SNMP Monitoring - Status Change Configuration

Post by treesquid »

Nagios XI Version: 5.5.7

I'm attempting to create some SNMP alerts for HP hardware that we have (DL360p G8 servers) utilizing the SNMP Walk wizard. I can get the service check created (as in successful recognition of the OID and supplying of a value from the OID), but i can't get the status (Ok/Warning/Critical) to change when the value changes.

Here's a screenshot of the how i configured it currently. To note there are actually more values i'd want to add to Warning and Critical, but just for now i want to just get it to successfully change state for at least one value.
SNMPWizardConfiguration.PNG
Bay 1 has a status of 4 because i have the power cable unplugged for testing purposes. Even though i stated the 4 value in the Critical Field it's showing as Warning
statuschecks.PNG
Here's the command used by the service check. To note i've attempted to put ** , '' , and "" around each of the numbers to see if that'd change anything and that was not successful.
check_xi_service_snmp! -p 161 -o enterprises.232.6.2.9.3.1.4.1.1 -C dcopublic -P 2c -m CPQHLTH-MIB -w 3 -c 4

Here's info on the OID i'm attempting to utilize
OIDinfo.PNG
You do not have the required permissions to view the files attached to this post.
User avatar
tgriep
Madmin
Posts: 9190
Joined: Thu Oct 30, 2014 9:02 am

Re: SNMP Monitoring - Status Change Configuration

Post by tgriep »

The critical threshold setting it set to create a critical alert is the returned value is over 4 so if you want a critical at exactly 4, you would use this example.

Code: Select all

@4:4
And for the Warning threshold, use this

Code: Select all

@3:3
All other values will generate an OK alert.
Be sure to check out our Knowledgebase for helpful articles and solutions!
treesquid
Posts: 5
Joined: Wed Jul 10, 2019 12:10 pm

Re: SNMP Monitoring - Status Change Configuration

Post by treesquid »

Thank you for your response tgriep! i just tested this and it worked. Out of interest, was there any documentation i missed that had this answer in it?

Until i read your post a co-worker found the solution of putting -r 2 at the end of the command, which would make anything critical that wasn't a 2, (as far as we observed).
User avatar
tgriep
Madmin
Posts: 9190
Joined: Thu Oct 30, 2014 9:02 am

Re: SNMP Monitoring - Status Change Configuration

Post by tgriep »

My example came from of the Thresholds example on this site.
https://nagios-plugins.org/doc/guidelin ... HOLDFORMAT

The @ means that the data falls between the values separated by the : but when you set the value to the same number, it pretty much changes it to exactly equal that number.
Be sure to check out our Knowledgebase for helpful articles and solutions!