Hey guys,
this hp_insight_agents pluging runs fine in the command line, however it returns null in nagios.

Code: Select all


#!/bin/bash
#########################################################
#							#
#	HP/Compaq Insight Management Agents Checker	#
#							#
# check_insight_agents					#
# 	Version 2.0 (October 7, 2011)			#
#							#
# Authored by Jason Leonard				#
# 	E-mail: [email protected]			#
#							#
# Overview						#
# ----------------------------------------------------- #
#	This plugin started out as individual rewrites	#
# of the check_hp plugins - 6 scripts that each provide #
# information on different HP component statuses. I	#
# found myself quite a fan of the plugin's output, and  #
# was using them to learn SNMP and Nagios scripting.	#
# Yet in the plugins, I saw where the code used many	#
# if/then conditions, where case/select statements 	#
# could provide a more efficient analysis and reduce	#
# redundancy in the code.				#
#							#
#	As things developped, I had a strong desire to	#
# find/use 1 plugin that could report all information.	#
# A few were already developped, but as I tested them,  #
# they each seemed to lack output that was meaningful.	#
# In addition, a more amateur programmer myself, I	#
# found myself struggling with the logic of other code. #
# So I set to try and combine the 6 individual plugins  #
# into 1. This is the result of that work.		#
#							#
#	The basic flow of the plugin is that it checks	#
# global health first, and reports on that condition 	#
# most of the time. This leaves the program to only	#
# make 1 check on most iterations. Individual compon-	#
# ents are checked only when the global status might	#
# indicate something wrong. At this point, although	#
# chances are only 1 item has failed, the plugin makes	#
# its best attempt to assume nothing and give info. on	#
# ANY component	that has failed. This also differs from #
# the check_hp plugin, which tended to output each	#
# components status as checked, whether failed or not.	#
#							#
#	I readily admit that the plugins have had	#
# limited testing in our own environment, but we did	#
# have a horrible old Compaq server that I was able to	#
# use to test a number of scenarios. It's multiple	#
# hardware failures actually encouraged me to make sure #
# the plugin could report more than 1 failed component. #
#							#
#	Hopefully, as this plugin is used, I can get 	#
# more feedback on where I may have missed something 	#
# in my logic - I took what seems to be a very unique	#
# approach in checking "global" health before checking	#
# any other conditions.					#
#							#
#	As with every piece of code I write, I made a	#
# strong effort for the code to be easy to follow, and	#
# employed meaningful variable names to help clarify	#
# whatever might be going on in the code.		#
#							#
# This plugin is distributed under the GNU GPL license.	#
# You may re-destribute only according to the terms of 	#
# the GNU GPL v2.					#
#							#
#########################################################

#########################################################
##		     GLOBAL VARIABLES 		       ##
#########################################################
APPNAME=$(basename $0)
VERSION="2.0"
COMMUNITY="public"
EXIT_CODE=0
EXIT_STRING=""

#########################################################
##		    print_help Function		       ##
#########################################################
# Prints out user help and gives examples of proper	#
# plugin usage						#
#########################################################

function print_help () {
	echo 'Insight Management Agent plugin for Nagios'
	echo ''
	echo 'This plugin is not developped by the Nagios Plugin group.'
	echo 'Please do not e-mail them for support on this plugin.'
	echo ''
	echo 'For contact info, please read the plugin script file.'
	echo ''
	echo "Usage of $APPNAME"
	echo " $APPNAME -H <host/IP> -C <community> | -h | -V "
	echo '---------------------------------------------------------------------'
	echo 'Usable Options:'
	echo '    -C public'
	echo '	  (required option)'
	echo '	     The SNMP Community variable - use the name of an SNMP community with read privileges'
	echo '	     By default, the community is assumed to be public'
	echo '    -H hostname'
	echo '    (required option)'
	echo '        The IP address or  hostname of the system to check'
	echo '    -h'
	echo '        This help screen'
	echo '    -V'
	echo '        show the current version of the plugin'
	echo ''
	echo 'Example:'
	echo "    $APPNAME -H 10.0.1.10 -C public"
	echo ''
	echo '---------------------------------------------------------------------'

	return 3
}

#########################################################
##		  ThermalChecks function	       ##
#########################################################
# Checks all thermal components	- fans, temperatures,	#
# etc. Reports details of all failed components.  	#
#########################################################

function ThermalChecks () {

# check fans / temps
	GLOBAL_THERMAL_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.1 2>/dev/null | cut -f4 -d ' ')
	
	case "$GLOBAL_THERMAL_STATUS" in
		1)
		THERMAL_STATUS_TEXT="UNKNOWN: Checking thermal conditions is not supported for $HOST_NAME! Make sure SNMP is properly configured and that all Insight Management Agents are installed.\n"
		THERMAL_EXIT_CODE=3
		;;
		2) # Thermal status is okay - we are only warning the user of anything that is degraded/failed
		THERMAL_EXIT_CODE=0
		;;
		3|4) # We have failed /degraded status - we need to check individual components - temperatures AND fans

