An unusual request maybe - Is there a way that I can get the Average, Min and Max counters for CPU and Memory for hosts being monitotred by Nagios for say last 2 weeks?
I know this information is available in the performance graphs but I was looking for a way to do this via the script and get the information on a command line.
Any assistnce is appreciated.
Get CPU and Memory data from Nagios
Re: Get CPU and Memory data from Nagios
If you have an Enterprise license, you should be able to use the rrdexport API endpoint. Usage can be found in the "Help" section of your Nagios XI GUI. If you don't have enterprise, rrdxport is another option.
As an example, to get the rta for the localhost PING service:
Which spits out:
Which could then be narrowed to the last 2 weeks down based on the timestamps in the historical object.
curl -XGET "http://192.168.67.11/nagiosxi/api/v1/objects/cpexport?apikey=<api_key_here>&pretty=1&host_name=localhost&service_description=PING&track=rta"Code: Select all
"emax": 0.08101789294232,
"eslope": -6.0179736441792e-11,
"evalue_max": 0.033573631363097,
"t_start": 1488211200,
"warn_level": 100,
"dmean": 0.029692525252525,
"t_stop": 1490027400,
"dmax": 0.13476944444444,
"integrity": 0.40861812778603,
"unit": "ms",
"residue": 0.012963440232965,
"emean": 0.029244522840266,
"edate": 1490025600,
"evalue": 0.029181498204823,
"nd": 672,
"ne": 336,
"evalue_min": 0.024789365046549,
"adjusted_sigma": 0.010748747692794,
"t_step": 1800,
"crit_level": 500,
"f_of_x_on_date": 0.029619731843325,
"sigma": 0.0043921331582737,
"data": {
"historical": {
"1488211200": 0.029692525252525,
"1488213000": 0.029692525252525,
"1488214800": 0.029692525252525,
"1488216600": 0.029692525252525,
"1488218400": 0.029692525252525,
"1488220200": 0.029692525252525,
"1488222000": 0.029692525252525,
"1488223800": 0.029692525252525,
"1488225600": 0.029692525252525,
"1488227400": 0.029692525252525,
"1488229200": 0.029692525252525,
"1488231000": 0.029692525252525,
"1488232800": 0.029692525252525,
"1488234600": 0.029692525252525,
"1488236400": 0.029692525252525,
"1488238200": 0.029692525252525,
"1488240000": 0.029692525252525,
"1488241800": 0.029692525252525,
"1488243600": 0.029692525252525,
"1488245400": 0.029692525252525,
"1488247200": 0.029692525252525,
"1488249000": 0.029692525252525,
"1488250800": 0.029692525252525,
"1488252600": 0.029692525252525,
"1488254400": 0.029692525252525,
"1488256200": 0.029692525252525,
"1488258000": 0.029692525252525,
"1488259800": 0.029692525252525,
"1488261600": 0.029692525252525,
"1488263400": 0.029692525252525,
"1488265200": 0.029692525252525,
"1488267000": 0.029692525252525,
"1488268800": 0.029692525252525,
"1488270600": 0.029692525252525,
"1488272400": 0.029692525252525,
"1488274200": 0.029692525252525,
"1488276000": 0.029692525252525,
"1488277800": 0.029692525252525,
"1488279600": 0.029692525252525,
"1488281400": 0.029692525252525,
"1488283200": 0.029692525252525,
"1488285000": 0.029692525252525,
"1488286800": 0.029692525252525,
"1488288600": 0.029692525252525,
"1488290400": 0.029692525252525,
"1488292200": 0.029692525252525,
"1488294000": 0.029692525252525,
"1488295800": 0.029692525252525,
"1488297600": 0.029692525252525,
"1488299400": 0.029692525252525,
"1488301200": 0.029692525252525,
"1488303000": 0.029692525252525,
"1488304800": 0.029692525252525,
"1488306600": 0.029692525252525,
"1488308400": 0.029692525252525,
"1488310200": 0.029692525252525,
"1488312000": 0.029692525252525,
"1488313800": 0.029692525252525,
"1488315600": 0.029692525252525,
"1488317400": 0.029692525252525,
"1488319200": 0.029692525252525,
"1488321000": 0.029692525252525,
"1488322800": 0.029692525252525,
"1488324600": 0.029692525252525,
"1488326400": 0.029692525252525,
"1488328200": 0.029692525252525,
"1488330000": 0.029692525252525,
"1488331800": 0.029692525252525,
"1488333600": 0.029692525252525,
"1488335400": 0.029692525252525,
"1488337200": 0.029692525252525,
"1488339000": 0.029692525252525,
"1488340800": 0.029692525252525,
"1488342600": 0.029692525252525,
"1488344400": 0.029692525252525,
"1488346200": 0.029692525252525,
"1488348000": 0.029692525252525,
"1488349800": 0.029692525252525,
"1488351600": 0.029692525252525,
"1488353400": 0.029692525252525,
"1488355200": 0.029692525252525,
"1488357000": 0.029692525252525,
"1488358800": 0.029692525252525,
"1488360600": 0.029692525252525,
"1488362400": 0.029692525252525,
"1488364200": 0.029692525252525,
