Constantly (well, often...) have to restart snmptt
snapon_admin
Post by snapon_admin »
Why?! For some reason, seemingly at random, snmp traps will stop being processed by Nagios all together. I have no idea why, but this is the scenario: We have 2 hosts in Nagios that we're monitoring traps on. There do appear to be more devices sending traps to Nagios, but not a lot (think maybe 20ish?) they just don't have anything associated with them. Every so often (every week/couple weeks or so) I'll get complaints from our operations team that there was an issue and they didn't receive a trap alert for it. So I'll log in and check the /var/logs/snmptt folder and notice that snmptt.log hasn't updated for x days. I restart snmptt and bam, the log starts growin and all the traps that we "missed" over the past x days start flooding in, generating alert after alert with old traps until it's caught up. I created a script to restart snmptt for me and tied it to a freshness check just to combat this, but even that seems to have failed me (though that's likely just because of my poor scripting skills) since I just checked our log and it hadn't updated in 2 days. My script ran, and snmptt was running, but no traps were coming in. I restarted snmptt myself, and the log started filling back up and alerts started coming in again.
Why does this happen, and is there anyway to correct it. I tried searching for other people having this issue, but couldn't find anything so I'm sort of at a loss at this point.
sreinhardt
-fno-stack-protector
Re: Constantly (well, often...) have to restart snmptt
Post by sreinhardt »
I hate to say it, but I'm glad you said this. I don't think I have observed this behavior before. Could you post the snmptt.ini file please? We will probably have to enable debug logging and let it fail to see what's actually going on, but we shall see.
snapon_admin
Sure thing.
# SNMPTT v1.3 Configuration File
# Linux / Unix
[General]
