rrd does not exist
Re: rrd does not exist
looking at your results file it appears the system date on your server was set into the future as you have data in the RRD's dated Fri, 04 Apr 2014 12:20:48 GMT.
It is because of this that the rrd's cannot update with performance data.
How important is the historical information on your installation? I ask because by far the easiest way to remedy the situation would be to delete the old .rrd files and let new ones be created.
gm_rajkumar
Re: Problems with Host Performance Graphs and Bandwidth
Post by gm_rajkumar »
Please find below result.
[root@monitoring ccm]# LANG=C LC_ALL=C /usr/bin/mrtg /etc/mrtg/mrtg.cfg
SNMP Error:
no response received
SNMPv1_Session (remote host: "192.168.14.61" [192.168.14.61].161)
                  community: "public"
                 request ID: 266393582
                PDU bufsize: 8000 bytes
                    timeout: 2s
                    retries: 5
                    backoff: 1)
 at /usr/bin/../lib/mrtg2/SNMP_util.pm line 490
SNMPGET Problem for ifInOctets.1 ifOutOctets.1 on [email protected]:::::1:v4only
 at /usr/bin/mrtg line 2035
Wednesday, 6 February 2013 at 7:06: WARNING: skipping because at least the query for ifInOctets.1 on  192.168.14.61 did not succeed
Wednesday, 6 February 2013 at 7:06: WARNING: no data for ifInOctets&ifOutOctets:[email protected]. Skipping further queries for Host 192.168.14.61 in this round.
SNMP Error:
SNMPv1_Session (remote host: "10.66.0.86" [10.66.0.86].161)
                  community: "=snmpDGRO"
                 request ID: 2054426717
                    timeout: 2s
                    retries: 5
                    backoff: 1)
Wednesday, 6 February 2013 at 7:06: WARNING: skipping because at least the query for ifInOctets.1 on  10.66.0.86 did not succeed
Wednesday, 6 February 2013 at 7:06: WARNING: no data for ifInOctets&ifOutOctets:[email protected]. Skipping further queries for Host 10.66.0.86 in this round.
SNMP Error:
SNMPv1_Session (remote host: "10.66.0.85" [10.66.0.85].161)
                 request ID: 1307097251
                    timeout: 2s
                    retries: 5
                    backoff: 1)
SNMPGET Problem for ifInOctets.2 ifOutOctets.2 on [email protected]:::::1:v4only
Wednesday, 6 February 2013 at 7:06: WARNING: skipping because at least the query for ifInOctets.2 on  10.66.0.85 did not succeed
Wednesday, 6 February 2013 at 7:06: WARNING: no data for ifInOctets&ifOutOctets:[email protected]. Skipping further queries for Host 10.66.0.85 in this round.
646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10106.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10106.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10107.rrd with '1360119646:230532860:529591619' /var/lib/mrtg/10.66.0.84_10107.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10108.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10108.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10109.rrd with '1360119646:713665707:534575695' /var/lib/mrtg/10.66.0.84_10109.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10110.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10110.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10111.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10111.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10113.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10113.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10114.rrd with '1360119646:1429266211:2346105797' /var/lib/mrtg/10.66.0.84_10114.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10115.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10115.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10116.rrd with '1360119646:395755243:498438890' /var/lib/mrtg/10.66.0.84_10116.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10117.rrd with '1360119646:697773472:3436816441' /var/lib/mrtg/10.66.0.84_10117.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10118.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10118.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10119.rrd with '1360119646:1506169328:2732035107' /var/lib/mrtg/10.66.0.84_10119.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10120.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10120.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10121.rrd with '1360119646:2660502729:3358640447' /var/lib/mrtg/10.66.0.84_10121.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10123.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10123.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10126.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10126.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10127.rrd with '1360119646:835734332:2274536688' /var/lib/mrtg/10.66.0.84_10127.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10128.rrd with '1360119646:1463141474:4027019408' /var/lib/mrtg/10.66.0.84_10128.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10129.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10129.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10130.rrd with '1360119646:2649401542:558833976' /var/lib/mrtg/10.66.0.84_10130.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10131.rrd with '1360119646:3996914628:3909112205' /var/lib/mrtg/10.66.0.84_10131.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10132.rrd with '1360119646:1370245502:3937177335' /var/lib/mrtg/10.66.0.84_10132.