How to log each service check?
jurijs
Post by jurijs »
Could you please let me know if it is possible to log each service check to nagios log file, similar to what I got in debug file when I turn debug level to 16?
Thank you!
With kind regards,
Jurijs
hsmith
Agent Smith
Re: How to log each service check?
Post by hsmith »
Is the information you're looking for in /usr/local/nagios/var/nagios.log ?
It contains information like this:
[1461042000] CURRENT SERVICE STATE: localhost;Current Load;OK;HARD;1;OK - load average: 0.00, 0.02, 0.02
[1461042000] CURRENT SERVICE STATE: localhost;Current Users;OK;HARD;1;USERS OK - 1 users currently logged in
[1461042000] CURRENT SERVICE STATE: localhost;HTTP;OK;HARD;1;HTTP OK: HTTP/1.1 200 OK - 3220 bytes in 0.001 second response time
[1461042000] CURRENT SERVICE STATE: localhost;PING;OK;HARD;1;PING OK - Packet loss = 0%, RTA = 0.03 ms
[1461042000] CURRENT SERVICE STATE: localhost;Root Partition;OK;HARD;1;DISK OK - free space: / 10498 MB (63% inode=92%):
[1461042000] CURRENT SERVICE STATE: localhost;SSH;OK;HARD;1;SSH OK - OpenSSH_5.3 (protocol 2.0)
[1461042000] CURRENT SERVICE STATE: localhost;Service Status - crond;OK;HARD;1;crond (pid  1488) is running...
[1461042000] CURRENT SERVICE STATE: localhost;Service Status - httpd;OK;HARD;1;httpd (pid  77440) is running...
[1461042000] CURRENT SERVICE STATE: localhost;Service Status - mysqld;OK;HARD;1;mysqld (pid  92012) is running...
[1461042000] CURRENT SERVICE STATE: localhost;Service Status - ndo2db;OK;HARD;1;ndo2db (pid 92082) is running...
[1461042000] CURRENT SERVICE STATE: localhost;Service Status - npcd;OK;HARD;1;NPCD running (pid 1500).
Former Nagios Employee.
me.
jurijs
Post by jurijs »
Yes, this is what I need, how I can turn this on?
In my log file I see only initial service state, like this:
[1461073760] INITIAL SERVICE STATE: localhost;Current Load;OK;HARD;1;OK - load average: 0.01, 0.03, 0.05
[1461073760] INITIAL SERVICE STATE: localhost;Current Users;OK;HARD;1;USERS OK - 1 users currently logged in
[1461073760] INITIAL SERVICE STATE: localhost;HTTP;OK;HARD;1;HTTP OK: HTTP/1.1 302 Found - 523 bytes in 0.000 second response time
[1461073760] INITIAL SERVICE STATE: localhost;Root Partition;OK;HARD;1;DISK OK - free space: / 70841 MB (98% inode=98%):
[1461073760] INITIAL SERVICE STATE: localhost;Total Processes;OK;HARD;1;PROCS OK: 76 processes with STATE = RSZDT
With kind regards,
Jurijs
hsmith
Agent Smith
Post by hsmith »
Can you post your /usr/local/nagios/etc/nagios.cfg file here for us to take a look at?
me.
jurijs
Post by jurijs »
First of all, I can see following in nagios.log:
[1461099600] CURRENT SERVICE STATE: localhost;Current Load;OK;HARD;1;OK - load average: 0.00, 0.01, 0.05
[1461099600] CURRENT SERVICE STATE: localhost;Current Users;OK;HARD;1;USERS OK - 0 users currently logged in
[1461099600] CURRENT SERVICE STATE: localhost;HTTP;OK;HARD;1;HTTP OK: HTTP/1.1 302 Found - 523 bytes in 0.000 second response time
[1461099600] CURRENT SERVICE STATE: localhost;Root Partition;OK;HARD;1;DISK OK - free space: / 70762 MB (97% inode=98%):
[1461099600] CURRENT SERVICE STATE: localhost;Total Processes;OK;HARD;1;PROCS OK: 73 processes with STATE = RSZDT
But as you can see it is very outdated, if I will check nagios.debug, then I will get following entries much more recent and this is what I need, I need after each service check to be written to nagios.log:
[1461141370.811492] [016.0] [pid=20321] Scheduling a non-forced, active check of service 'HTTP' on host 'localhost' @ Wed Apr 20 11:41:10 2016
[1461141370.811497] [016.1] [pid=20321] Checking service 'HTTP' on host 'localhost' for flapping...
[1461141370.811503] [016.1] [pid=20321] Checking host 'localhost' for flapping...
[1461141393.285031] [016.0] [pid=20321] Attempting to run scheduled check of service 'Root Partition' on host 'localhost': check options=0, latency=0.000000
[1461141393.285063] [016.0] [pid=20321] Checking service 'Root Partition' on host 'localhost'...
[1461141393.306410] [016.0] [pid=20321] ** Handling check result for service 'Root Partition' on host 'localhost' from 'Core Worker 20325'...
[1461141393.306427] [016.1] [pid=20321] HOST: localhost, SERVICE: Root Partition, CHECK TYPE: Active, OPTIONS: 0, SCHEDULED: Yes, RESCHEDULE: Yes, EXITED OK: Yes, RETURN CODE: 0, OUTPUT: DISK OK - free space: / 70744 MB (97% inode=98%);| /=1540MB;60363;67908;0;75454
[1461141393.306457] [016.0] [pid=20321] Scheduling a non-forced, active check of service 'Root Partition' on host 'localhost' @ Wed Apr 20 11:41:33 2016
[1461141393.306463] [016.1] [pid=20321] Checking service 'Root Partition' on host 'localhost' for flapping...
[1461141393.306469] [016.1] [pid=20321] Checking host 'localhost' for flapping...
[1461141405.532768] [016.0] [pid=20321] Attempting to run scheduled check of service 'Total Processes' on host 'localhost': check options=0, latency=0.000000
[1461141405.532804] [016.0] [pid=20321] Checking service 'Total Processes' on host 'localhost'...