		# ----------------------------------------
		# ----- Check our temperatures first -----
		# ----------------------------------------
		
		GLOBAL_TEMP_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.3 2>/dev/null | cut -f4 -d ' ')
		THERMAL_STATUS_TEXT=""
		case "$GLOBAL_TEMP_STATUS" in
			1) # A status of 1 is "unknown", but should be implicit if GLOBAL_THERMAL_STATUS is 1.
			TEMP_EXIT_CODE=3
			;;
			2) # A status of 2 is okay, so we don't need to check anything
			TEMP_EXIT_CODE=0
			;;
			3)
			THERMAL_STATUS_TEXT="CRITICAL:"
			TEMPERATURE_CONDITIONS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.8.1.6 2>/dev/null)
			
			# First, filter our conditions for only sensors in degraded state
			SENSORS_DEGRADED=$(echo "$TEMPERATURE_CONDITIONS" | grep "INTEGER: 3")
			# Determine how many bad sensors we have
			NUM_SENSORS_DEGRADED=$(echo "$SENSORS_DEGRADED" | wc -l)
			
			CURRENT_SENSOR=1
			
			while [ $CURRENT_SENSOR -le $NUM_SENSORS_DEGRADED ]; do
				SENSOR_NUM=$(echo "$SENSORS_DEGRADED" | cut -f1 -d ' ' | cut -f10 -d '.' | awk NR==$CURRENT_SENSOR)
				SENSOR_TYPE=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.8.1.3.0.$SENSOR_NUM 2>/dev/null | cut -f4 -d ' ')
				SENSOR_TEMP=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.8.1.4.0.$SENSOR_NUM 2>/dev/null | cut -f4 -d ' ')
				SENSOR_THRESHOLD=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.8.1.5.0.$SENSOR_NUM 2>/dev/null | cut -f4 -d ' ')

				case "$SENSOR_TYPE" in
					1) SENSOR_DESCR="other";;
					2) SENSOR_DESCR="unknown";;
					3) SENSOR_DESCR="system";;
					4) SENSOR_DESCR="systemBoard";;
					5) SENSOR_DESCR="ioBoard";;
					6) SENSOR_DESCR="cpu";;
					7) SENSOR_DESCR="memory";;
					8) SENSOR_DESCR="storage";;
					9) SENSOR_DESCR="removableMedia";;
					10) SENSOR_DESCR="powerSupply" ;;
					11) SENSOR_DESCR="ambient";;
					12) SENSOR_DESCR="chassis";;
					13) SENSOR_DESCR="bridgeCard";;
				esac
				
				# Make sure we list all sensors with problems, sequentially
				if [ $CURRENT_SENSOR -lt $NUM_SENSORS_DEGRADED ]; then
					THERMAL_STATUS_TEXT=$(echo "$THERMAL_STATUS_TEXT" "$SENSOR_DESCR temperature is $SENSOR_TEMP degrees Celsius - system will shut down at $SENSOR_THRESHOLD degrees Celsius!, ")
				else
					THERMAL_STATUS_TEXT=$(echo "$THERMAL_STATUS_TEXT" "$SENSOR_DESCR temperature is $SENSOR_TEMP degrees Celsius - system will shut down at $SENSOR_THRESHOLD degrees Celsius! ")
				fi
			
				CURRENT_SENSOR=$[ $CURRENT_SENSOR+1 ]

			done
			
			TEMP_EXIT_CODE=2
			;;
			4) # A status of 4 is one that will shut the system down, so we don't need to handle it
			;;
		esac
		
		# -------------------------------
		# ----- Check our fans next -----
		# -------------------------------
		GLOBAL_FAN_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.4 2>/dev/null | cut -f4 -d ' ')
		FAN_CONDITIONS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.7.1.9 2>/dev/null )
		
		case "$GLOBAL_FAN_STATUS" in
			1) # This should be implicit by the global thermal status - we don't need details
			FAN_EXIT_CODE=3
			;;
			2) # This should be implicit by the global thermal status - we don't need details
			FAN_EXIT_CODE=0
			;;
			3|4) # Apparently an individual component can be degraded but this is not set as degraded
			# So maybe we should not use the global status?
			
			if [ $GLOBAL_FAN_STATUS -eq 3 ]; then
				THERMAL_STATUS_TEXT="WARNING:"
				FAN_EXIT_CODE=1
			else
				# Theoretically, we will never see this if it is 4 - the system will shut down
				#	UNLESS 1.3.6.1.4.1.232.6.2.6.2.0 = 2
				THERMAL_STATUS_TEXT="CRITICAL:"
				FAN_EXIT_CODE=2
			fi
		
			# First, filter our conditions for only fans in degraded state
			FANS_AFFECTED=$(echo "$FAN_CONDITIONS" | egrep "INTEGER: 3|INTEGER: 4")
			# Determine how many degraded fans we have
			NUM_FANS_AFFECTED=$(echo "$FANS_AFFECTED" | wc -l)
						
