check_snmp help (missing MIB?)
jbennett
Post by jbennett »
I am trying to create a few more SNMP checks for our UPSs, but am running into issues. Please note: I am NOT trying to utilize traps. I've tried this in the past but they never seemd to update once issues had cleared so it was not a viable option for us.
When I look at the current checks, I see the following:
COMMAND: /usr/local/nagios/libexec/check_snmp -H 10.100.84.172 -C public -o upsBatteryStatus -m USHA-MIB -c 2:2
This check returns results successfully and all is fine. However,
Looking at the USHA-MIB file that I want to use, I see the following trap:
ushaUpsFailed       TRAP-TYPE
        ENTERPRISE      upsTrapGroup
        DESCRIPTION
                "SEVERE: The ups is not working fine."
        ::= 6
If I try and do the following:
COMMAND: /usr/local/nagios/libexec/check_snmp -H 10.100.84.172 -C public -o ushaUpsFailed -m USHA-MIB -c 2:2
It returns with:
OUTPUT: External command error: Error in packet
Reason: (noSuchName) There is no such variable name in this MIB.
Failed object: USHA-MIB::ushaUpsFailed
I went into the mib folder (/usr/share/snmp/mibs) to pull up the USHA-MIB.mib file and it doesn't exist...
So now I'm really confused. Per the first check command, we are looking at the MIB file titled USHA-MIB. However, it doesn't exist...so A) how is it looking at it B) where is it?
Re: check_snmp help (missing MIB?)
Post by Box293 »
This website is of great help:
http://www.net-snmp.org/wiki/index.php/ ... cations_09
For non-table objects ("scalars"), this instance subidentifier will always be '.0', and it must be included when making a GET request.
So your command should be:
/usr/local/nagios/libexec/check_snmp -H 10.100.84.172 -C public -o ushaUpsFailed.0 -m USHA-MIB -c 2:2
I added .0 to ushaUpsFailed
Does this fix your problem?
jbennett
Post by jbennett »
Failed object: USHA-MIB::ushaUpsFailed.0
Unfortunately, I'm still getting the same message.
sreinhardt
-fno-stack-protector
Post by sreinhardt »
I don't think this is going to work. One thing to note is that traps are not generally, its possible but not done often, made available via snmp get requests. Traps are intended to always be asynchronously sent from the "client" device to the receiver and not requested. Are there other non-trap-type or non-notification-type traps that might provide the same or similar information?
jbennett
Post by jbennett »
I'd really just prefer to use traps if at all possible, but they just don't seem to update. I can have a UPS send out a trap that a UPS has gone into bypass, but then once it's resolved, it doesn't update with a resolved message. It will stay there until there's another failure. I would think that there's a section within the MIB that I haven't edited correctly? Is that it or is this a normal issue?
sreinhardt
Actually if you would like the check to auto-resolve after a period of time, I would suggest setting a freshness check of say 1 hour, and use check_dummy to return OK with a message of "Cleared down trap" or something along those lines that gives you a clear message. All this will do is tell core to clear the trap if nothing has come in for 1 hour, allowing you to receive another alert when a new trap comes in as warning or critical. I believe this is what you were asking, but correct me if that is not the case.
rseiwert
Post by rseiwert »
Yes that Trap is not a MIB variable. You can poll MIB variables not traps. I typically test with snmpwalk and see what I get starting with enterprises. You will need the mib in your mibs directory.
You probably can query the upsBatteryGroupStatus object and get good feedback
upsBatteryGroupStatus OBJECT-TYPE
     SYNTAX     INTEGER {
           unknown(1),
           batteryNormal(2),
           batteryLow(3),
           batteryDepleted(4),
           batteryDischarging(5),
           batteryFailure(6)
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
               "The indication of the status in the UPS system's batteries."
     ::= { upsBatteryGroup 1 }
Grumpy Olde IT Guy
rseiwert
Post by rseiwert »
Also I would be checking and grabbing perf data from
Sorry to spam the forum but it looks like you can query a lot of useful info.
UpsInputGroupEntry ::=
    SEQUENCE {
             upsInputGroupLineIndex   PositiveInteger,
             upsInputGroupFrequency   NonNegativeInteger,
             upsInputGroupVoltage     NonNegativeInteger,
             upsInputGroupCurrent     NonNegativeInteger,
             upsInputGroupTruePower   NonNegativeInteger,
             upsInputGroupVoltageMax  NonNegativeInteger,
             upsInputGroupVoltageMin  NonNegativeInteger
UpsOutputGroupEntry ::=
    SEQUENCE {
             upsOutputGroupLineIndex   PositiveInteger,
             upsOutputGroupVoltage     NonNegativeInteger,
             upsOutputGroupCurrent     NonNegativeInteger,
             upsOutputGroupPower       NonNegativeInteger,
             upsOutputGroupPercentLoad INTEGER
upsTestBatteryTestResult OBJECT-TYPE
        SYNTAX  INTEGER {
                donePassed(1),
                doneWarning(2),
                doneError(3),
                aborted(4),
                inProgress(5),
                noTestsInitiated(6)
emdSatatusTemperature OBJECT-TYPE
        SYNTAX  INTEGER
        ACCESS read-only
        STATUS mandatory
        DESCRIPTION
                "The measurement of EMD temperature, in 0.1 degree"
        ::= { emdStatus 2}
emdSatatusHumidity OBJECT-TYPE
        SYNTAX  INTEGER
        ACCESS read-only
        STATUS mandatory
        DESCRIPTION
                "The measurement of EMD humidity, in 0.1 degree"
        ::= { emdStatus 3}
Grumpy Olde IT Guy
jbennett, did you try rseiwert's suggestion?