"1488366000": 0.029692525252525,
"1488367800": 0.029692525252525,
"1488369600": 0.029692525252525,
"1488371400": 0.029692525252525,
"1488373200": 0.029692525252525,
"1488375000": 0.029692525252525,
"1488376800": 0.029692525252525,
"1488378600": 0.029692525252525,
"1488380400": 0.029692525252525,
"1488382200": 0.029692525252525,
"1488384000": 0.029692525252525,
"1488385800": 0.029692525252525,
"1488387600": 0.029692525252525,
"1488389400": 0.029692525252525,
"1488391200": 0.029692525252525,
"1488393000": 0.029692525252525,
"1488394800": 0.029692525252525,
"1488396600": 0.029692525252525,
"1488398400": 0.029692525252525,
"1488400200": 0.029692525252525,
"1488402000": 0.029692525252525,
"1488403800": 0.029692525252525,
"1488405600": 0.029692525252525,
"1488407400": 0.029692525252525,
"1488409200": 0.029692525252525,
"1488411000": 0.029692525252525,
"1488412800": 0.029692525252525,
"1488414600": 0.029692525252525,
"1488416400": 0.029692525252525,
"1488418200": 0.029692525252525,
"1488420000": 0.029692525252525,
"1488421800": 0.029692525252525,
"1488423600": 0.029692525252525,
"1488425400": 0.029692525252525,
"1488427200": 0.029692525252525,
"1488429000": 0.029692525252525,
"1488430800": 0.029692525252525,
"1488432600": 0.029692525252525,
"1488434400": 0.029692525252525,
"1488436200": 0.029692525252525,
"1488438000": 0.029692525252525,
"1488439800": 0.029692525252525,
"1488441600": 0.029692525252525,
"1488443400": 0.029692525252525,
"1488445200": 0.029692525252525,
"1488447000": 0.029692525252525,
"1488448800": 0.029692525252525,
"1488450600": 0.029692525252525,
"1488452400": 0.029692525252525,
"1488454200": 0.029692525252525,
"1488456000": 0.029692525252525,
"1488457800": 0.029692525252525,
"1488459600": 0.029692525252525,
"1488461400": 0.029692525252525,
"1488463200": 0.029692525252525,
"1488465000": 0.029692525252525,
"1488466800": 0.029692525252525,
"1488468600": 0.029692525252525,
"1488470400": 0.029692525252525,
"1488472200": 0.029692525252525,
"1488474000": 0.029692525252525,
"1488475800": 0.029692525252525,
"1488477600": 0.029692525252525,
"1488479400": 0.029692525252525,
"1488481200": 0.029692525252525,
"1488483000": 0.029692525252525,
"1488484800": 0.029692525252525,
"1488486600": 0.029692525252525,
"1488488400": 0.029692525252525,
"1488490200": 0.029692525252525,
"1488492000": 0.029692525252525,
"1488493800": 0.029692525252525,
"1488495600": 0.029692525252525,
"1488497400": 0.029692525252525,
"1488499200": 0.029692525252525,
"1488501000": 0.029692525252525,
"1488502800": 0.029692525252525,
"1488504600": 0.029692525252525,
"1488506400": 0.029692525252525,
"1488508200": 0.029692525252525,
"1488510000": 0.029692525252525,
"1488511800": 0.029692525252525,
"1488513600": 0.029692525252525,
"1488515400": 0.029692525252525,
"1488517200": 0.029692525252525,
"1488519000": 0.029692525252525,
"1488520800": 0.029692525252525,
"1488522600": 0.029692525252525,
"1488524400": 0.029692525252525,
"1488526200": 0.029692525252525,
"1488528000": 0.029692525252525,
"1488529800": 0.029692525252525,
"1488531600": 0.029692525252525,
"1488533400": 0.029692525252525,
"1488535200": 0.029692525252525,
"1488537000": 0.029692525252525,
"1488538800": 0.029692525252525,
"1488540600": 0.029692525252525,
"1488542400": 0.029692525252525,
"1488544200": 0.029692525252525,
"1488546000": 0.029692525252525,
"1488547800": 0.029692525252525,
"1488549600": 0.029692525252525,
"1488551400": 0.029692525252525,
"1488553200": 0.029692525252525,
"1488555000": 0.029692525252525,
"1488556800": 0.029692525252525,
"1488558600": 0.029692525252525,
"1488560400": 0.029692525252525,
"1488562200": 0.029692525252525,
"1488564000": 0.029692525252525,
"1488565800": 0.029692525252525,
"1488567600": 0.029692525252525,
"1488569400": 0.029692525252525,
"1488571200": 0.029692525252525,
"1488573000": 0.029692525252525,
"1488574800": 0.029692525252525,
"1488576600": 0.029692525252525,
"1488578400": 0.029692525252525,
"1488580200": 0.029692525252525,
"1488582000": 0.029692525252525,
"1488583800": 0.029692525252525,
"1488585600": 0.029692525252525,
"1488587400": 0.029692525252525,
"1488589200": 0.029692525252525,
"1488591000": 0.029692525252525,
"1488592800": 0.029692525252525,
"1488594600": 0.029692525252525,
"1488596400": 0.029692525252525,
"1488598200": 0.029692525252525,
"1488600000": 0.029692525252525,
"1488601800": 0.029692525252525,
"1488603600": 0.029692525252525,
"1488605400": 0.029692525252525,
