Re: Checking APC UPS battery runtime

Posted: Wed Dec 16, 2015 7:06 pm
by rdobbsmacu
Ok that resolved the command line output but nagios web interface is still displaying as in warning state and 0 Minutes.

Any thoughts?

and thank you for all your help so far.

Re: Checking APC UPS battery runtime

Posted: Wed Dec 16, 2015 7:38 pm
by Box293
Check to make sure valid values are being returned by echoing the varibales:

Code: Select all

echo "runtime: $runtime"
echo "min: $min"
Add these lines after your a and b variables.

Re: Checking APC UPS battery runtime

Posted: Wed Dec 16, 2015 8:16 pm
by rdobbsmacu
Yes those values are returning correctly plus I also echoed stateid in all three sections.

Getting current battery runtime 95 minutes |calls=$runtime;27000;12000
Stateid 0


And nagios interface is showing warning and sending notifications.

Re: Checking APC UPS battery runtime

Posted: Wed Dec 16, 2015 10:54 pm
by Box293
Can you show us your command and service definitions.

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 2:44 pm
by rdobbsmacu
Here is the my updated script

Code: Select all

#!/bin/bash
host=$1
runtime=$(/usr/local/nagios/libexec/check_snmp -H $host -C macu-pub -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0|awk '{print $5}'| grep -o '[0-9]*')

echo $runtime

min=$(expr $runtime / 6000);
echo $min

a=27000
b=12000

##### IF else then begining #####

##### OK State #####
if [[ "$runtime" -gt "$a" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
stateid=0
echo $stateid
######Warning State ######
elif [[ "$runtime" -le "$a" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
stateid=1
echo $stateid
######Critical State #####
elif [[ "$runtime" -le "$b" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
stateid=2
echo $stateid
##### End of If Else Then ######

fi
exit $stateid
Here is the command i'm running and the output from the above script

Code: Select all

./check_apc_runtime 172.18.100.65
570000
95
Current Battery Runtime 95 Minutes|calles=570000;27000;12000
0

Here is the a screenshot of the service and command in nagios.
https://support.nagios.com/forum/downlo ... w&id=11444



https://support.nagios.com/forum/downlo ... w&id=11445

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 2:56 pm
by rdobbsmacu
I also have another script that i use to verify my equipment closets and rooms don't drop blow a set temperatures. The command line output is right but the nagios interface is also saying it is in a warning state when the temp is above the warning temp by 15 dergrees.

here is my low temp script

Code: Select all

#!/bin/bash
host=$1
temp=$(/usr/local/nagios/libexec/check_snmp -H $host -C macu-pub -o .1.3.6.1.4.1.318.1.1.25.1.2.1.5.1.1|awk '{print $4}'| grep -o '[0-9]*')

a=59
b=48

####### If statement normal ############
if [[ "$temp" -gt "$a" ]]
then
echo "Current Room Temperature is $(($temp))""|calls=$temp;59;48"
stateid=0
#echo $stateid


######## If statement warning ##########
elif [[ "$temp" -le "$a" ]]
then
echo "Currrent Room Temperature is $(($temp))""|calls=$temp;59;48"
stateid=1
#echo $stateid

######### If statement critical #########
elif [[ "$temp" -le "$b" ]]
then
echo "Current Room Temperature is $(($temp))""|calls=$temp;59;48"
stateid=2
#echo $stateid

fi

exit $stateid

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 3:24 pm
by rkennedy
Let's try to stick the conversation to the initial script posted, and get that fixed - because they are so related I think it'll fix things all around.

Can you give this a try and let us know the result? -

Code: Select all

#!/bin/bash
host=$1
runtime=$(/usr/local/nagios/libexec/check_snmp -H $host -C macu-pub -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0|awk '{print $5}'| grep -o '[0-9]*')
min=$(expr $runtime / 6000);

a=27000
b=12000

##### IF else then begining #####

##### OK State #####
if [[ "$runtime" -gt "$a" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
exit 0

######Warning State ######
elif [[ "$runtime" -le "$a" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
exit 1

######Critical State #####
elif [[ "$runtime" -le "$b" ]]
then
echo "Current Battery Runtime $(($min)) Minutes""|calles=$runtime;27000;12000"
exit 2
##### End of If Else Then ######

##### Catchall else #####
else
echo "Unkown error"
exit 3
fi
##### Catchall close #####
ups-script.PNG

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 3:27 pm
by rdobbsmacu
If I run the script from the command line and then right after the script completes I run echo $stateid and get a blank line. Almost like it is not setting the stateid value.

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 3:40 pm
by rdobbsmacu
updated the script but the status is still in the warning status .

output from command line

libexec]# ./check_apc_runtime 172.18.100.64
Current Battery Runtime 90 Minutes|calles=540000;27000;12000


https://support.nagios.com/forum/downlo ... 394f1c760l in the warning.

Re: Checking APC UPS battery runtime

Posted: Thu Dec 17, 2015 3:58 pm
by rkennedy
rdobbsmacu wrote:If I run the script from the command line and then right after the script completes I run echo $stateid and get a blank line. Almost like it is not setting the stateid value.
I took out the stateid variable, and lead directly to an exit value in each if statement.

Can you force a check and see if it changes? It looks like the service is checking only every 30 minutes.

Can you post a screenshot of the advanced tab for me to take a look at?