[1461141405.538713] [016.0] [pid=20321] ** Handling check result for service 'Total Processes' on host 'localhost' from 'Core Worker 20324'...
[1461141405.538728] [016.1] [pid=20321] HOST: localhost, SERVICE: Total Processes, CHECK TYPE: Active, OPTIONS: 0, SCHEDULED: Yes, RESCHEDULE: Yes, EXITED OK: Yes, RETURN CODE: 0, OUTPUT: PROCS OK: 76 processes with STATE = RSZDT | procs=76;250;400;0;
[1461141405.538756] [016.0] [pid=20321] Scheduling a non-forced, active check of service 'Total Processes' on host 'localhost' @ Wed Apr 20 11:41:45 2016
[1461141405.538762] [016.1] [pid=20321] Checking service 'Total Processes' on host 'localhost' for flapping...
[1461141405.538768] [016.1] [pid=20321] Checking host 'localhost' for flapping...
[1461141409.489020] [016.0] [pid=20321] Attempting to run scheduled check of service 'Current Users' on host 'localhost': check options=0, latency=0.000000
[1461141409.489059] [016.0] [pid=20321] Checking service 'Current Users' on host 'localhost'...
[1461141409.489977] [016.0] [pid=20321] ** Handling check result for service 'Current Users' on host 'localhost' from 'Core Worker 20327'...
[1461141409.489986] [016.1] [pid=20321] HOST: localhost, SERVICE: Current Users, CHECK TYPE: Active, OPTIONS: 0, SCHEDULED: Yes, RESCHEDULE: Yes, EXITED OK: Yes, RETURN CODE: 0, OUTPUT: USERS OK - 1 users currently logged in |users=1;20;50;0
[1461141409.490010] [016.0] [pid=20321] Scheduling a non-forced, active check of service 'Current Users' on host 'localhost' @ Wed Apr 20 11:41:49 2016
[1461141409.490024] [016.1] [pid=20321] Checking service 'Current Users' on host 'localhost' for flapping...
[1461141409.490030] [016.1] [pid=20321] Checking host 'localhost' for flapping...
My config you can find below:
