Help with SNMP traps?
Re: Help with SNMP traps?
jbennett wrote:
# snmptranslate .1.3.6.1.4.1.17420.0.6
SNMPv2-SMI::enterprises.17420.0.6
Is this to assume that the MIB file from the manufaturer is incorrect?
I would believe that either they are incorrect or there is another MIB that is needed for these OIDs.
I'm not totally sure, but Google thinks you may be looking for DGPUPS-MIB
jbennett
Post by jbennett »
This is what I've found as well, but I simply cannot find it to download (it's not on the provided CD). I've shot an email to the manufacturer.
In any case, this is only a few of the PDUs that I'm trying to monitor. I'm still not getting anything from any of the other devices. This MIB is only for 18 of the 190 PDUs that I am trying to monitor via traps and I still can't get anything from the 184 UPSs.
jbennett wrote:In any case, this is only a few of the PDUs that I'm trying to monitor. I'm still not getting anything from any of the other devices. This MIB is only for 18 of the 190 PDUs that I am trying to monitor via traps and I still can't get anything from the 184 UPSs.
Are we sure any of the 184 have sent traps? I ask because on many systems a trap is only sent when a problem is detected
jbennett
Post by jbennett »
At some point in the past week plus multiples should have generated traps as we have had power issues at a number of locations. I have not recieved any email notifications of these nor have any of these devices Traps check changed from an OK state when I've checked them at a known down time.
I have the same template applied to the SNMP Traps for both PDUs & UPS as I do for other devices that are sending emails.
Can we verify that Nagios has not changed the state for these by running a state history report for the hosts in question
jbennett
Post by jbennett »
I sent you the statehistory report via PM for the UPS host group for the past week
Let me know if that's not what you need.
Specifically, on page 5, take a look at the critical states for the standard SNMP checks that 'I currently have running for the UPS. There are a number of unknown states as a number of these were offline due to power outages but you won't find any SNMP Traps services listed.
Here is a current example of a UPS that should be generating a trap but isn't (attached).
Can you run the following commands and show us the output?
tail -n 50 /var/log/snmptt/snmptt.log
cat /var/log/messages | grep trap
jbennett
Post by jbennett »
Nothing but a bunch of authentication failures. Since it's just the same thing over and over again, I've snipped the output. I have also included my snmpd.conf for reference.
Thu Apr 18 13:31:47 2013 .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" nagiosserver - An authenticationFailure trap signifies that the SNMP
Thu Apr 18 13:31:48 2013 .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" localhost - An authenticationFailure trap signifies that the SNMP
Thu Apr 18 13:31:50 2013 .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" nagiosserver - An authenticationFailure trap signifies that the SNMP
Thu Apr 18 13:31:50 2013 .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" localhost - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:43 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:43 nagiosserver.company.local [xxx.xxx.xxx.xxx] (via UDP: [127.0.0.1]:40831) TRAP, SNMP v1, community public   .1.3.6.1.4.1.8072.3.2.10 Authentication Failure Trap (0) Uptime: 1 day, 4:54:03.25
Apr 18 13:31:44 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:44 localhost.localdomain [UDP: [127.0.0.1]:48797]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404325) 1 day, 4:54:03.25        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:44 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:44 localhost.localdomain [UDP: [127.0.0.1]:49972]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404325) 1 day, 4:54:03.25        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:45 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:45 nagiosserver.company.local [xxx.xxx.xxx.xxx] (via UDP: [127.0.0.1]:40831) TRAP, SNMP v1, community public   .1.3.6.1.4.1.8072.3.2.10 Authentication Failure Trap (0) Uptime: 1 day, 4:54:05.26
Apr 18 13:31:46 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:46 localhost.localdomain [UDP: [127.0.0.1]:48797]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404526) 1 day, 4:54:05.26        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:46 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:46 localhost.localdomain [UDP: [127.0.0.1]:49972]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404526) 1 day, 4:54:05.26        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:47 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:47 nagiosserver.company.local [xxx.xxx.xxx.xxx] (via UDP: [127.0.0.1]:40831) TRAP, SNMP v1, community public   .1.3.6.1.4.1.8072.3.2.10 Authentication Failure Trap (0) Uptime: 1 day, 4:54:07.27
Apr 18 13:31:47 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:47 localhost.localdomain [UDP: [127.0.0.1]:48797]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404727) 1 day, 4:54:07.27        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:48 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:48 localhost.localdomain [UDP: [127.0.0.1]:49972]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404727) 1 day, 4:54:07.27        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:48 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" nagiosserver - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:48 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" localhost - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:49 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" localhost - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:49 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" nagiosserver - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:49 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:49 nagiosserver.company.local [xxx.xxx.xxx.xxx] (via UDP: [127.0.0.1]:40831) TRAP, SNMP v1, community public   .1.3.6.1.4.1.8072.3.2.10 Authentication Failure Trap (0) Uptime: 1 day, 4:54:09.28
Apr 18 13:31:50 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:50 localhost.localdomain [UDP: [127.0.0.1]:48797]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404928) 1 day, 4:54:09.28        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:50 nagiosserver snmptrapd[2912]: 2013-04-18 13:31:50 localhost.localdomain [UDP: [127.0.0.1]:49972]: .1.3.6.1.2.1.1.3.0 = Timeticks: (10404928) 1 day, 4:54:09.28        .1.3.6.1.6.3.1.1.4.1.0 = OID: .1.3.6.1.6.3.1.1.5.5      .1.3.6.1.6.3.1.1.4.3.0 = OID: .1.3.6.1.4.1.8072.3.2.10
Apr 18 13:31:54 nagiosserver nagios: SERVICE ALERT: localhost;SNMP Traps;WARNING;HARD;1;An authenticationFailure trap signifies that the SNMP  /
Apr 18 13:31:54 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" localhost - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:54 nagiosserver snmptt[0]: .1.3.6.1.6.3.1.1.5.5 Warning "Status Events" nagiosserver - An authenticationFailure trap signifies that the SNMP
Apr 18 13:31:58 nagiosserver nagios: SERVICE ALERT: localhost;SNMP Traps;WARNING;HARD;1;An authenticationFailure trap signifies that the SNMP  /
Apr 18 13:31:59 nagiosserver nagios: SERVICE ALERT: localhost;SNMP Traps;WARNING;HARD;1;An authenticationFailure trap signifies that the SNMP  /