# Name of this system for $H variable.  If blank, system name will be the computer's
# hostname via Sys::Hostname.
snmptt_system_name =
# Set to either 'standalone' or 'daemon'
# standalone: snmptt called from snmptrapd.conf
# daemon: snmptrapd.conf calls snmptthandler
# Ignored by Windows.  See documentation
mode = daemon
# Set to 1 to allow multiple trap definitions to be executed for the same trap.
# Set to 0 to have it stop after the first match.
# This option should normally be set to 1.  See the section 'SNMPTT.CONF Configuration
# file Notes' in the SNMPTT documentation for more information.
# Note: Wildcard matches are only matched if there are NO exact matches.  This takes
#       into consideration the NODES list.  Therefore, if there is a matching trap, but
#       the NODES list prevents it from being considered a match, the wildcard entry will
#       only be used if there are no other exact matches.
multiple_event = 1
# SNMPTRAPD passes the IP address of device sending the trap, and the IP address of the
# actual SNMP agent.  These addresses could differ if the trap was sent on behalf of another
# device (relay, proxy etc).
# If DNS is enabled, the agent IP address is converted to a host name using a DNS lookup
# (which includes the local hosts file, depending on how the OS is configured).  This name
# will be used for: NODES entry matches, hostname field in logged traps (file / database),
# and the $A variable.  Host names on the NODES line will be resolved and the IP address
# will then be used for comparing.
# Set to 0 to disable DNS resolution
# Set to 1 to enable DNS resolution
dns_enable = 1
# Set to 0 to enable the use of FQDN (Fully Qualified Domain Names).  If a host name is
# passed to SNMPTT that contains a domain name, it will not be altered in any way by
# SNMPTT.  This also affects resolve_value_ip_addresses.
# Set to 1 to have SNMPTT strip the domain name from the host name passed to it.  For
# example, server01.domain.com would be changed to server01
# Set to 2 to have SNMPTT strip the domain name from the host name passed to it
# based on the list of domains in strip_domain_list
strip_domain = 1
# List of domain names that should be stripped when strip_domain is set to 2.
# List can contain one or more domains.  For example, if the FQDN of a host is
# server01.city.domain.com and the list contains domain.com, the 'host' will be
# set as server01.city.
strip_domain_list = <<END
domain.com
END
# Configures how IP addresses contained in the VALUE of the variable bindings are handled.
# This only applies to the values for $n, $+n, $-n, $vn, $+*, $-*.
# Set to 0 to disable resolving ip address to host names
# Set to 1 to enable resolving ip address to host names
# Note: net_snmp_perl_enable *must* be enabled.  The strip_domain settings influence the
# format of the resolved host name.  DNS must be enabled (dns_enable)
resolve_value_ip_addresses = 0
# Set to 1 to enable the use of the Perl module from the UCD-SNMP / NET-SNMP package.
# This is required for $v variable substitution to work, and also for some other options
# that are enabled in this .ini file.
# Set to 0 to disable the use of the Perl module from the UCD-SNMP / NET-SNMP package.
# Note: Enabling this with stand-alone mode can cause SNMPTT to run very slowly due to
#       the loading of the MIBS at startup.
net_snmp_perl_enable = 1
# This sets the best_guess parameter used by the UCD-SNMP / NET-SNMP Perl module for
# translating symbolic nams to OIDs and vice versa.
# For UCD-SNMP, and Net-SNMP 5.0.8 and previous versions, set this value to 0.
# For Net-SNMP 5.0.9, or any Net-SNMP with patch 722075 applied, set this value to 2.
# A value of 2 is equivalent to -IR on Net-SNMP command line utilities.
# UCD-SNMP and Net-SNMP 5.0.8 and previous may not be able to translate certain formats of
# symbolic names such as RFC1213-MIB::sysDescr.  Net-SNMP 5.0.9 or patch 722075 will allow
# all possibilities to be translated.  See the FAQ section in the README for more info
net_snmp_perl_best_guess = 0
# Configures how the OID of the received trap is handled when outputting to a log file /
# database.  It does NOT apply to the $O variable.
# Set to 0 to use the default of numerical OID
# Set to 1 to translate the trap OID to short text (symbolic form) (eg: linkUp)
# Set to 2 to translate the trap OID to short text with module name (eg: IF-MIB::linkUp)
# Set to 3 to translate the trap OID to long text (eg: iso...snmpTraps.linkUp)
# Set to 4 to translate the trap OID to long text with module name (eg:
# IF-MIB::iso...snmpTraps.linkUp)
# Note: -The output of the long format will vary depending on the version of Net-SNMP you
#        are using.
#       -net_snmp_perl_enable *must* be enabled
#       -If using database logging, ensure the trapoid column is large enough to hold the
#        entire line
translate_log_trap_oid = 0
# Configures how OIDs contained in the VALUE of the variable bindings are handled.
# This only applies to the values for $n, $+n, $-n, $vn, $+*, $-*.  For substitutions
# that include variable NAMES ($+n etc), only the variable VALUE is affected.
# Set to 0 to disable translating OID values to text (symbolic form)
# Set to 1 to translate OID values to short text (symbolic form) (eg: BuildingAlarm)
# Set to 2 to translate OID values to short text with module name (eg: UPS-MIB::BuildingAlarm)
# Set to 3 to translate OID values to long text (eg: iso...upsAlarm.BuildingAlarm)
# Set to 4 to translate OID values to long text with module name (eg:
# UPS-MIB::iso...upsAlarm.BuildingAlarm)
# For example, if the value contained: 'A UPS Alarm (.1.3.6.1.4.1.534.1.7.12) has cleared.',
# it could be translated to: 'A UPS Alarm (UPS-MIB::BuildingAlarm) has cleared.'
translate_value_oids = 1
# Configures how the symbolic enterprise OID will be displayed for $E.
# Set to 1, 2, 3 or 4.  See translate_value_oids options 1,2,3 and 4.
translate_enterprise_oid_format = 1
# Configures how the symbolic trap OID will be displayed for $O.
translate_trap_oid_format = 1
# Configures how the symbolic trap OID will be displayed for $v, $-n, $+n, $-* and $+*.
translate_varname_oid_format = 1
# Set to 0 to disable converting INTEGER values to enumeration tags as defined in the
# MIB files
# Set to 1 to enable converting INTEGER values to enumeration tags as defined in the
# MIB files
# Example: moverDoorState:open instead of moverDoorState:2
translate_integers = 1
# Allows you to set the MIBS environment variable used by SNMPTT
# Leave blank or comment out to have the systems enviroment settings used
# To have all MIBS processed, set to ALL
# See the snmp.conf manual page for more info
#mibs_environment = ALL
# Set what is used to separate variables when wildcards are expanded on the FORMAT /
# EXEC line.  Defaults to a space.  Value MUST be within quotes.  Can contain 1 or
# more characters
wildcard_expansion_separator = " "