# NAGIOS.CFG - Sample Main Config File for Nagios 4.1.1
# Read the documentation for more information on this configuration
# file.  I've provided some comments here, but things may not be so
# clear without further explanation.
# LOG FILE
# This is the main log file where service and host events are logged
# for historical purposes.  This should be the first option specified
# in the config file!!!
log_file=/usr/local/nagios/var/nagios.log
# OBJECT CONFIGURATION FILE(S)
# These are the object configuration files in which you define hosts,
# host groups, contacts, contact groups, services, etc.
# You can split your object definitions across several config files
# if you wish (as shown below), or keep them all in a single config file.
cfg_file=/usr/local/nagios/etc/objects/commands.cfg
cfg_file=/usr/local/nagios/etc/objects/contacts.cfg
cfg_file=/usr/local/nagios/etc/objects/timeperiods.cfg
cfg_file=/usr/local/nagios/etc/objects/templates.cfg
#cfg_file=/usr/local/nagios/etc/hosts.cfg
#cfg_file=/usr/local/nagios/etc/services.cfg
# Definitions for monitoring the local (Linux) host
cfg_file=/usr/local/nagios/etc/objects/localhost.cfg
# Definitions for monitoring a Windows machine
#cfg_file=/usr/local/nagios/etc/objects/windows.cfg
# Definitions for monitoring a router/switch
#cfg_file=/usr/local/nagios/etc/objects/switch.cfg
# Definitions for monitoring a network printer
#cfg_file=/usr/local/nagios/etc/objects/printer.cfg
# You can also tell Nagios to process all config files (with a .cfg
# extension) in a particular directory by using the cfg_dir
# directive as shown below:
cfg_dir=/usr/local/nagios/etc/servers
#cfg_dir=/usr/local/nagios/etc/printers
#cfg_dir=/usr/local/nagios/etc/switches
#cfg_dir=/usr/local/nagios/etc/routers
# OBJECT CACHE FILE
# This option determines where object definitions are cached when
# Nagios starts/restarts.  The CGIs read object definitions from
# this cache file (rather than looking at the object config files
# directly) in order to prevent inconsistencies that can occur
# when the config files are modified after Nagios starts.
object_cache_file=/usr/local/nagios/var/objects.cache
# PRE-CACHED OBJECT FILE
# This options determines the location of the precached object file.
# If you run Nagios with the -p command line option, it will preprocess
# your object configuration file(s) and write the cached config to this
# file.  You can then start Nagios with the -u option to have it read
# object definitions from this precached file, rather than the standard
# object configuration files (see the cfg_file and cfg_dir options above).
# Using a precached object file can speed up the time needed to (re)start
# the Nagios process if you've got a large and/or complex configuration.
# Read the documentation section on optimizing Nagios to find our more
# about how this feature works.
precached_object_file=/usr/local/nagios/var/objects.precache
# RESOURCE FILE
# This is an optional resource file that contains $USERx$ macro
# definitions. Multiple resource files can be specified by using
# multiple resource_file definitions.  The CGIs will not attempt to
# read the contents of resource files, so information that is
# considered to be sensitive (usernames, passwords, etc) can be
# defined as macros in this file and restrictive permissions (600)
# can be placed on this file.
resource_file=/usr/local/nagios/etc/resource.cfg
# STATUS FILE
# This is where the current status of all monitored services and
# hosts is stored.  Its contents are read and processed by the CGIs.
# The contents of the status file are deleted every time Nagios
#  restarts.
status_file=/usr/local/nagios/var/status.dat
# STATUS FILE UPDATE INTERVAL
# This option determines the frequency (in seconds) that
# Nagios will periodically dump program, host, and
# service status data.
status_update_interval=10
# NAGIOS USER
# This determines the effective user that Nagios should run as.
nagios_user=nagios
# NAGIOS GROUP
# This determines the effective group that Nagios should run as.
nagios_group=nagios
# EXTERNAL COMMAND OPTION
# This option allows you to specify whether or not Nagios should check
# for external commands (in the command file defined below).  By default
# Nagios will *not* check for external commands, just to be on the
# cautious side.  If you want to be able to use the CGI command interface
# you will have to enable this.
# Values: 0 = disable commands, 1 = enable commands
check_external_commands=1
# EXTERNAL COMMAND FILE
# This is the file that Nagios checks for external command requests.
# It is also where the command CGI will write commands that are submitted
# by users, so it must be writeable by the user that the web server
# is running as (usually 'nobody').  Permissions should be set at the
# directory level instead of on the file, as the file is deleted every
# time its contents are processed.
command_file=/usr/local/nagios/var/rw/nagios.cmd
# QUERY HANDLER INTERFACE
# This is the socket that is created for the Query Handler interface
#query_socket=/usr/local/nagios/var/rw/nagios.qh
# LOCK FILE
# This is the lockfile that Nagios will use to store its PID number
# in when it is running in daemon mode.
lock_file=/usr/local/nagios/var/nagios.lock
# TEMP FILE
# This is a temporary file that is used as scratch space when Nagios
# updates the status log, cleans the comment file, etc.  This file
# is created, used, and deleted throughout the time that Nagios is
# running.
temp_file=/usr/local/nagios/var/nagios.tmp
# TEMP PATH
# This is path where Nagios can create temp files for service and
# host check results, etc.
temp_path=/tmp
# EVENT BROKER OPTIONS
# Controls what (if any) data gets sent to the event broker.
# Values:  0      = Broker nothing
#         -1      = Broker everything
#         <other> = See documentation
event_broker_options=-1
# EVENT BROKER MODULE(S)
# This directive is used to specify an event broker module that should
# by loaded by Nagios at startup.  Use multiple directives if you want
# to load more than one module.  Arguments that should be passed to
# the module at startup are seperated from the module path by a space.
# WARNING !!! WARNING !!! WARNING !!! WARNING !!! WARNING !!! WARNING
# Do NOT overwrite modules while they are being used by Nagios or Nagios
# will crash in a fiery display of SEGFAULT glory.  This is a bug/limitation
# either in dlopen(), the kernel, and/or the filesystem.  And maybe Nagios...
# The correct/safe way of updating a module is by using one of these methods:
#    1. Shutdown Nagios, replace the module file, restart Nagios
#    2. Delete the original module file, move the new module file into place, restart Nagios
# Example:
#   broker_module=<modulepath> [moduleargs]
#broker_module=/somewhere/module1.o
#broker_module=/somewhere/module2.o arg1 arg2=3 debug=0
# LOG ROTATION METHOD
# This is the log rotation method that Nagios should use to rotate
# the main log file. Values are as follows..
#       n       = None - don't rotate the log
#       h       = Hourly rotation (top of the hour)
#       d       = Daily rotation (midnight every day)
#       w       = Weekly rotation (midnight on Saturday evening)
#       m       = Monthly rotation (midnight last day of month)
log_rotation_method=d
# LOG ARCHIVE PATH
# LOGGING OPTIONS
# If you want messages logged to the syslog facility, as well as the
# Nagios log file set this option to 1.  If not, set it to 0.
use_syslog=1
# NOTIFICATION LOGGING OPTION
# If you don't want notifications to be logged, set this value to 0.
# If notifications should be logged, set the value to 1.
log_notifications=1
# SERVICE RETRY LOGGING OPTION
# to 0.  If retries should be logged, set the value to 1.
log_service_retries=1
# HOST RETRY LOGGING OPTION
# 0.  If retries should be logged, set the value to 1.
log_host_retries=1
# EVENT HANDLER LOGGING OPTION
# If you don't want host and service event handlers to be logged, set
# this value to 0.  If event handlers should be logged, set the value
# to 1.
log_event_handlers=1
# INITIAL STATES LOGGING OPTION
# If you want Nagios to log all initial host and service states to
# the main log file (the first time the service or host is checked)
# you can enable this option by setting this value to 1.  If you
# are not using an external application that does long term state
# statistics reporting, you do not need to enable this option.  In
# this case, set the value to 0.
log_initial_states=1