			CURRENT_FAN=1
		
			while [ $CURRENT_FAN -le $NUM_FANS_AFFECTED ]; do
				# Looking at CURRENT_FAN (1st, 2nd) system fan failed (out of NUM_FANS_AFFECTED fans)
				FAN_NUM=$(echo "$FANS_AFFECTED" | cut -f1 -d ' ' | cut -f10 -d '.' | awk NR==$CURRENT_FAN)
				# 	We need to differentiate if it's status was degraded or failed
				FAN_STATUS=$(echo "$FANS_AFFECTED" | cut -f4 -d ' ' | awk NR==$CURRENT_FAN)
				# 	We need it's location code
				FAN_LOCATION=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.7.1.3.0.$CURRENT_FAN 2>/dev/null | cut -f4 -d ' ')
				
				# Get some descriptive text for the fan's location
				case "$FAN_LOCATION" in
					1) FAN_DESCR="other";;
					2) FAN_DESCR="unknown";;
					3) FAN_DESCR="system";;
					4) FAN_DESCR="systemBoard";;
					5) FAN_DESCR="ioBoard";;
					6) FAN_DESCR="cpu";;
					7) FAN_DESCR="memory";;
					8) FAN_DESCR="storage";;
					9) FAN_DESCR="removableMedia";;
					10) FAN_DESCR="powerSupply" ;;
					11) FAN_DESCR="ambient";;
					12) FAN_DESCR="chassis";;
					13) FAN_DESCR="bridgeCard";;
				esac

				# Report whether the status was failed/degraded
				if [ $FAN_STATUS -eq 3 ]; then
					FAN_STATUS_TEXT="is degraded"
				else
					FAN_STATUS_TEXT="has failed"
				fi
			
				# Theoretically, the MIBs state that degraded status means the fan is redundant; failed means it is not
				# 	However, I see no reason to NOT double-check that information!
				FAN_REDUNDANCY=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.7.1.7.0.$PSU_NUM 2>/dev/null | cut -f4 -d ' ')
				case "$FAN_REDUNDANCY" in
					2) FAN_REDUNDANCY_TEXT="NOT redundant";;
					3) FAN_REDUNDANCY_TEXT="redundant";;
				esac

				# Determine if the fan can be hot-swapped (so any user looking at the output knows if they'll have to take the system down
				IS_FAN_HOT_SWAPPABLE=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.6.7.1.10.0.$PSU_NUM 2>/dev/null | cut -f4 -d ' ')
				case "$IS_FAN_HOT_SWAPPABLE" in
					2) FAN_SWAPPABLE_TEXT="NOT hot-swappable";;
					3) FAN_SWAPPABLE_TEXT="hot-swappable";;
				esac

				# Report on the fan's details - providing a way to separate each fan by a ","
				if [ $CURRENT_FAN -lt $NUM_FANS_AFFECTED ]; then
					THERMAL_STATUS_TEXT=$(echo "$THERMAL_STATUS_TEXT" "System Fan # $FAN_LOCATION ($FAN_DESCR) $FAN_STATUS_TEXT (fan is $FAN_REDUNDANCY_TEXT, $FAN_SWAPPABLE_TEXT), ")
				else
					THERMAL_STATUS_TEXT=$(echo "$THERMAL_STATUS_TEXT" "System Fan # $FAN_LOCATION ($FAN_DESCR) $FAN_STATUS_TEXT (fan is $FAN_REDUNDANCY_TEXT, $FAN_SWAPPABLE_TEXT). ")
				fi
				
				CURRENT_FAN=$[ $CURRENT_FAN+1 ]
			
			done

			;;
		esac

		# If either component was critical, we want Nagios to return critical
		if [ $FAN_EXIT_CODE -o $TEMP_EXIT_CODE -eq 2 ]; then
			THERMAL_EXIT_CODE=2
		else
			# No component was higher than warning status, so return warning to Nagios
			THERMAL_EXIT_CODE=1
		fi
		;;
	esac

#	if [ $THERMAL_EXIT_CODE -eq 0]; then
	# If either of the individual return codes was OK, then CPU Fan Status codes must be the failing component
	#	I currently do not have any checks implemented for CPU Fan Status, as it appears the "agent" for this is not common
#		THERMAL_STATUS_TEXT="UNKNOWN: CPU Fan Status may be failed/degraded. This plugin does not support checking of these items.\n"
#	fi

	EXIT_STRING="$EXIT_STRING $THERMAL_STATUS_TEXT"
	return $THERMAL_EXIT_CODE
}


#########################################################
##		PowerSupplyCheck function 	       ##
#########################################################
# Checks all power supplies. Returns status of all	#
# failed components.					#
#########################################################

function PowerSupplyCheck () {

	GLOBAL_PSU_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.9.1 2>/dev/null | cut -f4 -d ' ')
	PSU_CONDITIONS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.9.3.1.4 2>/dev/null)
	
	case "$GLOBAL_PSU_STATUS" in
		1) 
		EXIT_STRING="UNKNOWN: Checking power supplies is not supported for $HOST_NAME! Make sure SNMP is properly configured and that all Insight Management Agents are installed.\n"
		PSU_EXIT_CODE=3
		;;
		2) # Power supplies are okay - we are only warning the user of anything that is degraded/failed
		PSU_EXIT_CODE=0
		;;
		3|4)
		
		if [ $GLOBAL_PSU_STATUS -eq 3 ]; then
			EXIT_STRING="$EXIT_STRING WARNING:"
			PSU_EXIT_CODE=1
		else
			EXIT_STRING="$EXIT_STRING CRITICAL:"
			PSU_EXIT_CODE=2
		fi

