do not process performance data
process_performance_data=0
# HOST AND SERVICE PERFORMANCE DATA PROCESSING COMMANDS
# These commands are run after every host and service check is
# performed. These commands are executed only if the
# enable_performance_data option (above) is set to 1. The command
# argument is the short name of a command definition that you
# define in your host configuration file. Read the HTML docs for
# more information on performance data.
#host_perfdata_command=process-host-perfdata
#service_perfdata_command=process-service-perfdata
# HOST AND SERVICE PERFORMANCE DATA FILES
# These files are used to store host and service performance data.
# Performance data is only written to these files if the
#host_perfdata_file=/tmp/host-perfdata
#service_perfdata_file=/tmp/service-perfdata
# HOST AND SERVICE PERFORMANCE DATA FILE TEMPLATES
# These options determine what data is written (and how) to the
# performance data files. The templates may contain macros, special
# characters (\t for tab, \r for carriage return, \n for newline)
# and plain text. A newline is automatically added after each write
# to the performance data file. Some examples of what you can do are
# shown below.
#host_perfdata_file_template=[HOSTPERFDATA]\t$TIMET$\t$HOSTNAME$\t$HOSTEXECUTIONTIME$\t$HOSTOUTPUT$\t$HOSTPERFDATA$
#service_perfdata_file_template=[SERVICEPERFDATA]\t$TIMET$\t$HOSTNAME$\t$SERVICEDESC$\t$SERVICEEXECUTIONTIME$\t$SERVICELATENCY$\t$SERVICEOUTPUT$\t$SERVICEPERFDATA$