# CURRENT STATES LOGGING OPTION
# If you don't want Nagios to log all current host and service states
# after log has been rotated to the main log file, you can disable this
# option by setting this value to 0. Default value is 1.
log_current_states=1
# EXTERNAL COMMANDS LOGGING OPTION
# If you don't want Nagios to log external commands, set this value
# to 0.  If external commands should be logged, set this value to 1.
# Note: This option does not include logging of passive service
# checks - see the option below for controlling whether or not
# passive checks are logged.
log_external_commands=1
# PASSIVE CHECKS LOGGING OPTION
# If you don't want Nagios to log passive host and service checks, set
# this value to 0.  If passive checks should be logged, set
# this value to 1.
log_passive_checks=1
# GLOBAL HOST AND SERVICE EVENT HANDLERS
# These options allow you to specify a host and service event handler
# command that is to be run for every host or service state change.
# The global event handler is executed immediately prior to the event
# handler that you have optionally specified in each host or
# service definition. The command argument is the short name of a
# command definition that you define in your host configuration file.
# Read the HTML docs for more information.
#global_host_event_handler=somecommand
#global_service_event_handler=somecommand
# SERVICE INTER-CHECK DELAY METHOD
# This is the method that Nagios should use when initially
# "spreading out" service checks when it starts monitoring.  The
# default is to use smart delay calculation, which will try to
# space all service checks out evenly to minimize CPU load.
# Using the dumb setting will cause all checks to be scheduled
# at the same time (with no delay between them)!  This is not a
# good thing for production, but is useful when testing the
# parallelization functionality.
#       n       = None - don't use any delay between checks
#       d       = Use a "dumb" delay of 1 second between checks
#       s       = Use "smart" inter-check delay calculation
#       x.xx    = Use an inter-check delay of x.xx seconds
# MAXIMUM SERVICE CHECK SPREAD
# This variable determines the timeframe (in minutes) from the
# program start time that an initial check of all services should
# be completed.  Default is 30 minutes.
max_service_check_spread=30
# SERVICE CHECK INTERLEAVE FACTOR
# This variable determines how service checks are interleaved.
# Interleaving the service checks allows for a more even
# distribution of service checks and reduced load on remote
# hosts.  Setting this value to 1 is equivalent to how versions
# of Nagios previous to 0.0.5 did service checks.  Set this
# value to s (smart) for automatic calculation of the interleave
# factor unless you have a specific reason to change it.
#       s       = Use "smart" interleave factor calculation
#       x       = Use an interleave factor of x, where x is a
#                 number greater than or equal to 1.
service_interleave_factor=s
# HOST INTER-CHECK DELAY METHOD
# "spreading out" host checks when it starts monitoring.  The
# space all host checks out evenly to minimize CPU load.
# MAXIMUM HOST CHECK SPREAD
# program start time that an initial check of all hosts should
max_host_check_spread=30
# MAXIMUM CONCURRENT SERVICE CHECKS
# This option allows you to specify the maximum number of
# service checks that can be run in parallel at any given time.
# Specifying a value of 1 for this variable essentially prevents
# any service checks from being parallelized.  A value of 0
# will not restrict the number of concurrent checks that are
# being executed.
max_concurrent_checks=0
# HOST AND SERVICE CHECK REAPER FREQUENCY
# This is the frequency (in seconds!) that Nagios will process
# the results of host and service checks.
# MAX CHECK RESULT REAPER TIME
# This is the max amount of time (in seconds) that  a single
# check result reaper event will be allowed to run before
# returning control back to Nagios so it can perform other
# duties.
max_check_result_reaper_time=30
# CHECK RESULT PATH
# This is directory where Nagios stores the results of host and
# service checks that have not yet been processed.
# Note: Make sure that only one instance of Nagios has access
# to this directory!
check_result_path=/usr/local/nagios/var/spool/checkresults
# MAX CHECK RESULT FILE AGE
# This option determines the maximum age (in seconds) which check
# result files are considered to be valid.  Files older than this
# threshold will be mercilessly deleted without further processing.
# CACHED HOST CHECK HORIZON
# This option determines the maximum amount of time (in seconds)
# that the state of a previous host check is considered current.
# Cached host states (from host checks that were performed more
# recently that the timeframe specified by this value) can immensely
# improve performance in regards to the host check logic.
# Too high of a value for this option may result in inaccurate host
# states being used by Nagios, while a lower value may result in a
# performance hit for host checks.  Use a value of 0 to disable host
# check caching.
cached_host_check_horizon=15
# CACHED SERVICE CHECK HORIZON
# that the state of a previous service check is considered current.
# Cached service states (from service checks that were performed more
# improve performance in regards to predictive dependency checks.
# Use a value of 0 to disable service check caching.
cached_service_check_horizon=15
# ENABLE PREDICTIVE HOST DEPENDENCY CHECKS
# This option determines whether or not Nagios will attempt to execute
# checks of hosts when it predicts that future dependency logic test
# may be needed.  These predictive checks can help ensure that your
# host dependency logic works well.
# Values:
#  0 = Disable predictive checks
#  1 = Enable predictive checks (default)
# ENABLE PREDICTIVE SERVICE DEPENDENCY CHECKS
# checks of service when it predicts that future dependency logic test
# service dependency logic works well.
# Values:
# SOFT STATE DEPENDENCIES
# This option determines whether or not Nagios will use soft state
# information when checking host and service dependencies. Normally
# Nagios will only use the latest hard host or service state when
# checking dependencies. If you want it to use the latest state (regardless
# of whether its a soft or hard state type), enable this option.
# Values:
#  0 = Don't use soft state dependencies (default)
#  1 = Use soft state dependencies
soft_state_dependencies=0
# TIME CHANGE ADJUSTMENT THRESHOLDS
# These options determine when Nagios will react to detected changes
# in system time (either forward or backwards).
#time_change_threshold=900
# AUTO-RESCHEDULING OPTION
# automatically reschedule active host and service checks to
# "smooth" them out over time.  This can help balance the load on
# the monitoring server.
# WARNING: THIS IS AN EXPERIMENTAL FEATURE - IT CAN DEGRADE
# PERFORMANCE, RATHER THAN INCREASE IT, IF USED IMPROPERLY
auto_reschedule_checks=0
# AUTO-RESCHEDULING INTERVAL
# This option determines how often (in seconds) Nagios will
# attempt to automatically reschedule checks.  This option only
# has an effect if the auto_reschedule_checks option is enabled.
# Default is 30 seconds.
auto_rescheduling_interval=30
# AUTO-RESCHEDULING WINDOW
# This option determines the "window" of time (in seconds) that
# Nagios will look at when automatically rescheduling checks.
# Only host and service checks that occur in the next X seconds
# (determined by this variable) will be rescheduled. This option
# only has an effect if the auto_reschedule_checks option is
# enabled.  Default is 180 seconds (3 minutes).
auto_rescheduling_window=180
# TIMEOUT VALUES
# These options control how much time Nagios will allow various
# types of commands to execute before killing them off.  Options
# are available for controlling maximum time allotted for
# service checks, host checks, event handlers, notifications, the
# ocsp command, and performance data commands.  All values are in
# seconds.
service_check_timeout=60
host_check_timeout=30
event_handler_timeout=30
notification_timeout=30
ocsp_timeout=5
perfdata_timeout=5