"1488607200": 0.029692525252525,
"1488609000": 0.029692525252525,
"1488610800": 0.029692525252525,
"1488612600": 0.029692525252525,
"1488614400": 0.029692525252525,
"1488616200": 0.029692525252525,
"1488618000": 0.029692525252525,
"1488619800": 0.029692525252525,
"1488621600": 0.029692525252525,
"1488623400": 0.029692525252525,
"1488625200": 0.029692525252525,
"1488627000": 0.029692525252525,
"1488628800": 0.029692525252525,
"1488630600": 0.029692525252525,
"1488632400": 0.029692525252525,
"1488634200": 0.029692525252525,
"1488636000": 0.029692525252525,
"1488637800": 0.029692525252525,
"1488639600": 0.029692525252525,
"1488641400": 0.029692525252525,
"1488643200": 0.029692525252525,
"1488645000": 0.029692525252525,
"1488646800": 0.029692525252525,
"1488648600": 0.029692525252525,
"1488650400": 0.029692525252525,
"1488652200": 0.029692525252525,
"1488654000": 0.029692525252525,
"1488655800": 0.029692525252525,
"1488657600": 0.029692525252525,
"1488659400": 0.029692525252525,
"1488661200": 0.029692525252525,
"1488663000": 0.029692525252525,
"1488664800": 0.029692525252525,
"1488666600": 0.029692525252525,
"1488668400": 0.029692525252525,
"1488670200": 0.029692525252525,
"1488672000": 0.029692525252525,
"1488673800": 0.029692525252525,
"1488675600": 0.029692525252525,
"1488677400": 0.029692525252525,
"1488679200": 0.029692525252525,
"1488681000": 0.029692525252525,
"1488682800": 0.029692525252525,
"1488684600": 0.029692525252525,
"1488686400": 0.029692525252525,
"1488688200": 0.029692525252525,
"1488690000": 0.029692525252525,
"1488691800": 0.029692525252525,
"1488693600": 0.029692525252525,
"1488695400": 0.029692525252525,
"1488697200": 0.029692525252525,
"1488699000": 0.029692525252525,
"1488700800": 0.029692525252525,
"1488702600": 0.029692525252525,
"1488704400": 0.029692525252525,
"1488706200": 0.029692525252525,
"1488708000": 0.029692525252525,
"1488709800": 0.029692525252525,
"1488711600": 0.029692525252525,
"1488713400": 0.029692525252525,
"1488715200": 0.029692525252525,
"1488717000": 0.029692525252525,
"1488718800": 0.029692525252525,
"1488720600": 0.029692525252525,
"1488722400": 0.029692525252525,
"1488724200": 0.029692525252525,
"1488726000": 0.029692525252525,
"1488727800": 0.029692525252525,
"1488729600": 0.029692525252525,
"1488731400": 0.029692525252525,
"1488733200": 0.029692525252525,
"1488735000": 0.029692525252525,
"1488736800": 0.029692525252525,
"1488738600": 0.029692525252525,
"1488740400": 0.029692525252525,
"1488742200": 0.029692525252525,
"1488744000": 0.029692525252525,
"1488745800": 0.029692525252525,
"1488747600": 0.029692525252525,
"1488749400": 0.029692525252525,
"1488751200": 0.029692525252525,
"1488753000": 0.029692525252525,
"1488754800": 0.029692525252525,
"1488756600": 0.029692525252525,
"1488758400": 0.029692525252525,
"1488760200": 0.029692525252525,
"1488762000": 0.029692525252525,
"1488763800": 0.029692525252525,
"1488765600": 0.029692525252525,
"1488767400": 0.029692525252525,
"1488769200": 0.029692525252525,
"1488771000": 0.029692525252525,
"1488772800": 0.029692525252525,
"1488774600": 0.029692525252525,
"1488776400": 0.029692525252525,
"1488778200": 0.029692525252525,
"1488780000": 0.029692525252525,
"1488781800": 0.029692525252525,
"1488783600": 0.029692525252525,
"1488785400": 0.029692525252525,
"1488787200": 0.029692525252525,
"1488789000": 0.029692525252525,
"1488790800": 0.029692525252525,
"1488792600": 0.029692525252525,
"1488794400": 0.029692525252525,
"1488796200": 0.029692525252525,
"1488798000": 0.029692525252525,
"1488799800": 0.029692525252525,
"1488801600": 0.029692525252525,
"1488803400": 0.029692525252525,
"1488805200": 0.029692525252525,
"1488807000": 0.029692525252525,
"1488808800": 0.029692525252525,
"1488810600": 0.029692525252525,
"1488812400": 0.029692525252525,
"1488814200": 0.029692525252525,
"1488816000": 0.029692525252525,
"1488817800": 0.029692525252525,
"1488819600": 0.029692525252525,
"1488821400": 0.029692525252525,
"1488823200": 0.029692525252525,
"1488825000": 0.029692525252525,
"1488826800": 0.029692525252525,
"1488828600": 0.029692525252525,
"1488830400": 0.029692525252525,
"1488832200": 0.029692525252525,
"1488834000": 0.029692525252525,
"1488835800": 0.029692525252525,
"1488837600": 0.029692525252525,
"1488839400": 0.029692525252525,
"1488841200": 0.029692525252525,
"1488843000": 0.029692525252525,
"1488844800": 0.029692525252525,