		# First, filter our conditions for only PSUs in degraded state
		PSUs_AFFECTED=$(echo "$PSU_CONDITIONS" | egrep "INTEGER: 3|INTEGER: 4")
		
		# Determine how many PSUs we have that are degraded
		NUM_PSUs_AFFECTED=$(echo "$PSUs_AFFECTED" | wc -l)
		
		CURRENT_PSU=1
		
		# For each degraded PSU, output it's status
		while [ $CURRENT_PSU -le $NUM_PSUs_AFFECTED ]; do
			# Looking at CURRENT_PSU (1st, 2nd) power supply failed (out of NUM_PSUs_AFFECTED power supplies)
			# 	We need it's location code (is it PSU 3, PSU 2, etc.?)...
			PSU_NUM=$(echo "$PSUs_AFFECTED" | cut -f1 -d ' ' | cut -f10 -d '.' | awk NR==$CURRENT_PSU)
			# 	We need to differentiate if it's status was degraded or failed
			PSU_STATUS=$(echo "$PSUs_AFFECTED" | cut -f4 -d ' ' | awk NR==$CURRENT_PSU)
			# 	And finally, we can get the error code for the current power supply
			PSU_ERROR_CODE=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.9.3.1.5.0.$PSU_NUM 2>/dev/null | cut -f4 -d ' ')
			
			case "$PSU_ERROR_CODE" in
				1) PSU_ERROR_DESCR="No Error";;
				2) PSU_ERROR_DESCR="2 (generalFailure)";;
				3) PSU_ERROR_DESCR="3 (bistFailure)";;
				4) PSU_ERROR_DESCR="4 (fanFailure)";;
				5) PSU_ERROR_DESCR="5 (tempFailure)";;
				6) PSU_ERROR_DESCR="6 (interlockOpen)";;
				7) PSU_ERROR_DESCR="7 (epromFailed)";;
				8) PSU_ERROR_DESCR="8 (vrefFailed)";;
				9) PSU_ERROR_DESCR="9 (dacFailed)";;
				10) PSU_ERROR_DESCR="10 (ramTestFailed)";;
				11) PSU_ERROR_DESCR="11 (voltageChannelFailed)";;
				12) PSU_ERROR_DESCR="12 (orringdiodeFailed)";;
				13) PSU_ERROR_DESCR="13 (brownOut)";;
				14) PSU_ERROR_DESCR="14 (giveupOnStartup)";;
				15) PSU_ERROR_DESCR="15 (nvramInvalid)";;
				16) PSU_ERROR_DESCR="16 (calibrationTableInvalid)";;
			esac

			# Report whether the status was failed/degraded
			if [ $PSU_STATUS -eq 3 ]; then
				PSU_STATUS_TEXT="is degraded"
			else
				PSU_STATUS_TEXT="has failed"
			fi
			
			# Determine redundant status of current psu
			PSU_REDUNDANCY=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.9.3.1.9.0.$PSU_NUM 2>/dev/null | cut -f4 -d ' ')
			
			case "$PSU_REDUNDANCY" in
				2) PSU_REDUNDANCY_TEXT="Non-redundant";;
				3) PSU_REDUNDANCY_TEXT="Redundant";;
				*) PSU_REDUNDANCY_TEXT=""
			esac
			
			# Make sure we list all PSU's affected, separating each by a ","
			if [ $CURRENT_PSU -lt $NUM_PSUs_DEGRADED ]; then
				EXIT_STRING="$EXIT_STRING $PSU_REDUNDANCY_TEXT Power Supply # $CURRENT_PSU $PSU_STATUS_TEXT with error $PSU_ERROR_DESCR, "
			else
				EXIT_STRING="$EXIT_STRING $PSU_REDUNDANCY_TEXT Power Supply # $CURRENT_PSU $PSU_STATUS_TEXT with error $PSU_ERROR_DESCR. "
			fi
			
			CURRENT_PSU=$[ $CURRENT_PSU+1 ]
			
		done
		;;
	esac

	return 	$PSU_EXIT_CODE
}


#########################################################
##		   DriveChecks function		       ##
#########################################################
# Checks all hard drives AND drive controllers. 	#
# Returns details on any failed components.		#
#########################################################

function DriveChecks () {

	CONTROLLERS_AFFECTED=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.2.1.1.6 2>/dev/null | egrep "INTEGER: 3|INTEGER: 4")
	NUM_CONTROLLERS_AFFECTED=$(echo "$CONTROLLERS_AFFECTED" | wc -l)