# RETAIN STATE INFORMATION
# This setting determines whether or not Nagios will save state
# information for services and hosts before it shuts down.  Upon
# startup Nagios will reload all saved service and host state
# information before starting to monitor.  This is useful for
# maintaining long-term data on state statistics, etc, but will
# slow Nagios down a bit when it (re)starts.  Since its only
# a one-time penalty, I think its well worth the additional
# startup delay.
retain_state_information=1
# STATE RETENTION FILE
# This is the file that Nagios should use to store host and
# service state information before it shuts down.  The state
# information in this file is also read immediately prior to
# starting to monitor the network when Nagios is restarted.
# This file is used only if the retain_state_information
# variable is set to 1.
state_retention_file=/usr/local/nagios/var/retention.dat
# RETENTION DATA UPDATE INTERVAL
# This setting determines how often (in minutes) that Nagios
# will automatically save retention data during normal operation.
# If you set this value to 0, Nagios will not save retention
# data at regular interval, but it will still save retention
# data before shutting down or restarting.  If you have disabled
# state retention, this option has no effect.
retention_update_interval=60
# USE RETAINED PROGRAM STATE
# This setting determines whether or not Nagios will set
# program status variables based on the values saved in the
# retention file.  If you want to use retained program status
# information, set this value to 1.  If not, set this value
# to 0.
use_retained_program_state=1
# USE RETAINED SCHEDULING INFO
# This setting determines whether or not Nagios will retain
# the scheduling info (next check time) for hosts and services
# based on the values saved in the retention file.  If you
# If you want to use retained scheduling info, set this
# value to 1.  If not, set this value to 0.
# RETAINED ATTRIBUTE MASKS (ADVANCED FEATURE)
# The following variables are used to specify specific host and
# service attributes that should *not* be retained by Nagios during
# program restarts.
# The values of the masks are bitwise ANDs of values specified
# by the "MODATTR_" definitions found in include/common.h.
# For example, if you do not want the current enabled/disabled state
# of flap detection and event handlers for hosts to be retained, you
# would use a value of 24 for the host attribute mask...
# MODATTR_EVENT_HANDLER_ENABLED (8) + MODATTR_FLAP_DETECTION_ENABLED (16) = 24
# This mask determines what host attributes are not retained
# This mask determines what service attributes are not retained
# These two masks determine what process attributes are not retained.
# There are two masks, because some process attributes have host and service
# options.  For example, you can disable active host checks, but leave active
# service checks enabled.
# These two masks determine what contact attributes are not retained.
# There are two masks, because some contact attributes have host and
# service options.  For example, you can disable host notifications for
# a contact, but leave service notifications enabled for them.
# INTERVAL LENGTH
# This is the seconds per unit interval as used in the
# host/contact/service configuration files.  Setting this to 60 means
# that each interval is one minute long (60 seconds).  Other settings
# have not been tested much, so your mileage is likely to vary...
interval_length=60
# CHECK FOR UPDATES
# This option determines whether Nagios will automatically check to
# see if new updates (releases) are available.  It is recommend that you
# enable this option to ensure that you stay on top of the latest critical
# patches to Nagios.  Nagios is critical to you - make sure you keep it in
# good shape.  Nagios will check once a day for new updates. Data collected
# by Nagios Enterprises from the update check is processed in accordance
# with our privacy policy - see https://api.nagios.org for details.
check_for_updates=1
# BARE UPDATE CHECK
# This option deterines what data Nagios will send to api.nagios.org when
# it checks for updates.  By default, Nagios will send information on the
# current version of Nagios you have installed, as well as an indicator as
# to whether this was a new installation or not.  Nagios Enterprises uses
# this data to determine the number of users running specific version of
# Nagios.  Enable this option if you do not want this information to be sent.
bare_update_check=0
# AGGRESSIVE HOST CHECKING OPTION
# If you don't want to turn on aggressive host checking features, set
# this value to 0 (the default).  Otherwise set this value to 1 to
# enable the aggressive check option.  Read the docs for more info
# on what aggressive host check is or check out the source code in
# base/checks.c
# SERVICE CHECK EXECUTION OPTION
# This determines whether or not Nagios will actively execute
# service checks when it initially starts.  If this option is
# disabled, checks are not actively made, but Nagios can still
# receive and process passive check results that come in.  Unless
# you're implementing redundant hosts or have a special need for
# disabling the execution of service checks, leave this enabled!
# Values: 1 = enable checks, 0 = disable checks
execute_service_checks=1
# PASSIVE SERVICE CHECK ACCEPTANCE OPTION
# This determines whether or not Nagios will accept passive
# service checks results when it initially (re)starts.
# Values: 1 = accept passive checks, 0 = reject passive checks
# HOST CHECK EXECUTION OPTION
# host checks when it initially starts.  If this option is
# disabling the execution of host checks, leave this enabled!
execute_host_checks=1
# PASSIVE HOST CHECK ACCEPTANCE OPTION
# host checks results when it initially (re)starts.
accept_passive_host_checks=1
# NOTIFICATIONS OPTION
# This determines whether or not Nagios will sent out any host or
# service notifications when it is initially (re)started.
# Values: 1 = enable notifications, 0 = disable notifications
enable_notifications=1
# EVENT HANDLER USE OPTION
# This determines whether or not Nagios will run any host or
# service event handlers when it is initially (re)started.  Unless
# you're implementing redundant hosts, leave this option enabled.
# Values: 1 = enable event handlers, 0 = disable event handlers
enable_event_handlers=1
# PROCESS PERFORMANCE DATA OPTION
# This determines whether or not Nagios will process performance
# data returned from service and host checks.  If this option is
# enabled, host performance data will be processed using the
# host_perfdata_command (defined below) and service performance
# data will be processed using the service_perfdata_command (also
# defined below).  Read the HTML docs for more information on
# performance data.
# Values: 1 = process performance data, 0 = do not process performance data
process_performance_data=0
# HOST AND SERVICE PERFORMANCE DATA PROCESSING COMMANDS
# These commands are run after every host and service check is
# performed.  These commands are executed only if the
# enable_performance_data option (above) is set to 1.  The command
# argument is the short name of a command definition that you
# define in your host configuration file.  Read the HTML docs for
# more information on performance data.
#host_perfdata_command=process-host-perfdata
#service_perfdata_command=process-service-perfdata
# HOST AND SERVICE PERFORMANCE DATA FILES
# These files are used to store host and service performance data.
# Performance data is only written to these files if the
#host_perfdata_file=/usr/local/nagios/var/host-perfdata
#service_perfdata_file=/usr/local/nagios/var/service-perfdata
# HOST AND SERVICE PERFORMANCE DATA FILE TEMPLATES
# These options determine what data is written (and how) to the
# performance data files.  The templates may contain macros, special
# characters (\t for tab, \r for carriage return, \n for newline)
# and plain text.  A newline is automatically added after each write
# to the performance data file.  Some examples of what you can do are
# shown below.
#host_perfdata_file_template=[HOSTPERFDATA]\t$TIMET$\t$HOSTNAME$\t$HOSTEXECUTIONTIME$\t$HOSTOUTPUT$\t$HOSTPERFDATA$
#service_perfdata_file_template=[SERVICEPERFDATA]\t$TIMET$\t$HOSTNAME$\t$SERVICEDESC$\t$SERVICEEXECUTIONTIME$\t$SERVICELATENCY$\t$SERVICEOUTPUT$\t$SERVICEPER