"1488846600": 0.029692525252525,
"1488848400": 0.029692525252525,
"1488850200": 0.029692525252525,
"1488852000": 0.029692525252525,
"1488853800": 0.029692525252525,
"1488855600": 0.029692525252525,
"1488857400": 0.029692525252525,
"1488859200": 0.029692525252525,
"1488861000": 0.029692525252525,
"1488862800": 0.029692525252525,
"1488864600": 0.029692525252525,
"1488866400": 0.029692525252525,
"1488868200": 0.029692525252525,
"1488870000": 0.029692525252525,
"1488871800": 0.029692525252525,
"1488873600": 0.029692525252525,
"1488875400": 0.029692525252525,
"1488877200": 0.029692525252525,
"1488879000": 0.029692525252525,
"1488880800": 0.029692525252525,
"1488882600": 0.029692525252525,
"1488884400": 0.029692525252525,
"1488886200": 0.029692525252525,
"1488888000": 0.029692525252525,
"1488889800": 0.029692525252525,
"1488891600": 0.029692525252525,
"1488893400": 0.029692525252525,
"1488895200": 0.029692525252525,
"1488897000": 0.029692525252525,
"1488898800": 0.029692525252525,
"1488900600": 0.029692525252525,
"1488902400": 0.029692525252525,
"1488904200": 0.029692525252525,
"1488906000": 0.029692525252525,
"1488907800": 0.029692525252525,
"1488909600": 0.029692525252525,
"1488911400": 0.029692525252525,
"1488913200": 0.029692525252525,
"1488915000": 0.029692525252525,
"1488916800": 0.029692525252525,
"1488918600": 0.029692525252525,
"1488920400": 0.029692525252525,
"1488922200": 0.029692525252525,
"1488924000": 0.029692525252525,
"1488925800": 0.028199333333333,
"1488927600": 0.027797333333333,
"1488929400": 0.028796666666667,
"1488931200": 0.027705777777778,
"1488933000": 0.029260888888889,
"1488934800": 0.027898666666667,
"1488936600": 0.028567777777778,
"1488938400": 0.027966666666667,
"1488940200": 0.031491777777778,
"1488942000": 0.029932888888889,
"1488943800": 0.029602444444444,
"1488945600": 0.028367777777778,
"1488947400": 0.028203333333333,
"1488949200": 0.027365333333333,
"1488951000": 0.029268,
"1488952800": 0.027168888888889,
"1488954600": 0.02896,
"1488956400": 0.028440666666667,
"1488958200": 0.028768777777778,
"1488960000": 0.029303111111111,
"1488961800": 0.028202333333333,
"1488963600": 0.029497666666667,
"1488965400": 0.030699,
"1488967200": 0.029305111111111,
"1488969000": 0.027466888888889,
"1488970800": 0.030030666666667,
"1488972600": 0.028500888888889,
"1488974400": 0.030634222222222,
"1488976200": 0.027703777777778,
"1488978000": 0.027265555555556,
"1488979800": 0.030334666666667,
"1488981600": 0.027764888888889,
"1488983400": 0.030161222222222,
"1488985200": 0.029103333333333,
"1488987000": 0.028729444444444,
"1488988800": 0.027670888888889,
"1488990600": 0.030333777777778,
"1488992400": 0.029928777777778,
"1488994200": 0.028406111111111,
"1488996000": 0.030063333333333,
"1488997800": 0.02787,
"1488999600": 0.029999111111111,
"1489001400": 0.031957777777778,
"1489003200": 0.029450888888889,
"1489005000": 0.027597555555556,
"1489006800": 0.027634666666667,
"1489008600": 0.028026888888889,
"1489010400": 0.02867,
"1489012200": 0.028735555555556,
"1489014000": 0.029827111111111,
"1489015800": 0.028073555555556,
"1489017600": 0.028666222222222,
"1489019400": 0.027401111111111,
"1489021200": 0.028698222222222,
"1489023000": 0.028060666666667,
"1489024800": 0.030172777777778,
"1489026600": 0.030365777777778,
"1489028400": 0.030165777777778,
"1489030200": 0.028606555555556,
"1489032000": 0.030557777777778,
"1489033800": 0.033890444444444,
"1489035600": 0.030753555555556,
"1489037400": 0.046272,
"1489039200": 0.028306777777778,
"1489041000": 0.027800888888889,
"1489042800": 0.028866444444444,
"1489044600": 0.031033333333333,
"1489046400": 0.028864888888889,
"1489048200": 0.027869555555556,
"1489050000": 0.13476944444444,
"1489051800": 0.028914666666667,
"1489053600": 0.03133,
"1489055400": 0.028462888888889,
"1489057200": 0.028167555555556,
"1489059000": 0.028000888888889,
"1489060800": 0.028130888888889,
"1489062600": 0.028567333333333,
"1489064400": 0.029098,
"1489066200": 0.029865333333333,
"1489068000": 0.029339111111111,
"1489069800": 0.028029777777778,
"1489071600": 0.031127111111111,
"1489073400": 0.029674,
"1489075200": 0.029699333333333,
"1489077000": 0.031598888888889,
"1489078800": 0.029163777777778,
"1489080600": 0.028976,
"1489082400": 0.028831666666667,
"1489084200": 0.029003333333333,
"1489086000": 0.029332444444444,
"1489087800": 0.030934,
"1489089600": 0.027605444444444,
"1489091400": 0.028965222222222,