	CURRENT_CONTROLLER=1
	while [ $CURRENT_CONTROLLER -le $NUM_CONTROLLERS_AFFECTED ]; do
		CONTROLLER_INDEX=$(echo "$CONTROLLERS_AFFECTED" | cut -f1 -d ' ' | cut -f9 -d '.' | awk NR==$CURRENT_CONTROLLER)
		CONTROLLER_LOCATION=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.2.1.1.20.$CONTROLLER_INDEX 2>/dev/null | cut -f4 -d ':'  | tr -d '"')
		CONTROLLER_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.2.1.1.6.$CONTROLLER_INDEX 2>/dev/null | cut -f4 -d ' ')

		LOGICAL_DRIVE_ERROR=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.3.1.1.11 2>/dev/null)
		PHYSICAL_DRIVE_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.5.1.1.37 2>/dev/null)
		DRIVE_STATUS_TEXT=""

		case "$CONTROLLER_STATUS" in
			1) # Unknown
			DRIVE_STATUS_TEXT="UNKNOWN: Checking drive conditions is not supported for $HOST_NAME! Make sure SNMP is properly configured and that all Insight Management Agents are installed.\n"
			DRIVE_EXIT_CODE=3
			;;
			2) # Everything is okay, no need to report anything
			DRIVE_EXIT_CODE=0
			;;
			3) # One or more components may be failed, but not all. The array controller is still usable but degraded
			DRIVE_STATUS_TEXT="Array Controller at$CONTROLLER_LOCATION is degraded. REASON -"

			LOGICAL_DRIVES_AFFECTED=$(echo "$LOGICAL_DRIVE_ERROR" | egrep "INTEGER: 3|INTEGER: 4")
			NUM_LOGICAL_DRIVES_AFFECTED=$(echo "$LOGICAL_DRIVES_AFFECTED" | wc -l)
			
			#------------------------------------
			#----- Check out logical drives -----
			#------------------------------------
			CURRENT_LOGICAL_DRIVE=1
			while [ $CURRENT_LOGICAL_DRIVE -le $NUM_LOGICAL_DRIVES_AFFECTED ]; do
				# Determine which drive number in the array
				LOGICAL_DRIVE_NUM=$(echo "$LOGICAL_DRIVES_AFFECTED" | cut -f1 -d ' ' | cut -f10 -d '.' | awk NR==$CURRENT_LOGICAL_DRIVE)
				# Determine whether or not this drive is degraded/failed
				LOGICAL_DRIVE_STATUS=$(echo "$LOGICAL_DRIVES_AFFECTED" | cut -f4 -d ' ' | awk NR==$CURRENT_LOGICAL_DRIVE)
				# Determine some basic identities/properties of this drive
				LOGICAL_DRIVE_TEXT=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.3.1.1.14.$CONTROLLER_INDEX.$LOGICAL_DRIVE_NUM 2>/dev/null | cut -f4 -d ':' | tr -d '"')
				LOGICAL_DRIVE_ERROR=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.3.1.1.4.$CONTROLLER_INDEX.$LOGICAL_DRIVE_NUM 2>/dev/null | cut -f4 -d ' ')
				
				case "$LOGICAL_DRIVE_ERROR" in
					1) LOGICAL_DRIVE_ERROR_DESCR="1 (other)";;
					2) LOGICAL_DRIVE_ERROR_DESCR="2 (ok)";;
					3) LOGICAL_DRIVE_ERROR_DESCR="3 (failed)";;
					4) LOGICAL_DRIVE_ERROR_DESCR="4 (unconfigured)";;
					5) LOGICAL_DRIVE_ERROR_DESCR="5 (recovering)";;
					6) LOGICAL_DRIVE_ERROR_DESCR="6 (readyForRebuild)";;
					7) LOGICAL_DRIVE_ERROR_DESCR="7 (rebuilding)";;
					8) LOGICAL_DRIVE_ERROR_DESCR="8 (wrongDrive)";;
					9) LOGICAL_DRIVE_ERROR_DESCR="9 (badConnect)";;
					10) LOGICAL_DRIVE_ERROR_DESCR="10 (overheating)";;
					11) LOGICAL_DRIVE_ERROR_DESCR="11 (shutdown)";;
					12) LOGICAL_DRIVE_ERROR_DESCR="12 (expanding)";;
					13) LOGICAL_DRIVE_ERROR_DESCR="13 (notAvailable)";;
					14) LOGICAL_DRIVE_ERROR_DESCR="14 (queuedForExpansion)";;
				esac
				
				# Report whether the status was failed/degraded
				if [ $LOGICAL_DRIVE_STATUS -eq 3 ]; then
					LOGICAL_DRIVE_STATUS_TEXT="is degraded"
				else
					LOGICAL_DRIVE_STATUS_TEXT="has failed"
				fi
				