FDATA$
# HOST AND SERVICE PERFORMANCE DATA FILE MODES
# This option determines whether or not the host and service
# performance data files are opened in write ("w") or append ("a")
# mode. If you want to use named pipes, you should use the special
# pipe ("p") mode which avoid blocking at startup, otherwise you will
# likely want the defult append ("a") mode.
#host_perfdata_file_mode=a
#service_perfdata_file_mode=a
# HOST AND SERVICE PERFORMANCE DATA FILE PROCESSING INTERVAL
# These options determine how often (in seconds) the host and service
# performance data files are processed using the commands defined
# below.  A value of 0 indicates the files should not be periodically
# processed.
#host_perfdata_file_processing_interval=0
#service_perfdata_file_processing_interval=0
# HOST AND SERVICE PERFORMANCE DATA FILE PROCESSING COMMANDS
# These commands are used to periodically process the host and
# service performance data files.  The interval at which the
# processing occurs is determined by the options above.
#host_perfdata_file_processing_command=process-host-perfdata-file
#service_perfdata_file_processing_command=process-service-perfdata-file
# HOST AND SERVICE PERFORMANCE DATA PROCESS EMPTY RESULTS
# These options determine wether the core will process empty perfdata
# results or not. This is needed for distributed monitoring, and intentionally
# turned on by default.
# If you don't require empty perfdata - saving some cpu cycles
# on unwanted macro calculation - you can turn that off. Be careful!
# Values: 1 = enable, 0 = disable
#host_perfdata_process_empty_results=1
#service_perfdata_process_empty_results=1
# OBSESS OVER SERVICE CHECKS OPTION
# This determines whether or not Nagios will obsess over service
# checks and run the ocsp_command defined below.  Unless you're
# planning on implementing distributed monitoring, do not enable
# this option.  Read the HTML docs for more information on
# implementing distributed monitoring.
# Values: 1 = obsess over services, 0 = do not obsess (default)
obsess_over_services=0
# OBSESSIVE COMPULSIVE SERVICE PROCESSOR COMMAND
# This is the command that is run for every service check that is
# processed by Nagios.  This command is executed only if the
# obsess_over_services option (above) is set to 1.  The command
# more information on implementing distributed monitoring.
#ocsp_command=somecommand
# OBSESS OVER HOST CHECKS OPTION
# This determines whether or not Nagios will obsess over host
# checks and run the ochp_command defined below.  Unless you're
# Values: 1 = obsess over hosts, 0 = do not obsess (default)
obsess_over_hosts=0
# OBSESSIVE COMPULSIVE HOST PROCESSOR COMMAND
# This is the command that is run for every host check that is
# obsess_over_hosts option (above) is set to 1.  The command
#ochp_command=somecommand
# TRANSLATE PASSIVE HOST CHECKS OPTION
# This determines whether or not Nagios will translate
# DOWN/UNREACHABLE passive host check results into their proper
# state for this instance of Nagios.  This option is useful
# if you have distributed or failover monitoring setup.  In
# these cases your other Nagios servers probably have a different
# "view" of the network, with regards to the parent/child relationship
# of hosts.  If a distributed monitoring server thinks a host
# is DOWN, it may actually be UNREACHABLE from the point of
# this Nagios instance.  Enabling this option will tell Nagios
# to translate any DOWN or UNREACHABLE host states it receives
# passively into the correct state from the view of this server.
# Values: 1 = perform translation, 0 = do not translate (default)
# PASSIVE HOST CHECKS ARE SOFT OPTION
# This determines whether or not Nagios will treat passive host
# checks as being HARD or SOFT.  By default, a passive host check
# result will put a host into a HARD state type.  This can be changed
# by enabling this option.
# Values: 0 = passive checks are HARD, 1 = passive checks are SOFT
# ORPHANED HOST/SERVICE CHECK OPTIONS
# These options determine whether or not Nagios will periodically
# check for orphaned host service checks.  Since service checks are
# not rescheduled until the results of their previous execution
# instance are processed, there exists a possibility that some
# checks may never get rescheduled.  A similar situation exists for
# host checks, although the exact scheduling details differ a bit
# from service checks.  Orphaned checks seem to be a rare
# problem and should not happen under normal circumstances.
# If you have problems with service checks never getting
# rescheduled, make sure you have orphaned service checks enabled.
check_for_orphaned_services=1
check_for_orphaned_hosts=1
# SERVICE FRESHNESS CHECK OPTION
# This option determines whether or not Nagios will periodically
# check the "freshness" of service results.  Enabling this option
# is useful for ensuring passive checks are received in a timely
# manner.
# Values: 1 = enabled freshness checking, 0 = disable freshness checking
check_service_freshness=1
# SERVICE FRESHNESS CHECK INTERVAL
# This setting determines how often (in seconds) Nagios will
# check the "freshness" of service check results.  If you have
# disabled service freshness checking, this option has no effect.
# SERVICE CHECK TIMEOUT STATE
# This setting determines the state Nagios will report when a
# service check times out - that is does not respond within
# service_check_timeout seconds.  This can be useful if a
# machine is running at too high a load and you do not want
# to consider a failed service check to be critical (the default).
# Valid settings are:
# c - Critical (default)
# u - Unknown
# w - Warning
# o - OK
service_check_timeout_state=c
# HOST FRESHNESS CHECK OPTION
# check the "freshness" of host results.  Enabling this option
# manner.
check_host_freshness=0