"1489093200": 0.027467,
"1489095000": 0.028435444444444,
"1489096800": 0.028267444444444,
"1489098600": 0.027433333333333,
"1489100400": 0.028199666666667,
"1489102200": 0.028302444444444,
"1489104000": 0.028000666666667,
"1489105800": 0.027800666666667,
"1489107600": 0.029362777777778,
"1489109400": 0.028475444444444,
"1489111200": 0.028032888888889,
"1489113000": 0.028065777777778,
"1489114800": 0.028405111111111,
"1489116600": 0.031557444444444,
"1489118400": 0.028400777777778,
"1489120200": 0.029508333333333,
"1489122000": 0.029735111111111,
"1489123800": 0.029331888888889,
"1489125600": 0.029399888888889,
"1489127400": 0.030501,
"1489129200": 0.028365222222222,
"1489131000": 0.028034777777778,
"1489132800": 0.028934666666667,
"1489134600": 0.028865777777778,
"1489136400": 0.028899444444444,
"1489138200": 0.029032666666667,
"1489140000": 0.029168888888889,
"1489141800": 0.027865777777778,
"1489143600": 0.030666666666667,
"1489145400": 0.027735555555556,
"1489147200": 0.028865111111111,
"1489149000": 0.029638333333333,
"1489150800": 0.032165666666667,
"1489152600": 0.028504777777778,
"1489154400": 0.029965222222222,
"1489156200": 0.027938111111111,
"1489158000": 0.028469,
"1489159800": 0.029865111111111,
"1489161600": 0.028036222222222,
"1489163400": 0.027766555555556,
"1489165200": 0.027832,
"1489167000": 0.028199333333333,
"1489168800": 0.029065111111111,
"1489170600": 0.028168777777778,
"1489172400": 0.028499333333333,
"1489174200": 0.028567888888889,
"1489176000": 0.031567333333333,
"1489177800": 0.028669555555556,
"1489179600": 0.028500444444444,
"1489181400": 0.027333777777778,
"1489183200": 0.026932555555556,
"1489185000": 0.028600777777778,
"1489186800": 0.029098555555556,
"1489188600": 0.028866555555556,
"1489190400": 0.029436222222222,
"1489192200": 0.030166444444444,
"1489194000": 0.029167111111111,
"1489195800": 0.028267,
"1489197600": 0.031937333333333,
"1489199400": 0.029733888888889,
"1489201200": 0.027932777777778,
"1489203000": 0.028400333333333,
"1489204800": 0.028600333333333,
"1489206600": 0.031499777777778,
"1489208400": 0.027567888888889,
"1489210200": 0.027666666666667,
"1489212000": 0.029467111111111,
"1489213800": 0.029867777777778,
"1489215600": 0.028265888888889,
"1489217400": 0.028666666666667,
"1489219200": 0.028699333333333,
"1489221000": 0.027797555555556,
"1489222800": 0.030151555555556,
"1489224600": 0.028869222222222,
"1489226400": 0.029366,
"1489228200": 0.029230333333333,
"1489230000": 0.029036222222222,
"1489231800": 0.027966777777778,
"1489233600": 0.028232444444444,
"1489235400": 0.030866555555556,
"1489237200": 0.028000444444444,
"1489239000": 0.028202111111111,
"1489240800": 0.029397777777778,
"1489242600": 0.029771222222222,
"1489244400": 0.029533666666667,
"1489246200": 0.029133666666667,
"1489248000": 0.030466444444444,
"1489249800": 0.029201666666667,
"1489251600": 0.027698222222222,
"1489253400": 0.028132888888889,
"1489255200": 0.029198444444444,
"1489257000": 0.029798777777778,
"1489258800": 0.028599555555556,
"1489260600": 0.036400111111111,
"1489262400": 0.029365444444444,
"1489264200": 0.030002666666667,
"1489266000": 0.029434666666667,
"1489267800": 0.028932777777778,
"1489269600": 0.029930444444444,
"1489271400": 0.030068777777778,
"1489273200": 0.029032888888889,
"1489275000": 0.029066333333333,
"1489276800": 0.028103111111111,
"1489278600": 0.028731333333333,
"1489280400": 0.029599222222222,
"1489282200": 0.030667666666667,
"1489284000": 0.028597222222222,
"1489285800": 0.028699555555556,
"1489287600": 0.029395888888889,
"1489289400": 0.028601777777778,
"1489291200": 0.028232888888889,
"1489293000": 0.027800444444444,
"1489294800": 0.028833111111111,
"1489296600": 0.028065777777778,
"1489298400": 0.028310222222222,
"1489300200": 0.028498888888889,
"1489302000": 0.030065333333333,
"1489303800": 0.060234555555556,
"1489305600": 0.029632888888889,
"1489307400": 0.027900333333333,
"1489309200": 0.028566777777778,
"1489311000": 0.029334,
"1489312800": 0.028301333333333,
"1489314600": 0.028969,
"1489316400": 0.027265666666667,
"1489318200": 0.031934222222222,
"1489320000": 0.029164333333333,
"1489321800": 0.029635111111111,
"1489323600": 0.032267,
"1489325400": 0.027837111111111,
"1489327200": 0.030265,
"1489329000": 0.028634666666667,
"1489330800": 0.029632555555556,
"1489332600": 0.029934222222222,
"1489334400": 0.02867,
"1489336200": 0.028730555555556,
"1489338000": 0.028867,