# HOST AND SERVICE PERFORMANCE DATA FILE MODES
# This option determines whether or not the host and service
# performance data files are opened in write ("w") or append ("a")
# mode. If you want to use named pipes, you should use the special
# pipe ("p") mode which avoid blocking at startup, otherwise you will
# likely want the defult append ("a") mode.
#host_perfdata_file_mode=a
#service_perfdata_file_mode=a
# HOST AND SERVICE PERFORMANCE DATA FILE PROCESSING INTERVAL
# These options determine how often (in seconds) the host and service
# performance data files are processed using the commands defined
# below. A value of 0 indicates the files should not be periodically
# processed.
#host_perfdata_file_processing_interval=0
#service_perfdata_file_processing_interval=0
# HOST AND SERVICE PERFORMANCE DATA FILE PROCESSING COMMANDS
# These commands are used to periodically process the host and
# service performance data files. The interval at which the
# processing occurs is determined by the options above.
#host_perfdata_file_processing_command=process-host-perfdata-file
#service_perfdata_file_processing_command=process-service-perfdata-file
# HOST AND SERVICE PERFORMANCE DATA PROCESS EMPTY RESULTS
# THese options determine wether the core will process empty perfdata
# results or not. This is needed for distributed monitoring, and intentionally
# turned on by default.
# If you don't require empty perfdata - saving some cpu cycles
# on unwanted macro calculation - you can turn that off. Be careful!
# Values: 1 = enable, 0 = disable
#host_perfdata_process_empty_results=1
#service_perfdata_process_empty_results=1
# OBSESS OVER SERVICE CHECKS OPTION
# This determines whether or not Nagios will obsess over service
# checks and run the ocsp_command defined below. Unless you're
# planning on implementing distributed monitoring, do not enable
# this option. Read the HTML docs for more information on
# implementing distributed monitoring.
# Values: 1 = obsess over services, 0 = do not obsess (default)
obsess_over_services=0
# OBSESSIVE COMPULSIVE SERVICE PROCESSOR COMMAND
# This is the command that is run for every service check that is
# processed by Nagios. This command is executed only if the
# obsess_over_services option (above) is set to 1. The command
# more information on implementing distributed monitoring.
#ocsp_command=somecommand
# OBSESS OVER HOST CHECKS OPTION
# This determines whether or not Nagios will obsess over host
# checks and run the ochp_command defined below. Unless you're
# Values: 1 = obsess over hosts, 0 = do not obsess (default)
obsess_over_hosts=0
# OBSESSIVE COMPULSIVE HOST PROCESSOR COMMAND
# This is the command that is run for every host check that is
# obsess_over_hosts option (above) is set to 1. The command
#ochp_command=somecommand
# TRANSLATE PASSIVE HOST CHECKS OPTION
# This determines whether or not Nagios will translate
# DOWN/UNREACHABLE passive host check results into their proper
# state for this instance of Nagios. This option is useful
# if you have distributed or failover monitoring setup. In
# these cases your other Nagios servers probably have a different
# "view" of the network, with regards to the parent/child relationship
# of hosts. If a distributed monitoring server thinks a host
# is DOWN, it may actually be UNREACHABLE from the point of
# this Nagios instance. Enabling this option will tell Nagios
# to translate any DOWN or UNREACHABLE host states it receives
# passively into the correct state from the view of this server.
# Values: 1 = perform translation, 0 = do not translate (default)
# PASSIVE HOST CHECKS ARE SOFT OPTION
# This determines whether or not Nagios will treat passive host
# checks as being HARD or SOFT. By default, a passive host check
# result will put a host into a HARD state type. This can be changed
# by enabling this option.
# Values: 0 = passive checks are HARD, 1 = passive checks are SOFT
# ORPHANED HOST/SERVICE CHECK OPTIONS
# These options determine whether or not Nagios will periodically
# check for orphaned host service checks. Since service checks are
# not rescheduled until the results of their previous execution
# instance are processed, there exists a possibility that some
# checks may never get rescheduled. A similar situation exists for
# host checks, although the exact scheduling details differ a bit
# from service checks. Orphaned checks seem to be a rare
# problem and should not happen under normal circumstances.
# If you have problems with service checks never getting
# rescheduled, make sure you have orphaned service checks enabled.
check_for_orphaned_services=1
check_for_orphaned_hosts=1
# SERVICE FRESHNESS CHECK OPTION
# This option determines whether or not Nagios will periodically
# check the "freshness" of service results. Enabling this option
# is useful for ensuring passive checks are received in a timely
# manner.
# Values: 1 = enabled freshness checking, 0 = disable freshness checking
check_service_freshness=1
# SERVICE FRESHNESS CHECK INTERVAL
# This setting determines how often (in seconds) Nagios will
# check the "freshness" of service check results. If you have
# disabled service freshness checking, this option has no effect.
# SERVICE CHECK TIMEOUT STATE
# This setting determines the state Nagios will report when a
# service check times out - that is does not respond within
# service_check_timeout seconds. This can be useful if a
# machine is running at too high a load and you do not want
# to consider a failed service check to be critical (the default).
# Valid settings are:
# c - Critical (default)
# u - Unknown
# w - Warning
# o - OK
service_check_timeout_state=c
# HOST FRESHNESS CHECK OPTION
# check the "freshness" of host results. Enabling this option
# manner.
check_host_freshness=0
# HOST FRESHNESS CHECK INTERVAL
# check the "freshness" of host check results. If you have
# disabled host freshness checking, this option has no effect.
# ADDITIONAL FRESHNESS THRESHOLD LATENCY
# This setting determines the number of seconds that Nagios
# will add to any host and service freshness thresholds that
# it calculates (those not explicitly specified by the user).
additional_freshness_latency=15
# FLAP DETECTION OPTION
# This option determines whether or not Nagios will try
# and detect hosts and services that are "flapping".
# Flapping occurs when a host or service changes between
# states too frequently. When Nagios detects that a
# host or service is flapping, it will temporarily suppress
# notifications for that host/service until it stops
# flapping. Flap detection is very experimental, so read
# the HTML documentation before enabling this feature!
# Values: 1 = enable flap detection
# 0 = disable flap detection (default)
enable_flap_detection=1
# FLAP DETECTION THRESHOLDS FOR HOSTS AND SERVICES
# Read the HTML documentation on flap detection for
# an explanation of what this option does. This option
# has no effect if flap detection is disabled.
low_host_flap_threshold=5.0