				# Make sure we list all drives affected, separating each by a ","
				if [ $CURRENT_LOGICAL_DRIVE -lt $NUM_LOGICAL_DRIVES_AFFECTED ]; then
					DRIVE_STATUS_TEXT=$(echo "$DRIVE_STATUS_TEXT" "Logical Drive$LOGICAL_DRIVE_TEXT $LOGICAL_DRIVE_STATUS_TEXT with error $LOGICAL_DRIVE_ERROR_DESCR, ")
				else
					DRIVE_STATUS_TEXT=$(echo "$DRIVE_STATUS_TEXT" "Logical Drive$LOGICAL_DRIVE_TEXT $LOGICAL_DRIVE_STATUS_TEXT with error $LOGICAL_DRIVE_ERROR_DESCR. ")
				fi
				
				CURRENT_LOGICAL_DRIVE=$[ $CURRENT_LOGICAL_DRIVE+1 ]
				
			done
			
			#-------------------------------------
			#----- Check out physical drives -----
			#-------------------------------------
			PHYSICAL_DRIVES_AFFECTED=$(echo "$PHYSICAL_DRIVE_STATUS" | egrep "INTEGER: 3|INTEGER: 4")
			NUM_PHYSICAL_DRIVES_AFFECTED=$(echo "$PHYSICAL_DRIVES_AFFECTED" | wc -l)

			CURRENT_PHYSICAL_DRIVE=1
			while [ $CURRENT_PHYSICAL_DRIVE -le $NUM_PHYSICAL_DRIVES_AFFECTED ]; do
				# Determine which drive number in the array
				PHYSICAL_DRIVE_NUM=$(echo "$PHYSICAL_DRIVES_AFFECTED" | cut -f1 -d ' ' | cut -f10 -d '.' | awk NR==$CURRENT_PHYSICAL_DRIVE)
				# Determine whether or not this drive is degraded/failed
				PHYSICAL_DRIVE_STATUS=$(echo "$PHYSICAL_DRIVES_AFFECTED" | cut -f4 -d ' ' | awk NR==$CURRENT_PHYSICAL_DRIVE)
				# Determine some basic identities/properties of this drive
				PHYSICAL_DRIVE_BAY=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.5.1.1.64.$CONTROLLER_INDEX.$PHYSICAL_DRIVE_NUM 2>/dev/null | cut -f4 -d ':' | tr -d '"')
				PHYSICAL_DRIVE_ERROR=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.5.1.1.6.$CONTROLLER_INDEX.$PHYSICAL_DRIVE_NUM 2>/dev/null | cut -f4 -d ' ')
				# PHYSICAL_DRIVE_MODEL=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.3.2.5.1.1.3.0.$CURRENT_PHYSICAL_DRIVE 2>/dev/null | gawk -F: '{ print $4 }'))
			
				case "$PHYSICAL_DRIVE_ERROR" in
					1) PHYSICAL_DRIVE_ERROR_DESCR="1 (other)";;
					2) PHYSICAL_DRIVE_ERROR_DESCR="2 (ok)";;
					3) PHYSICAL_DRIVE_ERROR_DESCR="3 (failed)";;
					4) PHYSICAL_DRIVE_ERROR_DESCR="4 (predictiveFailure)";;
				esac
					
				if [ $PHYSICAL_DRIVE_STATUS -eq 3 ]; then
					PHYSICAL_DRIVE_STATUS_TEXT="degraded"
				else
					PHYSICAL_DRIVE_STATUS_TEXT="failed"
				fi

				# Make sure we list all drives affected, separating each by a ","
				if [ $CURRENT_PHYSICAL_DRIVE -lt $NUM_PHYSICAL_DRIVES_AFFECTED ]; then
					DRIVE_STATUS_TEXT=$(echo "$DRIVE_STATUS_TEXT" "$PHYSICAL_DRIVE_BAY is $PHYSICAL_DRIVE_STATUS_TEXT with error $PHYSICAL_DRIVE_ERROR_DESCR, ")
				else
					DRIVE_STATUS_TEXT=$(echo "$DRIVE_STATUS_TEXT" "$PHYSICAL_DRIVE_BAY is $PHYSICAL_DRIVE_STATUS_TEXT with error $PHYSICAL_DRIVE_ERROR_DESCR. ")
				fi
				
				CURRENT_PHYSICAL_DRIVE=$[ $CURRENT_PHYSICAL_DRIVE+1 ]
			done
			
			#	Currently, this function checks drives in much the way that Systems Management would. 
			# Controller condition is based on the logical drive status, and logical drive status 
			# is based on physical drive status. The error codes  returned by this plugin should match
			# the Systems Management global page. 
			# The problem with this approach is that if a physical drive is failed, the global status
			# is not considered critical. But we want Nagios to alert us!