"1489339800": 0.029500222222222,
"1489341600": 0.038871777777778,
"1489343400": 0.036098222222222,
"1489345200": 0.029562444444444,
"1489347000": 0.030782888888889,
"1489348800": 0.031991444444444,
"1489350600": 0.031072888888889,
"1489352400": 0.028930333333333,
"1489354200": 0.029099222222222,
"1489356000": 0.029499777777778,
"1489357800": 0.028033555555556,
"1489359600": 0.029566333333333,
"1489361400": 0.028599666666667,
"1489363200": 0.029232444444444,
"1489365000": 0.037327333333333,
"1489366800": 0.028578,
"1489368600": 0.029467333333333,
"1489370400": 0.029463222222222,
"1489372200": 0.028234111111111,
"1489374000": 0.028800666666667,
"1489375800": 0.027333777777778,
"1489377600": 0.028101111111111,
"1489379400": 0.028501888888889,
"1489381200": 0.030030111111111,
"1489383000": 0.028635666666667,
"1489384800": 0.029068666666667,
"1489386600": 0.028464444444444,
"1489388400": 0.027135666666667,
"1489390200": 0.026500666666667,
"1489392000": 0.030327333333333,
"1489393800": 0.028903444444444,
"1489395600": 0.031364333333333,
"1489397400": 0.028077222222222,
"1489399200": 0.028868888888889,
"1489401000": 0.027903444444444,
"1489402800": 0.027863444444444,
"1489404600": 0.028868222222222,
"1489406400": 0.028195666666667,
"1489408200": 0.033533222222222,
"1489410000": 0.030565666666667,
"1489411800": 0.029096777777778,
"1489413600": 0.028002555555556,
"1489415400": 0.027699777777778,
"1489417200": 0.026467333333333,
"1489419000": 0.028995888888889,
"1489420800": 0.029692525252525
"predicted": {
"1489422600": 0.029306915797535,
"1489424400": 0.029306611583729,
"1489426200": 0.029306299640856,
"1489428000": 0.029305980781347,
"1489429800": 0.029305655735246,
"1489431600": 0.029305325157941,
"1489433400": 0.029304989637306,
"1489435200": 0.029304649700256,
"1489437000": 0.029304305818754,
"1489438800": 0.029303958415296,
"1489440600": 0.029303607867888,
"1489442400": 0.02930325451458,
"1489444200": 0.029302898657557,
"1489446000": 0.029302540566849,
"1489447800": 0.029302180483668,
"1489449600": 0.029301818623424,
"1489451400": 0.02930145517843,
"1489453200": 0.029301090320345,
"1489455000": 0.029300724202354,
"1489456800": 0.029300356961133,
"1489458600": 0.029299988718611,
"1489460400": 0.029299619583542,
"1489462200": 0.029299249652914,
"1489464000": 0.029298879013218,
"1489465800": 0.029298507741572,
"1489467600": 0.02929813590673,
"1489469400": 0.029297763569986,
"1489471200": 0.029297390785978,
"1489473000": 0.029297017603409,
"1489474800": 0.029296644065688,
"1489476600": 0.029296270211505,
"1489478400": 0.029295896075338,
"1489480200": 0.029295521687918,
"1489482000": 0.029295147076627,
"1489483800": 0.029294772265867,
"1489485600": 0.029294397277385,
"1489487400": 0.029294022130555,
"1489489200": 0.029293646842644,
"1489491000": 0.029293271429036,
"1489492800": 0.029292895903437,
"1489494600": 0.029292520278061,
"1489496400": 0.029292144563791,
"1489498200": 0.029291768770321,
"1489500000": 0.029291392906292,
"1489501800": 0.029291016979398,
"1489503600": 0.029290640996499,
"1489505400": 0.029290264963702,
"1489507200": 0.029289888886452,
"1489509000": 0.029289512769598,
"1489510800": 0.029289136617461,
"1489512600": 0.029288760433889,
"1489514400": 0.029288384222313,
"1489516200": 0.029288007985788,
"1489518000": 0.029287631727035,
"1489519800": 0.029287255448481,
"1489521600": 0.029286879152284,
"1489523400": 0.029286502840371,
"1489525200": 0.029286126514457,
"1489527000": 0.029285750176068,
"1489528800": 0.028549005604982,
"1489530600": 0.028350386018975,
"1489532400": 0.028842838225074,
"1489534200": 0.028304500047645,
"1489536000": 0.029071024435861,
"1489537800": 0.028398890865458,
"1489539600": 0.028728486742521,
"1489541400": 0.028431692903988,
"1489543200": 0.030169614737333,
"1489545000": 0.029400520614005,
"1489546800": 0.029237199238203,
"1489548600": 0.028628019010466,
"1489550400": 0.028546564630431,
"1489552200": 0.028132986823312,
"1489554000": 0.029070801467211,
"1489555800": 0.0280353973678,
"1489557600": 0.028918194322905,
"1489559400": 0.028661754967811,
"1489561200": 0.028823166588468,
"1489563000": 0.029086250409671,
"1489564800": 0.02854313803763,
"1489566600": 0.029181425579304,
"1489568400": 0.029773333345012,
"1489570200": 0.029085728685267,
"1489572000": 0.028179077107742,
"1489573800": 0.029442690026567,
"1489575600": 0.028688123382762,
"1489577400": 0.029739474677213,
"1489579200": 0.028294414472927,