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10133.rrd with '1360119646:1941551226:206148032' /var/lib/mrtg/10.66.0.84_10133.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10134.rrd with '1360119646:4238269768:225943381' /var/lib/mrtg/10.66.0.84_10134.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10135.rrd with '1360119646:506824519:1727728428' /var/lib/mrtg/10.66.0.84_10135.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10136.rrd with '1360119646:2212075181:457892280' /var/lib/mrtg/10.66.0.84_10136.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10137.rrd with '1360119646:8067791:838658434' /var/lib/mrtg/10.66.0.84_10137.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10138.rrd with '1360119646:304230190:3681117731' /var/lib/mrtg/10.66.0.84_10138.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10139.rrd with '1360119646:25324193:2773481056' /var/lib/mrtg/10.66.0.84_10139.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10140.rrd with '1360119646:23416271:3149564681' /var/lib/mrtg/10.66.0.84_10140.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10141.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10141.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10142.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10142.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10143.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10143.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10144.rrd with '1360119646:2159013435:4099120539' /var/lib/mrtg/10.66.0.84_10144.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10145.rrd with '1360119646:3277160279:2629845904' /var/lib/mrtg/10.66.0.84_10145.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10146.rrd with '1360119646:506213001:3420991914' /var/lib/mrtg/10.66.0.84_10146.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10147.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10147.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10148.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10148.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10149.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10149.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10150.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10150.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10151.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10151.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10152.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10152.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10201.rrd with '1360119646:3333420952:3755340032' /var/lib/mrtg/10.66.0.84_10201.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10202.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10202.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10602.rrd with '1360119646:213084654:1414753032' /var/lib/mrtg/10.66.0.84_10602.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10603.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10603.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10604.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10604.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10605.rrd with '1360119646:469688632:3048406593' /var/lib/mrtg/10.66.0.84_10605.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10606.rrd with '1360119646:90664527:489381741' /var/lib/mrtg/10.66.0.84_10606.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10607.rrd with '1360119646:3430396352:3527479432' /var/lib/mrtg/10.66.0.84_10607.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10608.rrd with '1360119646:2509709918:1321706124' /var/lib/mrtg/10.66.0.84_10608.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10609.rrd with '1360119646:633988172:2134450342' /var/lib/mrtg/10.66.0.84_10609.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10610.rrd with '1360119646:54417:333878' /var/lib/mrtg/10.66.0.84_10610.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10611.rrd with '1360119646:1144231501:2336194454' /var/lib/mrtg/10.66.0.84_10611.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10612.rrd with '1360119646:618775217:3198358389' /var/lib/mrtg/10.66.0.84_10612.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10613.rrd with '1360119646:2553828405:541146727' /var/lib/mrtg/10.66.0.84_10613.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10614.rrd with '1360119646:469671180:3048612731' /var/lib/mrtg/10.66.0.84_10614.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10615.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10615.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10616.rrd with '1360119646:2597045806:4101411785' /var/lib/mrtg/10.66.0.84_10616.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10617.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10617.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10618.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10618.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10619.rrd with '1360119646:882703876:3462300591' /var/lib/mrtg/10.66.0.84_10619.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10620.rrd with '1360119646:509033319:3087985913' /var/lib/mrtg/10.66.0.84_10620.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10621.rrd with '1360119646:25907441:2446312544' /var/lib/mrtg/10.66.0.84_10621.