# Set to 1 to allow unsafe REGEX code to be executed.
# Set to 0 to prevent unsafe REGEX code from being executed (default).
# Enabling unsafe REGEX code will allow variable interopolation and the use of the e
# modifier to allow statements such as substitution with captures such
# as:            (one (two) three)(five $1 six)
# which outputs: five two six
# or:            (one (two) three)("five ".length($1)." six")e
# which outputs: five 3 six
# This is considered unsafe because the contents of the regular expression
# (right) is executed (eval) by Perl which *could contain unsafe code*.
# BE SURE THAT THE SNMPTT CONFIGURATION FILES ARE SECURE!
allow_unsafe_regex = 0
# Set to 1 to have the backslash (escape) removed from quotes passed from
# snmptrapd.  For example, \" would be changed to just "
remove_backslash_from_quotes = 0
# Set to 1 to have NODES files loaded each time a trap is processed.
# Set to 0 to have all NODES files loaded when the snmptt.conf files are loaded.
# If NODES files are used (files that contain lists of NODES), then setting to 1
# will cause the list to be loaded each time an EVENT is processed that uses
# NODES files.  This will allow the NODES file to be modified while SNMPTT is
# running but can result in many file reads depending on the number of traps
# received.  Defaults to 0
dynamic_nodes = 0
# This option allows you to use the $D substitution variable to include the
# description text from the SNMPTT.CONF or MIB files.
# Set to 0 to disable the $D substitution variable.  If $D is used, nothing
#  will be outputted.
# Set to 1 to enable the $D substitution variable and have it use the
#  descriptions stored in the SNMPTT .conf files.  Enabling this option can
#  greatly increase the amount of memory used by SNMPTT.
# Set to 2 to enable the $D substitution variable and have it use the
#  description from the MIB files.  This enables the UCD-SNMP / NET-SNMP Perl
#  module save_descriptions variable.  Enabling this option can greatly
#  increase the amount of memory used by the Net-SNMP SNMP Perl module, which
#  will result in an increase of memory usage by SNMPTT.
description_mode = 0
# Set to 1 to remove any white space at the start of each line from the MIB
# or SNMPTT.CONF description when description_mode is set to 1 or 2.
description_clean = 1
# Warning: Experimental.  Not recommended for production environments.
#          When threads are enabled, SNMPTT may quit unexpectedly.
# Set to 1 to enable threads (ithreads) in Perl 5.6.0 or higher.  If enabled,
# EXEC will launch in a thread to allow SNMPTT to continue processing other
# traps.  See also threads_max.
# Set to 0 to disable threads (ithreads).
# Defaults to 0
threads_enable = 0
# This option allows you to set the maximum number of threads that will
# execute at once.  Defaults to 10
threads_max = 10
# The date format for $x in strftime() format.  If not defined, defaults
# to %a %b %e %Y.
#date_format = %a %b %e %Y
# The time format for $X in strftime() format.  If not defined, defaults
# to %H:%M:%S.
#time_format = %H:%M:%S
# The date time format in strftime() format for the date/time when logging
# to standard output, snmptt log files (log_file) and the unknown log file
# (unknown_trap_log_file).  Defaults to localtime().  For SQL, see
# date_time_format_sql.
# Example:  %a %b %e %Y %H:%M:%S
#date_time_format =
[DaemonMode]