"1489581000": 0.028078008136176,
"1489582800": 0.029590666933866,
"1489584600": 0.028323448089779,
"1489586400": 0.029504401970315,
"1489588200": 0.02898252267158,
"1489590000": 0.02879784001901,
"1489591800": 0.028275653443319,
"1489593600": 0.029587943317333,
"1489595400": 0.029387917377288,
"1489597200": 0.02863697720243,
"1489599000": 0.02945348418823,
"1489600800": 0.028371982533724,
"1489602600": 0.02942107264672,
"1489604400": 0.030386087792176,
"1489606200": 0.02915009207013,
"1489608000": 0.028236243350154,
"1489609800": 0.028254166784263,
"1489611600": 0.02844712049868,
"1489613400": 0.028763728603158,
"1489615200": 0.028795669391974,
"1489617000": 0.029333280662413,
"1489618800": 0.028468656947833,
"1489620600": 0.02876038765809,
"1489622400": 0.028136511503629,
"1489624200": 0.02877542396548,
"1489626000": 0.028460843228315,
"1489627800": 0.029501383251514,
"1489629600": 0.029596103978678,
"1489631400": 0.029497152504276,
"1489633200": 0.028728390412016,
"1489635000": 0.029689560411185,
"1489636800": 0.031331379444506,
"1489638600": 0.02978523939309,
"1489640400": 0.037430874045086,
"1489642200": 0.028578931809251,
"1489644000": 0.028329269342634,
"1489645800": 0.028853897372059,
"1489647600": 0.029921164881846,
"1489649400": 0.028852382516016,
"1489651200": 0.028361591739034,
"1489653000": 0.08101789294232,
"1489654800": 0.028876344836291,
"1489656600": 0.030065658562049,
"1489658400": 0.028652865572429,
"1489660200": 0.028506903007262,
"1489662000": 0.028424341149196,
"1489663800": 0.02848794459965,
"1489665600": 0.028702533095049,
"1489667400": 0.028963555414317,
"1489669200": 0.029341174502492,
"1489671000": 0.029081563217306,
"1489672800": 0.028436170623605,
"1489674600": 0.029961588018335,
"1489676400": 0.029245392477241,
"1489678200": 0.029257492958003,
"1489680000": 0.030192824672476,
"1489681800": 0.028992931755904,
"1489683600": 0.028900055255794,
"1489685400": 0.028828580728667,
"1489687200": 0.028912765378377,
"1489689000": 0.029074504411429,
"1489690800": 0.029863006873063,
"1489692600": 0.028223086086501,
"1489694400": 0.028892498580576,
"1489696200": 0.028154148982389,
"1489698000": 0.02863080387536,
"1489699800": 0.028547684195713,
"1489701600": 0.028136464297493,
"1489703400": 0.028513565048153,
"1489705200": 0.028563822358348,
"1489707000": 0.028414815077371,
"1489708800": 0.028315940953191,
"1489710600": 0.029084978095707,
"1489712400": 0.028647562674992,
"1489714200": 0.028429224025229,
"1489716000": 0.028445058056105,
"1489717800": 0.028611820986938,
"1489719600": 0.030163977590784,
"1489721400": 0.028608941823344,
"1489723200": 0.029154031597351,
"1489725000": 0.029265334991779,
"1489726800": 0.029066380388718,
"1489728600": 0.029099492200478,
"1489730400": 0.029641357477036,
"1489732200": 0.028589219805418,
"1489734000": 0.028426125588625,
"1489735800": 0.028868901931854,
"1489737600": 0.028834607328315,
"1489739400": 0.028850814774319,
"1489741200": 0.028916044786945,
"1489743000": 0.028982749806918,
"1489744800": 0.028340711947533,
"1489746600": 0.029719507940927,
"1489748400": 0.028275861064645,
"1489750200": 0.028831682412529,
"1489752000": 0.029212031364467,
"1489753800": 0.030456015695455,
"1489755600": 0.028653148152954,
"1489757400": 0.029371835387555,
"1489759200": 0.028373410311466,
"1489761000": 0.028634426369706,
"1489762800": 0.029321418683411,
"1489764600": 0.028420616360363,
"1489766400": 0.028287483146246,
"1489768200": 0.028319338913151,
"1489770000": 0.028499823803703,
"1489771800": 0.02892569800228,
"1489773600": 0.028484047229754,
"1489775400": 0.028646417605994,
"1489777200": 0.028679799430953,
"1489779000": 0.030156018021786,
"1489780800": 0.028729102267739,
"1489782600": 0.028645483396934,
"1489784400": 0.028070792415806,
"1489786200": 0.02787291617048,
"1489788000": 0.028693779514769,
"1489789800": 0.028938445777228,
"1489791600": 0.028823867382325,
"1489793400": 0.029103909357479,
"1489795200": 0.02946296722405,
"1489797000": 0.02897068449124,
"1489798800": 0.028527257285839,
"1489800600": 0.030333453363802,
"1489802400": 0.029248522920732,
"1489804200": 0.028361650499419,
"1489806000": 0.02859141220191,
"1489807800": 0.028689482092818,
"1489809600": 0.030116138801142,
"1489811400": 0.028180600529095,
"1489813200": 0.028228850254395,
"1489815000": 0.029114600642742,
"1489816800": 0.029311410810371,
"1489818600": 0.028522667990176,
"1489820400": 0.028719541656312,