# snmpd.conf
#   - created by the snmpconf configuration program
# SECTION: Access Control Setup
#   This section defines who is allowed to talk to your running
#   snmp agent.
# rwuser: a SNMPv3 read-write user
#   arguments:  user [noauth|auth|priv] [restriction_oid]
rwuser  public auth
# rouser: a SNMPv3 read-only user
rouser  public auth
# rocommunity: a SNMPv1/SNMPv2c read-only access community name
#   arguments:  community [default|hostname|network/bits] [oid]
rocommunity  public
# rwcommunity: a SNMPv1/SNMPv2c read-write access community name
rwcommunity  public
# SECTION: Trap Destinations
#   Here we define who the agent will send traps to.
# trapsink: A SNMPv1 trap receiver
#   arguments: host [community] [portnum]
trapsink  localhost public 162
# trap2sink: A SNMPv2c trap receiver
trap2sink  localhost public 162
# informsink: A SNMPv2c inform (acknowledged trap) receiver
informsink  localhost public 162
# trapcommunity: Default trap sink community to use
#   arguments: community-string
trapcommunity  public
# authtrapenable: Should we send traps when authentication failures occur
#   arguments: 1 | 2   (1 = yes, 2 = no)
authtrapenable  1
# SECTION: Monitor Various Aspects of the Running Host
#   The following check up on various aspects of a host.
# proc: Check for processes that should be running.
#     proc NAME [MAX=0] [MIN=0]
#     NAME:  the name of the process to check for.  It must match
#            exactly (ie, http will not find httpd processes).
#     MAX:   the maximum number allowed to be running.  Defaults to 0.
#     MIN:   the minimum number to be running.  Defaults to 0.
#   The results are reported in the prTable section of the UCD-SNMP-MIB tree
#   Special Case:  When the min and max numbers are both 0, it assumes
#   you want a max of infinity and a min of 1.
proc
# disk: Check for disk space usage of a partition.
#   The agent can check the amount of available disk space, and make
#   sure it is above a set limit.
#    disk PATH [MIN=100000]
#    PATH:  mount path to the disk in question.
#    MIN:   Disks with space below this value will have the Mib's errorFlag set.
#           Can be a raw byte value or a percentage followed by the %
#           symbol.  Default value = 100000.
#   The results are reported in the dskTable section of the UCD-SNMP-MIB tree
disk  / 10%
disk  /tmp 10%
disk  /var 10%
disk  /boot 10%
disk  /var/nagiosramdisk 10%
# load: Check for unreasonable load average values.
#   Watch the load average levels on the machine.
#    load [1MAX=12.0] [5MAX=12.0] [15MAX=12.0]
#    1MAX:   If the 1 minute load average is above this limit at query
#            time, the errorFlag will be set.
#    5MAX:   Similar, but for 5 min average.
#    15MAX:  Similar, but for 15 min average.
#   The results are reported in the laTable section of the UCD-SNMP-MIB tree
load  5.0 4.0 3.0
# file: Check on the size of a file.
#   Display a files size statistics.
#   If it grows to be too large, report an error about it.
#    file /path/to/file [maxsize_in_bytes]
#      if maxsize is not specified, assume only size reporting is needed.
#   The results are reported in the fileTable section of the UCD-SNMP-MIB tree
file  /var/log/maillog 209715200
file
# vi /etc/snmp/snmptrapd.conf
disableAuthorization yes
traphandle default /usr/local/sbin/snmptthandler
# ls -lh /etc/snmp
total 108K
-rw-r--r-- 1 root   root   3.8K Apr 16 08:44 snmpd.conf
-rw-r--r-- 1 root   root   3.9K Jan 29 10:16 snmpd.conf.new
-rw-r--r-- 1 root   root    19K Jan 29 10:17 snmpd.conf.old
-rw-r--r-- 1 root   root     74 Jan 29 13:24 snmptrapd.conf
-rw-r--r-- 1 root   root    45K Apr 18 08:24 snmptt.conf
-rw-rw-r-- 1 apache nagios  26K Mar 28 09:11 snmptt.ini
It looks like the only traps that are making it to the server are from the local machine
Is there a firewall that could be blocking port 162 UDP?
jbennett
Post by jbennett »
I have asked our networking guys and was told no. I specifically asked about it again and was told that they do not block anything on 162 UDP on our network.