# Set to 1 to have snmptt fork to the background when run in daemon mode
daemon_fork = 1
# Set to the numerical user id (eg: 500) or textual user id (eg: snmptt)
# that snmptt should change to when running in daemon mode.  Leave blank
# to disable.  The user used should have read/write access to all log
# files, the spool folder, and read access to the configuration files.
# Only use this if you are starting snmptt as root.
# A second (child) process will be started as the daemon_uid user so
# there will be two snmptt processes running.  The first process will
# continue to run as the user that ran snmptt (root), waiting for the
# child to quit.  After the child quits, the parent process will remove
# the snmptt.pid file and exit.
daemon_uid =
# Complete path of file to store process ID when running in daemon mode.
pid_file = /var/run/snmptt.pid
# Directory to read received traps from.  Ex: /var/spool/snmptt/
# Don't forget the trailing slash!
spool_directory = /var/spool/snmptt/
# Amount of time in seconds to sleep between processing spool files
sleep = 5
# Set to 1 to have SNMPTT use the time that the trap was processed by SNMPTTHANDLER
# Set to 0 to have SNMPTT use the time the trap was processed.  Note:  Using 0 can
# result in the time being off by the number of seconds used for 'sleep'
use_trap_time = 1
# Set to 0 to have SNMPTT erase the spooled trap file after it attempts to process
# the trap even if it did not successfully log the trap to any of the log systems.
# Set to 1 to have SNMPTT erase the spooled trap file only after it successfully
# logs to at least ONE log system.
# Set to 2 to have SNMPTT erase the spooled trap file only after it successfully
# logs to ALL of the enabled log systems.  Warning:  If multiple log systems are
# enabled and only one fails, the other log system will continuously be logged to
# until ALL of the log systems function.
# The recommended setting is 1 with only one log system enabled.
keep_unlogged_traps = 1
# How often duplicate traps will be processed.  An MD5 hash of all incoming traps
# is stored in memory and is used to check for duplicates.  All variables except for
# the uptime variable are used when calculating the MD5.  The larger this variable,
# the more memory snmptt will require.
# Note:  In most cases it may be a good idea to enable this but sometimes it can have a
#        negative effect.  For example, if you are trying to troubleshoot a wireless device
#        that keeps losing it's connection you may want to disable this so that you see
#        all the associations and disassociations.
# 5 minutes = 300
# 10 minutes = 600
# 15 minutes = 900
duplicate_trap_window = 0
[Logging]