# HOST FRESHNESS CHECK INTERVAL
# check the "freshness" of host check results.  If you have
# disabled host freshness checking, this option has no effect.
# ADDITIONAL FRESHNESS THRESHOLD LATENCY
# This setting determines the number of seconds that Nagios
# will add to any host and service freshness thresholds that
# it calculates (those not explicitly specified by the user).
additional_freshness_latency=15
# FLAP DETECTION OPTION
# This option determines whether or not Nagios will try
# and detect hosts and services that are "flapping".
# Flapping occurs when a host or service changes between
# states too frequently.  When Nagios detects that a
# host or service is flapping, it will temporarily suppress
# notifications for that host/service until it stops
# flapping.  Flap detection is very experimental, so read
# the HTML documentation before enabling this feature!
# Values: 1 = enable flap detection
#         0 = disable flap detection (default)
enable_flap_detection=1
# FLAP DETECTION THRESHOLDS FOR HOSTS AND SERVICES
# Read the HTML documentation on flap detection for
# an explanation of what this option does.  This option
# has no effect if flap detection is disabled.
low_host_flap_threshold=5.0
high_host_flap_threshold=20.0
# DATE FORMAT OPTION
# This option determines how short dates are displayed. Valid options
# include:
#       us              (MM-DD-YYYY HH:MM:SS)
#       euro            (DD-MM-YYYY HH:MM:SS)
#       iso8601         (YYYY-MM-DD HH:MM:SS)
#       strict-iso8601  (YYYY-MM-DDTHH:MM:SS)
date_format=us
# TIMEZONE OFFSET
# This option is used to override the default timezone that this
# instance of Nagios runs in.  If not specified, Nagios will use
# the system configured timezone.
# NOTE: In order to display the correct timezone in the CGIs, you
# will also need to alter the Apache directives for the CGI path
# to include your timezone.  Example:
#   <Directory "/usr/local/nagios/sbin/">
#      SetEnv TZ "Australia/Brisbane"
#   </Directory>
#use_timezone=US/Mountain
#use_timezone=Australia/Brisbane
# ILLEGAL OBJECT NAME CHARACTERS
# This option allows you to specify illegal characters that cannot
# be used in host names, service descriptions, or names of other
# object types.
# ILLEGAL MACRO OUTPUT CHARACTERS
# This option allows you to specify illegal characters that are
# stripped from macros before being used in notifications, event
# handlers, etc.  This DOES NOT affect macros used in service or
# host check commands.
# The following macros are stripped of the characters you specify:
#       $HOSTOUTPUT$
#       $LONGHOSTOUTPUT$
#       $HOSTPERFDATA$
#       $HOSTACKAUTHOR$
#       $HOSTACKCOMMENT$
#       $SERVICEOUTPUT$
#       $LONGSERVICEOUTPUT$
#       $SERVICEPERFDATA$
#       $SERVICEACKAUTHOR$
#       $SERVICEACKCOMMENT$
# REGULAR EXPRESSION MATCHING
# takes place in the object config files.  Regular expression
use_regexp_matching=0
# "TRUE" REGULAR EXPRESSION MATCHING
# This option controls whether or not "true" regular expression
# matching takes place in the object config files.  This option
# only has an effect if regular expression matching is enabled
# (see above).  If this option is DISABLED, regular expression
# matching only occurs if a string contains wildcard characters
# (* and ?).  If the option is ENABLED, regexp matching occurs
# all the time (which can be annoying).
# Values: 1 = enable true matching, 0 = disable true matching
use_true_regexp_matching=0
# ADMINISTRATOR EMAIL/PAGER ADDRESSES
# The email and pager address of a global administrator (likely you).
# Nagios never uses these values itself, but you can access them by
# using the $ADMINEMAIL$ and $ADMINPAGER$ macros in your notification
# commands.
admin_email=nagios@localhost
admin_pager=pagenagios@localhost
# DAEMON CORE DUMP OPTION
# This option determines whether or not Nagios is allowed to create
# a core dump when it runs as a daemon.  Note that it is generally
# considered bad form to allow this, but it may be useful for
# debugging purposes.  Enabling this option doesn't guarantee that
# a core file will be produced, but that's just life...
# Values: 1 - Allow core dumps
#         0 - Do not allow core dumps (default)
daemon_dumps_core=0
# LARGE INSTALLATION TWEAKS OPTION
# This option determines whether or not Nagios will take some shortcuts
# which can save on memory and CPU usage in large Nagios installations.
# Read the documentation for more information on the benefits/tradeoffs
# of enabling this option.
# Values: 1 - Enabled tweaks
#         0 - Disable tweaks (default)
# ENABLE ENVIRONMENT MACROS
# This option determines whether or not Nagios will make all standard
# macros available as environment variables when host/service checks
# and system commands (event handlers, notifications, etc.) are
# executed.
# Enabling this is a very bad idea for anything but very small setups,
# as it means plugins, notification scripts and eventhandlers may run
# out of environment space. It will also cause a significant increase
# in CPU- and memory usage and drastically reduce the number of checks
# you can run.
# Values: 1 - Enable environment variable macros
#         0 - Disable environment variable macros (default)
enable_environment_macros=0
# CHILD PROCESS MEMORY OPTION
# This option determines whether or not Nagios will free memory in
# child processes (processed used to execute system commands and host/
# service checks).  If you specify a value here, it will override
# program defaults.
# Value: 1 - Free memory in child processes
#        0 - Do not free memory in child processes
#free_child_process_memory=1