high_host_flap_threshold=20.0
# DATE FORMAT OPTION
# This option determines how short dates are displayed. Valid options
# include:
# us (MM-DD-YYYY HH:MM:SS)
# euro (DD-MM-YYYY HH:MM:SS)
# iso8601 (YYYY-MM-DD HH:MM:SS)
# strict-iso8601 (YYYY-MM-DDTHH:MM:SS)
date_format=us
# TIMEZONE OFFSET
# This option is used to override the default timezone that this
# instance of Nagios runs in. If not specified, Nagios will use
# the system configured timezone.
# NOTE: In order to display the correct timezone in the CGIs, you
# will also need to alter the Apache directives for the CGI path
# to include your timezone. Example:
# <Directory "/usr/local/nagios/sbin/">
# SetEnv TZ "Australia/Brisbane"
# </Directory>
#use_timezone=US/Mountain
#use_timezone=Australia/Brisbane
# P1.PL FILE LOCATION
# This value determines where the p1.pl perl script (used by the
# embedded Perl interpreter) is located. If you didn't compile
# Nagios with embedded Perl support, this option has no effect.
p1_file=/usr/sbin/p1.pl
# EMBEDDED PERL INTERPRETER OPTION
# This option determines whether or not the embedded Perl interpreter
# will be enabled during runtime. This option has no effect if Nagios
# has not been compiled with support for embedded Perl.
# Values: 0 = disable interpreter, 1 = enable interpreter
enable_embedded_perl=1
# EMBEDDED PERL USAGE OPTION
# This option determines whether or not Nagios will process Perl plugins
# and scripts with the embedded Perl interpreter if the plugins/scripts
# do not explicitly indicate whether or not it is okay to do so. Read
# the HTML documentation on the embedded Perl interpreter for more
# information on how this option works.
use_embedded_perl_implicitly=1
# ILLEGAL OBJECT NAME CHARACTERS
# This option allows you to specify illegal characters that cannot
# be used in host names, service descriptions, or names of other
# object types.
# ILLEGAL MACRO OUTPUT CHARACTERS
# This option allows you to specify illegal characters that are
# stripped from macros before being used in notifications, event
# handlers, etc. This DOES NOT affect macros used in service or
# host check commands.
# The following macros are stripped of the characters you specify:
# $HOSTOUTPUT$
# $HOSTPERFDATA$
# $HOSTACKAUTHOR$
# $HOSTACKCOMMENT$
# $SERVICEOUTPUT$
# $SERVICEPERFDATA$
# $SERVICEACKAUTHOR$
# $SERVICEACKCOMMENT$
# REGULAR EXPRESSION MATCHING
# takes place in the object config files. Regular expression
use_regexp_matching=0
# "TRUE" REGULAR EXPRESSION MATCHING
# This option controls whether or not "true" regular expression
# matching takes place in the object config files. This option
# only has an effect if regular expression matching is enabled
# (see above). If this option is DISABLED, regular expression
# matching only occurs if a string contains wildcard characters
# (* and ?). If the option is ENABLED, regexp matching occurs
# all the time (which can be annoying).
# Values: 1 = enable true matching, 0 = disable true matching
use_true_regexp_matching=0
# ADMINISTRATOR EMAIL/PAGER ADDRESSES
# The email and pager address of a global administrator (likely you).
# Nagios never uses these values itself, but you can access them by
# using the $ADMINEMAIL$ and $ADMINPAGER$ macros in your notification
# commands.
admin_email=nagios@localhost
admin_pager=pagenagios@localhost
# DAEMON CORE DUMP OPTION
# This option determines whether or not Nagios is allowed to create
# a core dump when it runs as a daemon. Note that it is generally
# considered bad form to allow this, but it may be useful for
# debugging purposes. Enabling this option doesn't guarantee that
# a core file will be produced, but that's just life...
# Values: 1 - Allow core dumps
# 0 - Do not allow core dumps (default)
daemon_dumps_core=0
# LARGE INSTALLATION TWEAKS OPTION
# This option determines whether or not Nagios will take some shortcuts
# which can save on memory and CPU usage in large Nagios installations.
# Read the documentation for more information on the benefits/tradeoffs
# of enabling this option.
# Values: 1 - Enabled tweaks
# 0 - Disable tweaks (default)
# ENABLE ENVIRONMENT MACROS
# This option determines whether or not Nagios will make all standard
# macros available as environment variables when host/service checks
# and system commands (event handlers, notifications, etc.) are
# executed. Enabling this option can cause performance issues in
# large installations, as it will consume a bit more memory and (more
# importantly) consume more CPU.
# Values: 1 - Enable environment variable macros (default)
# 0 - Disable environment variable macros
enable_environment_macros=1
# CHILD PROCESS MEMORY OPTION
# This option determines whether or not Nagios will free memory in
# child processes (processed used to execute system commands and host/
# service checks). If you specify a value here, it will override
# program defaults.
# Value: 1 - Free memory in child processes
# 0 - Do not free memory in child processes
#free_child_process_memory=1
# CHILD PROCESS FORKING BEHAVIOR
# This option determines how Nagios will fork child processes
# (used to execute system commands and host/service checks). Normally
# child processes are fork()ed twice, which provides a very high level
# of isolation from problems. Fork()ing once is probably enough and will
# save a great deal on CPU usage (in large installs), so you might
# want to consider using this. If you specify a value here, it will
# program defaults.
# Value: 1 - Child processes fork() twice
# 0 - Child processes fork() just once
#child_processes_fork_twice=1
# DEBUG LEVEL
# be written to the debug file. OR values together to log multiple
# types of information.
# Values:
# -1 = Everything
# 0 = Nothing
# 1 = Functions
# 2 = Configuration
# 4 = Process information
# 8 = Scheduled events
# 16 = Host/service checks
# 32 = Notifications
# 64 = Event broker
# 128 = External commands
# 256 = Commands
# 512 = Scheduled downtime
# 1024 = Comments
# 2048 = Macros
debug_level= 32 OR 64 OR 2048
# DEBUG VERBOSITY
# This option determines how verbose the debug log out will be.
# Values: 0 = Brief output
# 1 = More detailed
# 2 = Very detailed
debug_verbosity=2
# DEBUG FILE
# This option determines where Nagios should write debugging information.
debug_file=/var/log/nagios/nagios.debug
# MAX DEBUG FILE SIZE
# This option determines the maximum size (in bytes) of the debug file. If
# the file grows larger than this size, it will be renamed with a .old
# extension. If a file already exists with a .old extension it will
# automatically be deleted. This helps ensure your disk space usage doesn't
# get out of control when debugging Nagios.
max_debug_file_size=1000000
Re: event handler
yes, I have global_event_handler =1, shall I disable it?
Re: event handler
For now, disable those event handlers because you have configured them on the objects.
When you get a chance can you post the contents of test.txt from my previous post?