# Set to 1 to enable messages to be sent to standard output, or 0 to disable.
# Would normally be disabled unless you are piping this program to another
stdout_enable = 0
# Set to 1 to enable text logging of *TRAPS*.  Make sure you specify a log_file
# location
log_enable = 1
# Log file location.  The COMPLETE path and filename.  Ex: '/var/log/snmptt/snmptt.log'
log_file = /var/log/snmptt/snmptt.log
# Set to 1 to enable text logging of *SNMPTT system errors*.  Make sure you
# specify a log_system_file location
log_system_enable = 1
# Ex: '/var/log/snmptt/snmpttsystem.log'
log_system_file = /var/log/snmptt/snmpttsystem.log
# Set to 1 to enable logging of unknown traps.  This should normally be left off
# as the file could grow large quickly.  Used primarily for troubleshooting.  If
# you have defined a trap in snmptt.conf, but it is not executing, enable this to
# see if it is being considered an unknown trap due to an incorrect entry or
# simply missing from the snmptt.conf file.
# Unknown traps can be logged either a text file, a SQL table or both.
# See SQL section to define a SQL table to log unknown traps to.
unknown_trap_log_enable = 1
# Unknown trap log file location.  The COMPLETE path and filename.
# Ex: '/var/log/snmptt/snmpttunknown.log'
# Leave blank to disable logging to text file if logging to SQL is enabled
# for unknown traps
unknown_trap_log_file = /var/log/snmptt/snmpttunknown.log
# How often in seconds statistics should be logged to syslog or the event log.
# 1 hour = 216000
# 12 hours = 2592000
# 24 hours = 5184000
statistics_interval = 0
# Set to 1 to enable logging of *TRAPS* to syslog.  If you do not have the Sys::Syslog
# module then disable this.  Windows users should disable this.
syslog_enable = 1
# Syslog facility to use for logging of *TRAPS*.  For example: 'local0'
syslog_facility = local0
# Set the syslog level for *TRAPS* based on the severity level of the trap
# as defined in the snmptt.conf file.  Values must be one per line between
# the syslog_level_* and END lines, and are not case sensitive.  For example:
#   Warning
#   Critical
# Duplicate definitions will use the definition with the higher severity.
syslog_level_debug = <<END
END
syslog_level_info = <<END
END
syslog_level_notice = <<END
END
syslog_level_warning = <<END
END
syslog_level_err = <<END
END
syslog_level_crit = <<END
END
syslog_level_alert = <<END
END
# Syslog default level to use for logging of *TRAPS*.  For example: warning
# Valid values: emerg, alert, crit, err, warning, notice, info, debug
syslog_level = info
# Set to 1 to enable logging of *SNMPTT system errors* to syslog.  If you do not have the
# Sys::Syslog module then disable this.  Windows users should disable this.
syslog_system_enable = 1
# Syslog facility to use for logging of *SNMPTT system errors*.  For example: 'local0'
syslog_system_facility = local0
# Syslog level to use for logging of *SNMPTT system errors*..  For example: 'warning'
syslog_system_level = warning
[SQL]
# Determines if the enterprise column contains the numeric OID or symbolic OID
# Set to 0 for numeric OID
# Set to 1 for symbolic OID
# Uses translate_enterprise_oid_format to determine format
db_translate_enterprise = 0
# FORMAT line to use for unknown traps.  If not defined, defaults to $-*.
db_unknown_trap_format = '$-*'