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10622.rrd with '1360119646:686251467:3272277123' /var/lib/mrtg/10.66.0.84_10622.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10623.rrd with '1360119646:436612363:1861287260' /var/lib/mrtg/10.66.0.84_10623.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10624.rrd with '1360119646:174201983:2025048360' /var/lib/mrtg/10.66.0.84_10624.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10625.rrd with '1360119646:412304154:2121036789' /var/lib/mrtg/10.66.0.84_10625.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10626.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10626.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10627.rrd with '1360119646:125514502:1176069885' /var/lib/mrtg/10.66.0.84_10627.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10628.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10628.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10629.rrd with '1360119646:3688794599:702715705' /var/lib/mrtg/10.66.0.84_10629.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10630.rrd with '1360119646:493492173:3072477020' /var/lib/mrtg/10.66.0.84_10630.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10631.rrd with '1360119646:396641127:3459091848' /var/lib/mrtg/10.66.0.84_10631.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10632.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10632.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10633.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10633.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10634.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10634.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10635.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10635.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10636.rrd with '1360119646:19568640:1227841581' /var/lib/mrtg/10.66.0.84_10636.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10637.rrd with '1360119646:20648881:2212975704' /var/lib/mrtg/10.66.0.84_10637.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10638.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10638.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10639.rrd with '1360119646:3271201970:2710033877' /var/lib/mrtg/10.66.0.84_10639.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10640.rrd with '1360119646:2364071734:1476176209' /var/lib/mrtg/10.66.0.84_10640.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10641.rrd with '1360119646:12812204:3104535779' /var/lib/mrtg/10.66.0.84_10641.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10642.rrd with '1360119646:2191349418:4191975887' /var/lib/mrtg/10.66.0.84_10642.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10643.rrd with '1360119646:1312843068:1516081708' /var/lib/mrtg/10.66.0.84_10643.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10644.rrd with '1360119646:2817015083:2160420103' /var/lib/mrtg/10.66.0.84_10644.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10645.rrd with '1360119646:3615434170:4005179975' /var/lib/mrtg/10.66.0.84_10645.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10646.rrd with '1360119646:3787045074:3858307366' /var/lib/mrtg/10.66.0.84_10646.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10649.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10649.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10650.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10650.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10651.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10651.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10652.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10652.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10701.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10701.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_10702.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_10702.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11101.rrd with '1360119646:1878854109:4095017976' /var/lib/mrtg/10.66.0.84_11101.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11102.rrd with '1360119646:1211308086:4036250556' /var/lib/mrtg/10.66.0.84_11102.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11103.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11103.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11104.rrd with '1360119646:2440323389:832587476' /var/lib/mrtg/10.66.0.84_11104.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11105.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11105.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11106.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11106.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11107.rrd with '1360119646:139875073:2698938960' /var/lib/mrtg/10.66.0.84_11107.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11108.rrd with '1360119646:361118954:2921400969' /var/lib/mrtg/10.66.0.84_11108.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11110.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11110.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11111.rrd with '1360119646:122346422:805038747' /var/lib/mrtg/10.66.0.84_11111.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11112.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11112.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11113.rrd with '1360119646:1585590955:446871204' /var/lib/mrtg/10.66.0.84_11113.