# CHILD PROCESS FORKING BEHAVIOR
# This option determines how Nagios will fork child processes
# (used to execute system commands and host/service checks).  Normally
# child processes are fork()ed twice, which provides a very high level
# of isolation from problems.  Fork()ing once is probably enough and will
# save a great deal on CPU usage (in large installs), so you might
# want to consider using this.  If you specify a value here, it will
# program defaults.
# Value: 1 - Child processes fork() twice
#        0 - Child processes fork() just once
#child_processes_fork_twice=1
# DEBUG LEVEL
# be written to the debug file.  OR values together to log multiple
# types of information.
# Values:
#          -1 = Everything
#          0 = Nothing
#          1 = Functions
#          2 = Configuration
#          4 = Process information
#          8 = Scheduled events
#          16 = Host/service checks
#          32 = Notifications
#          64 = Event broker
#          128 = External commands
#          256 = Commands
#          512 = Scheduled downtime
#          1024 = Comments
#          2048 = Macros
debug_level=16
# DEBUG VERBOSITY
# This option determines how verbose the debug log out will be.
# Values: 0 = Brief output
#         1 = More detailed
#         2 = Very detailed
debug_verbosity=1
# DEBUG FILE
# This option determines where Nagios should write debugging information.
debug_file=/usr/local/nagios/var/nagios.debug
# MAX DEBUG FILE SIZE
# This option determines the maximum size (in bytes) of the debug file.  If
# the file grows larger than this size, it will be renamed with a .old
# extension.  If a file already exists with a .old extension it will
# automatically be deleted.  This helps ensure your disk space usage doesn't
# get out of control when debugging Nagios.
max_debug_file_size=1000000
# Should we allow hostgroups to have no hosts, we default this to off since
# that was the old behavior
allow_empty_hostgroup_assignment=0
# Normally worker count is dynamically allocated based on 1.5 * number of cpu's
# with a minimum of 4 workers.  This value will override the defaults
#check_workers=3
# DISABLE SERVICE CHECKS WHEN HOST DOWN
# This option will disable all service checks if the host is not in an UP state
# While desirable in some environments, enabling this value can distort report
# values as the expected quantity of checks will not have been performed
#host_down_disable_service_checks=0
# EXPERIMENTAL load controlling options
# To get current defaults based on your system issue a command to
# the query handler. Please note that this is an experimental feature
# and not meant for production use. Used incorrectly it can induce
# enormous latency.
# #core loadctl
#   jobs_max - The maximum amount of jobs to run at one time
#   jobs_min - The minimum amount of jobs to run at one time
#   jobs_limit - The maximum amount of jobs the current load lets us run
#   backoff_limit - The minimum backoff_change
#   backoff_change - # of jobs to remove from jobs_limit when backing off
#   rampup_limit - Minimum rampup_change
#   rampup_change - # of jobs to add to jobs_limit when ramping up
# NOTE: The backoff_limit and rampup_limit are NOT used by anything currently,
#       so if your system is under load nothing will actively modify the jobs
#       even if you have these options enabled, they are for external
#       connector information only.  However, if you change the jobs_max or
#       jobs_min manually here or through the query handler interface that
#       WILL affect your system
#loadctl_options=jobs_max=100;backoff_limit=10;rampup_change=5
Your nagios.cfg file has logging enabled to the nagios.log file as well as syslog.
Can you look at the /var/log/messages and see if the service checks are logged in that file?
Try restarting the nagios process to see if the logs start up.
service nagios restart
jurijs
Post by jurijs »
I tried to restart nagios service and it didn't helped.
There is no service check logs in /var/log/syslog too.
With kind regards,
Jurijs
Can you run the following commands and post the output?
chage -l nagios
grep nag /etc/group
ls -l /usr/local/nagios
ls -l /usr/local/nagios/var
What OS and version did you install Nagios on?
jurijs
Post by jurijs »
As requested:
root@nagios:/home/ubuntu# chage -l nagios
Last password change                                    : Jan 11, 2016
Password expires                                        : never
Password inactive                                       : never
Account expires                                         : never
Minimum number of days between password change          : 0
Maximum number of days between password change          : 99999
Number of days of warning before password expires       : 7
root@nagios:/home/ubuntu# grep nag /etc/group
nagios:x:1001:
nagcmd:x:1002:nagios,www-data
root@nagios:/home/ubuntu# ls -l /usr/local/nagios
total 28
drwxrwxr-x  2 nagios nagios 4096 Jan 11 17:33 bin
drwxrwxr-x  4 nagios nagios 4096 Jan 12 12:13 etc
drwxr-xr-x  2 root   root   4096 Jan 11 17:35 include
drwxrwxr-x  2 nagios nagios 4096 Apr 26 10:57 libexec
drwxrwxr-x  2 nagios nagios 4096 Jan 11 17:33 sbin
drwxrwxr-x 15 nagios nagios 4096 Jan 11 17:35 share
drwxrwxr-x  5 nagios nagios 4096 Apr 26 12:46 var
root@nagios:/home/ubuntu# ls -l /usr/local/nagios/var
total 2012
drwxrwxr-x 2 nagios nagios    4096 Apr 25 23:59 archives
-rw-r--r-- 1 nagios nagios  914355 Apr 26 12:46 nagios.debug
-rw-r--r-- 1 nagios nagios 1000021 Apr 26 11:02 nagios.debug.old
-rw-r--r-- 1 nagios nagios       5 Apr 26 12:34 nagios.lock
-rw-r--r-- 1 nagios nagios   11108 Apr 26 12:43 nagios.log
-rw-r--r-- 1 nagios nagios   25785 Apr 26 12:34 objects.cache
-rw------- 1 nagios nagios   34452 Apr 26 12:34 retention.dat
drwxrwsr-x 2 nagios nagcmd    4096 Apr 26 12:34 rw
drwxr-xr-x 3 root   root      4096 Jan 11 17:33 spool
-rw-rw-r-- 1 nagios nagios   34914 Apr 26 12:46 status.dat
Ubuntu 14.04
Can you edit the /etc/group file and change the following line from
nagios:x:1001:
to
nagios:x:1001:nagios,www-data
Then reboot the server and see if that fixes the issue.