# List of custom SQL column names and values for the table of received traps
# (defined by *_table below).  The format is
#   column name
#   value
# For example:
#   binding_count
#   uptime2
#   The agent has been up for $T.
sql_custom_columns = <<END
END
# List of custom SQL column names and values for the table of unknown traps
# (defined by *_table_unknown below).  See sql_custom_columns for the format.
sql_custom_columns_unknown = <<END
END
# MySQL: Set to 1 to enable logging to a MySQL database via DBI (Linux / Windows)
# This requires DBI:: and DBD::mysql
mysql_dbi_enable = 0
# MySQL: Hostname of database server (optional - default localhost)
mysql_dbi_host = localhost
# MySQL: Port number of database server (optional - default 3306)
mysql_dbi_port = 3306
# MySQL: Database to use
mysql_dbi_database = snmptt
# MySQL: Table to use
mysql_dbi_table = snmptt
# MySQL: Table to use for unknown traps
# Leave blank to disable logging of unknown traps to MySQL
# Note: unknown_trap_log_enable must be enabled.
mysql_dbi_table_unknown = snmptt_unknown
# MySQL: Table to use for statistics
# Note: statistics_interval must be set.  See also stat_time_format_sql.
#mysql_dbi_table_statistics = snmptt_statistics
# MySQL: Username to use
mysql_dbi_username = snmpttuser
# MySQL: Password to use
mysql_dbi_password = password
# MySQL: Whether or not to 'ping' the database before attempting an INSERT
# to ensure the connection is still valid.  If *any* error is generate by
# the ping such as 'Unable to connect to database', it will attempt to
# re-create the database connection.
# Note:  This has no effect on mysql_ping_interval.
mysql_ping_on_insert = 1
# MySQL: How often in seconds the database should be 'pinged' to ensure the
# connection is still valid.  If *any* error is generate by the ping such as
# 'Unable to connect to database', it will attempt to re-create the database
# connection.  Set to 0 to disable pinging.
# Note:  This has no effect on mysql_ping_on_insert.
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
mysql_ping_interval = 300
# PostgreSQL: Set to 1 to enable logging to a PostgreSQL database via DBI (Linux / Windows)
# This requires DBI:: and DBD::PgPP
postgresql_dbi_enable = 0
# Set to 0 to use the DBD::PgPP module
# Set to 1 to use the DBD::Pg module
postgresql_dbi_module = 0
# Set to 0 to disable host and port network support
# Set to 1 to enable host and port network support
# If set to 1, ensure PostgreSQL is configured to allow connections via TCPIP by setting
# tcpip_socket = true in the $PGDATA/postgresql.conf file, and adding the ip address of
# the SNMPTT server to $PGDATApg_hba.conf.  The common location for the config files for
# RPM installations of PostgreSQL is /var/lib/pgsql/data.
postgresql_dbi_hostport_enable = 0
# PostgreSQL: Hostname of database server (optional - default localhost)
postgresql_dbi_host = localhost
# PostgreSQL: Port number of database server (optional - default 5432)
postgresql_dbi_port = 5432
# PostgreSQL: Database to use
postgresql_dbi_database = snmptt
# PostgreSQL: Table to use for unknown traps
# Leave blank to disable logging of unknown traps to PostgreSQL
postgresql_dbi_table_unknown = snmptt_unknown
# PostgreSQL: Table to use for statistics
#postgresql_dbi_table_statistics = snmptt_statistics
postgresql_dbi_table = snmptt
# PostgreSQL: Username to use
postgresql_dbi_username = snmpttuser
# PostgreSQL: Password to use
postgresql_dbi_password = password
# PostgreSQL: Whether or not to 'ping' the database before attempting an INSERT
# Note:  This has no effect on postgresqll_ping_interval.
postgresql_ping_on_insert = 1
# PostgreSQL: How often in seconds the database should be 'pinged' to ensure the
# Note:  This has no effect on postgresql_ping_on_insert.
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
postgresql_ping_interval = 300
# ODBC: Set to 1 to enable logging to a database via ODBC using DBD::ODBC.
# This requires both DBI:: and DBD::ODBC
dbd_odbc_enable = 0
# DBD:ODBC: Database to use
dbd_odbc_dsn = snmptt
# DBD:ODBC: Table to use
dbd_odbc_table = snmptt
# DBD:ODBC: Table to use for unknown traps
# Leave blank to disable logging of unknown traps to DBD:ODBC
dbd_odbc_table_unknown = snmptt_unknown
# DBD:ODBC: Table to use for statistics
#dbd_odbc_table_statistics = snmptt_statistics
# DBD:ODBC: Username to use
dbd_odbc_username = snmptt
# DBD:DBC:: Password to use
dbd_odbc_password = password
# DBD:ODBC: Whether or not to 'ping' the database before attempting an INSERT
# Note:  This has no effect on dbd_odbc_ping_interval.
dbd_odbc_ping_on_insert = 1
# DBD:ODBC:: How often in seconds the database should be 'pinged' to ensure the
# Note:  This has no effect on dbd_odbc_ping_on_insert.
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
dbd_odbc_ping_interval = 300
# The date time format for the traptime column in SQL.  Defaults to
# localtime().  When a date/time field is used in SQL, this should
# be changed to follow a standard that is supported by the SQL server.
# Example:  For a MySQL DATETIME, use %Y-%m-%d %H:%M:%S.
#date_time_format_sql =
# The date time format for the stat_time column in SQL.  Defaults to
#stat_time_format_sql =
[Exec]
# Set to 1 to allow EXEC statements to execute.  Should normally be left on unless you
# want to temporarily disable all EXEC commands
exec_enable = 1
# Set to 1 to allow PREEXEC statements to execute.  Should normally be left on unless you
# want to temporarily disable all PREEXEC commands
pre_exec_enable = 1
# If defined, the following command will be executed for ALL unknown traps.  Passed to the
# command will be all standard and enterprise variables, similar to unknown_trap_log_file
# but without the newlines.
unknown_trap_exec =
# FORMAT line that is passed to the unknown_trap_exec command.  If not defined, it
# defaults to what is described in the unknown_trap_exec setting.  The following
# would be *similar* to the default described in the unknown_trap_exec setting
# (all on one line):
# $x !! $X: Unknown trap ($o) received from $A at: Value 0: $A Value 1: $aR
# Value 2: $T Value 3: $o Value 4: $aA Value 5: $C Value 6: $e Ent Values: $+*
unknown_trap_exec_format =
# Set to 1 to escape wildards (* and ?) in EXEC, PREEXEC and the unknown_trap_exec
# commands.  Enable this to prevent the shell from expanding the wildcard
# characters.  The default is 1.
exec_escape = 1
[Debugging]
# 0 - do not output messages
# 1 - output some basic messages
# 2 - out all messages
DEBUGGING = 0
# Debugging file - SNMPTT
# Location of debugging output file.  Leave blank to default to STDOUT (good for
# standalone mode, or daemon mode without forking)
DEBUGGING_FILE =
#DEBUGGING_FILE = /var/log/snmptt/snmptt.debug
# Debugging file - SNMPTTHANDLER
DEBUGGING_FILE_HANDLER =
#DEBUGGING_FILE_HANDLER = /var/log/snmptt/snmptthandler.debug
[TrapFiles]
# A list of snmptt.conf files (this is NOT the snmptrapd.conf file).  The COMPLETE path
# and filename.  Ex: '/etc/snmp/snmptt.conf'
snmptt_conf_files = <<END
END
sreinhardt
You should probably just reinstall snmptt with our script here. It looks like you are on version 1.3, and there are many things that should be changed in the config. This should take care of all that, the pdf has the link and any further instructions you would need.