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11114.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11114.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11115.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11115.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11116.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11116.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11117.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11117.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11118.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11118.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11119.rrd with '1360119646:800064450:1571209309' /var/lib/mrtg/10.66.0.84_11119.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11122.rrd with '1360119646:3968257121:1664707391' /var/lib/mrtg/10.66.0.84_11122.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11123.rrd with '1360119646:40440301:2508195634' /var/lib/mrtg/10.66.0.84_11123.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11124.rrd with '1360119646:790982291:1440186082' /var/lib/mrtg/10.66.0.84_11124.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11125.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11125.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11126.rrd with '1360119646:2283214713:829801450' /var/lib/mrtg/10.66.0.84_11126.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11127.rrd with '1360119646:774513780:3286463701' /var/lib/mrtg/10.66.0.84_11127.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11128.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11128.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11129.rrd with '1360119646:2451650952:739832436' /var/lib/mrtg/10.66.0.84_11129.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11130.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11130.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11131.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11131.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11132.rrd with '1360119646:944087727:3803451801' /var/lib/mrtg/10.66.0.84_11132.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11133.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11133.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11134.rrd with '1360119646:1187019166:402767890' /var/lib/mrtg/10.66.0.84_11134.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11135.rrd with '1360119646:3306863458:3699385991' /var/lib/mrtg/10.66.0.84_11135.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11136.rrd with '1360119646:576116300:3161625059' /var/lib/mrtg/10.66.0.84_11136.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11137.rrd with '1360119646:27598852:2788786486' /var/lib/mrtg/10.66.0.84_11137.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11138.rrd with '1360119646:3258099028:2376243275' /var/lib/mrtg/10.66.0.84_11138.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11139.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11139.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11140.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11140.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11141.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11141.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11142.rrd with '1360119646:1880131478:3052394414' /var/lib/mrtg/10.66.0.84_11142.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11143.rrd with '1360119646:2613767213:3121249443' /var/lib/mrtg/10.66.0.84_11143.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11144.rrd with '1360119646:271841400:3624249934' /var/lib/mrtg/10.66.0.84_11144.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11147.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11147.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11148.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11148.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11149.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11149.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11150.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11150.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11151.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11151.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11152.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11152.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11201.rrd with '1360119646:4016041471:3899867289' /var/lib/mrtg/10.66.0.84_11201.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/10.66.0.84_11202.rrd with '1360119646:0:0' /var/lib/mrtg/10.66.0.84_11202.rrd: illegal attempt to update using time 1360119646 when last update time is 1396614048 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_1][_IN_] ' $target->[945]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_1][_OUT_] ' $target->[945]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/192.168.204.1_1.rrd with '1360119656:U:U' /var/lib/mrtg/192.168.204.1_1.rrd: illegal attempt to update using time 1360119656 when last update time is 1396614058 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_2][_IN_] ' $target->[946]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_2][_OUT_] ' $target->[946]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/192.168.204.1_2.rrd with '1360119656:U:U' /var/lib/mrtg/192.168.204.1_2.rrd: illegal attempt to update using time 1360119656 when last update time is 1396614058 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_6][_IN_] ' $target->[947]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_6][_OUT_] ' $target->[947]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/192.168.204.1_6.rrd with '1360119656:U:U' /var/lib/mrtg/192.168.204.1_6.rrd: illegal attempt to update using time 1360119656 when last update time is 1396614058 (minimum one second step)