			#	So here, rather than assume a warning status only, I want to report the worst
			# condition reported from all the subcomponents. This means eventhough the controller might be
			# okay - redundancy is in effect and the server is operating - we can still get notified of a failed
			# drive and have the entire thing treated as critical (since at least 1 subcomponent
			if [ $LOGICAL_DRIVE_STATUS -eq 4 ] || [ $PHYSICAL_DRIVE_STATUS -eq 4 ]; then
				DRIVE_STATUS_TEXT="CRITICAL: $DRIVE_STATUS_TEXT\n"
				DRIVE_EXIT_CODE=2
			else
				if [ $LOGICAL_DRIVE_STATUS -eq 3 ] || [ $PHYSICAL_DRIVE_STATUS -eq 3 ]; then
				# Something has to have flagged critical
				# We know all components are at warning
					DRIVE_STATUS_TEXT="WARNING: $DRIVE_STATUS_TEXT\n"
				else
					DRIVE_STATUS_TEXT="WARNING: There appears to be a problem on the controller at $CONTROLLER_LOCATION, but no drives are effected. Possible causes are outdated firmware, a tape drive needs cleaned, etc. Check Systems Management homepage for more details.\n"
				fi
				DRIVE_EXIT_CODE=1
			fi
			;;
			4) # A "failed" state means all individual components have "failed" - if any 1 component is "degraded" the system returns a degraded instead
			DRIVE_STATUS_TEXT="CRITICAL: Array Controller at $CONTROLLER_LOCATION has failed!\n"
			DRIVE_EXIT_CODE=2
			;;
		esac

		CURRENT_CONTROLLER=$[ $CURRENT_CONTROLLER+1 ]

	done
	
	EXIT_STRING="$EXIT_STRING $DRIVE_STATUS_TEXT"
	return $DRIVE_EXIT_CODE
}


#########################################################
##		   MemoryCheck function		       ##
#########################################################
# Checks memory sticks for any errors they might be	#
#	reporting to the system. I hope to be able to	#
#	implement more checks in the future but did	#
#	not find much useful information in the Compaq  #
#	MIBs for memory information.			#
#########################################################

function MemoryCheck () {
	MEMORY_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.3.2.0 2>/dev/null | cut -f4 -d ' ')
	MEMORY_EXIT_CODE=0
	
	case "$MEMORY_STATUS" in
		1) 
		MEMORY_EXIT_CODE=3
		EXIT_STRING="$EXIT_STRING UNKNOWN: Condition of correctable memory is undetermined for this machine.\n"
		;;
		3|4) 
		# Determine how many memory errors we have gotten on the memory chips
		NUM_MEM_ERRORS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.3.3 2>/dev/null | cut -f4 -d ' ')

		# Use the HP Agents to determine how many memory errors are critical for the sticks installed
		MEM_CRITICAL=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.2.3.5 2>/dev/null | cut -f4 -d ' ')

		# Set our warning at 80% of the critical value returned by the HP Agents
		MEM_WARNING=$(echo $MEM_CRITICAL*0.8/1 | bc)

		if [ $NUM_MEM_ERRORS -ge $MEM_CRITICAL ]; then
			EXIT_STRING="$EXIT_STRING CRITICAL: $NUM_MEM_ERRORS memory errors occured! Please replace the faulty memory!\n"
			MEMORY_EXIT_CODE=2
		else
			if [ $NUM_MEM_ERRORS -ge $MEM_WARNING ]; then
				EXIT_STRING="$EXIT_STRING WARNING: $NUM_MEM_ERRORS memory errors occured! Memory will need to be replaced soon. (CRITICAL = $MEM_CRITICAL)\n"
				MEMORY_EXIT_CODE=1
			fi
		fi
		;;
	esac
	
	return $MEMORY_EXIT_CODE
}


#########################################################
##			  MAIN CODE		       ##
#########################################################

# Check that all required binaries for the script are available
# 	EXIT with an UNKNOWN status if not
binaries="snmpwalk awk cut grep wc"

for required_binary in $binaries; 
do
	which $required_binary > /dev/null
	if [ "$?" != '0' ];then
		printf "UNKNOWN: $APPNAME: No usable '$required_binary' binary in '$PATH'\n"
		exit 3
	fi
done

# Parse our options as passed, and make sure things are peachy
while getopts "C:H:hV" OPTION;
do
	case $OPTION in
		"C") 
		COMMUNITY=$OPTARG 
		;;
		"H") 
		HOST_NAME=$OPTARG
		;;
		"h") 
		print_help
		exit $?
		;;
		"V") 
		printf "$APPNAME - version $VERSION\n"
		exit $EXIT_CODE
		;;
	esac
done

# Make sure all necessary arguments were given; EXIT with an UNKNOWN status if not
if [ -z "$COMMUNITY" ] || [ -z "$HOST_NAME" ];then
	EXIT_STRING="UNKNOWN: Hostname and/or Community variables have not been set!\n"
	EXIT_CODE=3
else
	# Determine health of most major components (hard drives are under a differet MIB tree and are not included)
	COMPONENT_SYSTEM_STATUS=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.6.1.3 2>/dev/null | cut -f4 -d ' ')
	if [ $? -ne 0 ]; then
		#Check  for server response - is SNMP even setup okay?
		EXIT_STRING="WARNING: No SNMP response from $HOST_NAME! Make sure host is up and SNMP is configured properly.\n"
		EXIT_CODE=1
	else
			
		case "$COMPONENT_SYSTEM_STATUS" in
			1) # A value of 1 indicates that the system agents aren't working or SNMP could be broke - no sense going further!
			EXIT_STRING="UNKNOWN: Check your SNMP configuration and be sure all Insight Agents are installed.\n"
			EXIT_CODE=3
			;;
			2) # A value of 2 means everything is sweet with regular components; we don't know about drive status though
			DriveChecks
			DRIVE_STATUS=$?