http://assets.nagios.com/downloads/nagi ... ith_XI.pdf
eclypse
Post by eclypse »
I have had a very similar (perhaps the same) issue that I have been dealing with for a while. My thread below shows more detail:
http://support.nagios.com/forum/viewtop ... =16&t=9295
I have about 40-50 machines which send snmp trap heartbeats every 60 seconds, which I believe makes this issue occur more often for me. I have just been working around this by configuring my log indexer to send me an alert if there are no snmptt messages in my logs in the past 15 minutes, and then I restart snmptt. At least one other person has tried to configure Nagios to restart snmptt when Nagios is restarted (http://support.nagios.com/forum/viewtop ... rt#p111083). Presumably this can also be detected as the /var/spool/snmptt directory begins to fill with entries like "/var/spool/snmptt/#snmptt-trap-1418965534755692"
FWIW, I'm running Nagios XI 2014R1.5 with snmptt-1.4-0.9.beta2.el6.noarch, and I used the NagiosXI-SNMPTrap-setup.sh
snmptt script to install this. Below is my snmptt.ini file which should be the default config except for me changing strip_domain to 0.
# SNMPTT v1.4beta2 Configuration File
# Linux / Unix
[General]
mode = daemon
multiple_event = 1
dns_enable = 1
strip_domain = 0
domain.com
END
# Set to 1 to enable caching of OID and ENUM translations when net_snmp_perl_enable is
# enabled.  Enabling this should result in faster translations.
# Set to 0 to disable caching.
# Note: Restart SNMPTT after updating the MIB files for Net-SNMP, otherwise the cache may
# contain inaccurate data.  Defaults to 1.
net_snmp_perl_cache_enable = 1
#        are using.
#        entire line
# MIB files
# MIB files
# more characters
dynamic_nodes = 0
# Defaults to 0
threads_enable = 0
threads_max = 10
# to %a %b %e %Y.
# to %H:%M:%S.
#date_time_format =
[DaemonMode]
daemon_fork = 1
daemon_uid = snmptt
sleep = 5
use_trap_time = 1
# 5 minutes = 300
# 10 minutes = 600
# 15 minutes = 900
[Logging]
stdout_enable = 0
# location
log_enable = 1
# for unknown traps
# 1 hour = 216000
syslog_enable = 1
#   Warning
#   Critical
END
END
END
END
END
END
END
syslog_level = info
[SQL]
#   column name
#   value
# For example:
#   binding_count
#   uptime2
END
END
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
dbd_odbc_enable = 0
# disabled = 0
# 5 minutes = 300
# 15 minutes = 900
# 30 minutes = 1800
[Exec]
exec_enable = 1
pre_exec_enable = 1
unknown_trap_exec =
exec_escape = 1
[Debugging]
DEBUGGING = 1
DEBUGGING_FILE =
# DEBUGGING_FILE_HANDLER = /var/log/snmptt/snmptthandler.debug
[TrapFiles]
END
Post by slansing »
Thank you for your response eclypse, it is much appreciated, I hope the OP may be able to glean something from this that could help!
snapon_admin
It kind of does, but employing a workaround like this seems pretty inefficient. It's been a busy past couple weeks so I haven't had a chance to re-install snmptt yet, but seeing this thread pop back up at the top here reminded me of it and made me double check my trap services. Sure enough, no updates to the log since Monday and I had to restart snmptt again. I'll have to wait until after the holiday to re-install snmptt, hopefully that will correct the issue. I'd rather not have to rely on a workaround for it...
abrist
Red Shirt
Post by abrist »
snapon_admin wrote:I'd rather not have to rely on a workaround for it...
No doubt. Let us know how it goes.
snapon_admin
Will do. As soon as my holiday hangover wears off... :P
cmerchant
Post by cmerchant »
There is certainly a cure for that. It just involves more of the same.... Good cheers.