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_7][_IN_] ' $target->[948]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Target[192.168.204.1_7][_OUT_] ' $target->[948]{$mode} ' did not eval into defined data
Wednesday, 6 February 2013 at 7:00: ERROR: Cannot update /var/lib/mrtg/192.168.204.1_7.rrd with '1360119656:U:U' /var/lib/mrtg/192.168.204.1_7.rrd: illegal attempt to update using time 1360119656 when last update time is 1396614058 (minimum one second step)
You have new mail in /var/spool/mail/root
[root@monitoring ccm]# top
top - 07:02:22 up 8 days, 22:24,  5 users,  load average: 4.77, 4.68, 4.46
Tasks: 237 total,   3 running, 228 sleeping,   6 stopped,   0 zombie
Cpu(s): 38.3%us, 11.5%sy,  0.0%ni, 48.5%id,  1.2%wa,  0.1%hi,  0.4%si,  0.0%st
Mem:   3107040k total,  2815600k used,   291440k free,   149120k buffers
Swap:  2031608k total,       68k used,  2031540k free,  1762696k cached
  PID USER      PR  NI  VIRT  RES  SHR S %CPU %MEM    TIME+  COMMAND
12418 postgres  18   0 22028  10m 9.8m S 75.5  0.4   0:11.89 postmaster
12496 postgres  17   0 22028  10m 9.8m S 50.2  0.4   0:06.13 postmaster
  973 apache    16   0 43464  21m 4068 S 10.6  0.7   0:30.35 httpd
27568 apache    16   0 45340  22m 4076 S 10.6  0.8   3:57.24 httpd
 1264 postgres  17   0 21912  10m 9964 R  7.6  0.4   0:22.14 postmaster
28023 postgres  18   0 21912  10m 9.9m R  7.3  0.4   4:08.53 postmaster
 9940 root      15   0 65616  16m 9800 S  3.3  0.5   0:15.13 gnome-terminal
 2994 mysql     15   0  155m  36m 5072 S  1.7  1.2 453:26.93 mysqld
18071 nagios    15   0 15936 4048  908 S  1.7  0.1   5:58.41 nagios
 9851 root      15   0 50688  13m 9464 S  1.0  0.4  41:41.97 vino-server
22291 root      15   0  544m 183m  30m S  1.0  6.1 250:02.89 firefox
 3447 root      15   0 31988  19m 9876 S  0.7  0.7  13:32.28 Xorg
17850 nagios    15   0  7740 2028  912 S  0.7  0.1   2:16.98 ndo2db
  619 root      10  -5     0    0    0 S  0.3  0.0  40:46.72 kjournald
 9645 root      15   0  2444 1168  824 R  0.3  0.0   0:00.20 top
    1 root      15   0  2176  636  556 S  0.0  0.0   0:02.50 init
    2 root      RT  -5     0    0    0 S  0.0  0.0   0:23.39 migration/0
    3 root      39  19     0    0    0 S  0.0  0.0   0:05.13 ksoftirqd/0
    4 root      RT  -5     0    0    0 S  0.0  0.0   0:16.07 migration/1
    5 root      34  19     0    0    0 S  0.0  0.0   0:44.88 ksoftirqd/1
    6 root      RT  -5     0    0    0 S  0.0  0.0   0:19.27 migration/2
    7 root      34  19     0    0    0 S  0.0  0.0   0:00.63 ksoftirqd/2
[6]+  Stopped                 top
gm_rajkumar
I have followed http://assets.nagios.com/downloads/nagi ... Router.pdf cleared all of rrd does not exist entries from /etc/mrtg/mrtg.conf once after that
LANG=C LC_ALL=C /usr/bin/mrtg /etc/mrtg/mrtg.cfg --lock-file /var/lock/mrtg/mrtg_l --confcache-file /var/lib/mrtg/mrtg.ok
I have executed the command, i didnt get any errors. However, its not showing any graph.
Let me know if anything else wants to check further..
Regards,
Raj.
Post by slansing »
Raj, please keep your information separate from the other thread's. As was aforementioned you may be seeing the same issue, but we may run into separate issues down the line, we need to keep them as separate cases in separate threads.
gm_rajkumar
Still this issue persists and i've received the same results referred by David.
[root@monitoring libexec]# service npcd restart
NPCD Stopped.
NPCD started.
[root@monitoring libexec]# ls /usr/local/nagios/share/perfdata/ | wc -l
209
[root@monitoring libexec]# ls /usr/local/nagios/share/xidpe | wc -l
ls: /usr/local/nagios/share/xidpe: No such file or directory
0
[root@monitoring libexec]# ./check_rrdtraf -f /var/lib/mrtg/10.66.0.84_10636.rrd -w 750 -c 900 -l M
OK - Current BW in: 0Mbps Out: 0Mbps|in=.000020Mb/s;750;900 out=.000663Mb/s;750;900
Let me know if you need further.. thanks!!
Regards,
Raj.
Post by slansing »
Raj, we do understand you are getting similar responses, but once again please keep the above information separate on your thread. We are working to resolve both issues, this one has progressed further than yours but you should still be able to follow along on your end. This is the third time I've moved it.
gm_rajkumar
Okay, i can understand your concern. Please let me know if you need further details from my end. Thanks again!!
Regards,
Raj.
I looked at the post here and saw in the error the last update time was 1396614048 which translates to
Was the time on the server off significantly into the future?
gm_rajkumar
There is no issue on system time, it has been sync with ntp.
Regards,
Raj.
gm_rajkumar
I have got the solution for this....
I have updated the http://assets.nagios.com/downloads/nagi ... ios_XI.pdf in Nagios.
After that rrdcached, i have manually created the rrd files respective host. Now this issue has been addressed..however i couldn't able to see performance graphs for routers/switches (ill update on the separate thread).. Thanks!!
Regards,
Raj.