			if [ $DRIVE_STATUS -gt 0 ]; then
			# Eventhough other components are okay, drives are not - let's report their condition
				EXIT_CODE=$DRIVE_STATUS
			else
			# Everything is fine - let's output some info. on the server
				SERVER_SERIAL_NUMBER=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.2.2.2.5 2>/dev/null | cut -f4 -d ':' | tr -d '"')
				SERVER_MODEL_NUMBER=$(snmpwalk -v 2c -c $COMMUNITY $HOST_NAME .1.3.6.1.4.1.232.2.2.4.2 2>/dev/null | cut -f4 -d ':' | tr -d '"')
				EXIT_STRING="OK: All system components are normal. Server is a$SERVER_MODEL_NUMBER with serial #$SERVER_SERIAL_NUMBER.\n"
				EXIT_CODE=0
			fi
			;;
			3|4) # 3 is degraded status, 4 is failed - we need to investigate for more details
			# Let's run checks of all the components that we can, and report details ony on warnings/failures.
			# This builds a culmulative output, in the event that more than 1 component has failed
			ThermalChecks
			PowerSupplyCheck
			MemoryCheck
			DriveChecks

			if [ $COMPONENT_SYSTEM_STATUS -eq 3 ]; then
				EXIT_CODE=1
			else
				EXIT_CODE=2
			fi
			;;
		esac
	fi
fi

printf "$EXIT_STRING"

exit $EXIT_CODE
You do not have the required permissions to view the files attached to this post.
mguthrie
Posts: 4380
Joined: Mon Jun 14, 2010 10:21 am

Re: Plugin Returning NULL

Post by mguthrie »

Can you post the command definition and service definition that this check is using?
lamin
Posts: 177
Joined: Thu Oct 28, 2010 6:59 am

Re: Plugin Returning NULL

Post by lamin »

define service {
host_name DTW-VAN-VSM2
service_description HPHardware-Critical-Status
use generic-service
check_command check_insigth_agents!-H hostip -C community
max_check_attempts 5
check_interval 5
retry_interval 10
check_period 24x7
notification_interval 1200
notification_period 24x7
contacts nagiosadmin
contact_groups VantageGroup
register 1
}
scottwilkerson
DevOps Engineer
Posts: 19396
Joined: Tue Nov 15, 2011 3:11 pm
Location: Nagios Enterprises
Contact:

Re: Plugin Returning NULL

Post by scottwilkerson »

we also need the command definition

A screenshot is fine :lol:
Former Nagios employee
Creator:
Human Design Website
Get Your Human Design Chart
lamin
Posts: 177
Joined: Thu Oct 28, 2010 6:59 am

Re: Plugin Returning NULL

Post by lamin »

Here it is.
You do not have the required permissions to view the files attached to this post.
scottwilkerson
DevOps Engineer
Posts: 19396
Joined: Tue Nov 15, 2011 3:11 pm
Location: Nagios Enterprises
Contact:

Re: Plugin Returning NULL

Post by scottwilkerson »

Can you run this from the command line as the nagios user?

Code: Select all

su nagios -c '/usr/local/nagios/libexec/check_insight_agents -H hostip -C community'
what are the permissions on?

Code: Select all

ls -l /usr/local/nagios/libexec/check_insight_agents
Former Nagios employee
Creator:
Human Design Website
Get Your Human Design Chart
lamin
Posts: 177
Joined: Thu Oct 28, 2010 6:59 am

Re: Plugin Returning NULL

Post by lamin »

I think the permission is ok (see attachment). However, I am assuming that the pluging is looking for a directory within the code. By the way i may be wrong I am not a good coder.
You do not have the required permissions to view the files attached to this post.
lamin
Posts: 177
Joined: Thu Oct 28, 2010 6:59 am

Re: Plugin Returning NULL

Post by lamin »

see attachment
You do not have the required permissions to view the files attached to this post.
scottwilkerson
DevOps Engineer
Posts: 19396
Joined: Tue Nov 15, 2011 3:11 pm
Location: Nagios Enterprises
Contact:

Re: Plugin Returning NULL

Post by scottwilkerson »

It seems to be working fine from the command prompt, the only thing I could see that would cause that is nagios take the last line output and the exit code th delive what you see in the display

If this 3rd party plugin is sending a blank line last before exiting it will be null

You may need to contact the creator of the plugin, his email is in the top of the script along with this warning
# I readily admit that the plugins have had #
# limited testing in our own environment
, but we did #
# have a horrible old Compaq server that I was able to #
# use to test a number of scenarios. It's multiple #
# hardware failures actually encouraged me to make sure #
# the plugin could report more than 1 failed component. #