"1489822200": 0.028735248834742,
"1489824000": 0.028291083282466,
"1489825800": 0.029449184568454,
"1489827600": 0.028817743676168,
"1489829400": 0.029061841473348,
"1489831200": 0.028994703713399,
"1489833000": 0.028898808330913,
"1489834800": 0.028372170607774,
"1489836600": 0.02850253770877,
"1489838400": 0.029798357616318,
"1489840200": 0.028387640688947,
"1489842000": 0.028486509637081,
"1489843800": 0.029074486348364,
"1489845600": 0.029257862362642,
"1489847400": 0.029140594121545,
"1489849200": 0.028943402698308,
"1489851000": 0.029598789724404,
"1489852800": 0.028976110987196,
"1489854600": 0.028236016221722,
"1489856400": 0.028449514498587,
"1489858200": 0.028973412563644,
"1489860000": 0.029268400904115,
"1489861800": 0.028678013286133,
"1489863600": 0.032515255399675,
"1489865400": 0.029054068210014,
"1489867200": 0.029367177614268,
"1489869000": 0.029087373458967,
"1489870800": 0.028840097255411,
"1489872600": 0.029330515130321,
"1489874400": 0.029398186795324,
"1489876200": 0.028888229891932,
"1489878000": 0.028904309003041,
"1489879800": 0.028430108053203,
"1489881600": 0.028738772177001,
"1489883400": 0.029165323939896,
"1489885200": 0.029690510481848,
"1489887000": 0.028671693069991,
"1489888800": 0.028721659576145,
"1489890600": 0.029063804761456,
"1489892400": 0.028672824123453,
"1489894200": 0.028491006299847,
"1489896000": 0.028277929155321,
"1489897800": 0.028785503380259,
"1489899600": 0.028407708119001,
"1489901400": 0.028527575764677,
"1489903200": 0.028620006031387,
"1489905000": 0.029390086380118,
"1489906800": 0.044225914627099,
"1489908600": 0.029176671034231,
"1489910400": 0.02832425079676,
"1489912200": 0.02865159785101,
"1489914000": 0.029028514941893,
"1489915800": 0.028520297382902,
"1489917600": 0.028848258462205,
"1489919400": 0.028010227588816,
"1489921200": 0.030305680832228,
"1489923000": 0.028943193818775,
"1489924800": 0.029174324181181,
"1489926600": 0.030468137693194,
"1489928400": 0.028289433290903,
"1489930200": 0.029482929708954,
"1489932000": 0.02868087642918,
"1489933800": 0.029171187165987,
"1489935600": 0.029319144166052,
"1489937400": 0.0286971378313,
"1489939200": 0.028726541203765,
"1489941000": 0.028793259834456,
"1489942800": 0.029104241403579,
"1489944600": 0.033711498629012,
"1489946400": 0.032347352685595,
"1489948200": 0.029133746238486,
"1489950000": 0.029733374847351,
"1489951800": 0.030327142913666,
"1489953600": 0.029875180865974,
"1489955400": 0.02882148666564,
"1489957200": 0.028904128395552,
"1489959000": 0.029100664450484,
"1489960800": 0.028379469221456,
"1489962600": 0.029132620267343,
"1489964400": 0.028657023515856,
"1489966200": 0.028967724573009,
"1489968000": 0.032946592758614,
"1489969800": 0.028645290493769,
"1489971600": 0.029082082104202,
"1489973400": 0.029079682985907,
"1489975200": 0.028475113534682,
"1489977000": 0.028753236895516,
"1489978800": 0.028031785787829,
"1489980600": 0.028408609041222,
"1489982400": 0.028605247344417,
"1489984200": 0.029356081896843,
"1489986000": 0.028670267767906,
"1489987800": 0.028882736456396,
"1489989600": 0.028585365317841,
"1489991400": 0.02793184700623,
"1489993200": 0.027619348194683,
"1489995000": 0.029499933697548,
"1489996800": 0.028799673080953,
"1489998600": 0.030008848932727,
"1490000400": 0.028392830104379,
"1490002200": 0.028781570283398,
"1490004000": 0.028306685699076,
"1490005800": 0.028286660869456,
"1490007600": 0.028780135750586,
"1490009400": 0.028449214440611,
"1490011200": 0.031072061703657,
"1490013000": 0.029613224057543,
"1490014800": 0.028890962521189,
"1490016600": 0.028352841074942,
"1490018400": 0.028203674547531,
"1490020200": 0.027597624714202,
"1490022000": 0.028839907334769,
"1490023800": 0.029181880113194,
"1490025600": 0.029181498204823
"name": "localhost_PING_rta"
Thanks.
Still no joy.
I have the enterprise version and what I would like is the export of CPU data collected for the last 2 weeks for all my hosts preferably from a report. It would be so time consuming to do this individually.
Please any assistance is appreciated.
Still no joy.
avandemore
The rrd files are usually located in /usr/local/nagios/share/perfdata/. You'd need to create a script that parses those files for the data you want, there is nothing Nagios that will natively do what you want.
Here is an example of plugins that may be of use to you:
https://exchange.nagios.org/directory/P ... on/details
https://exchange.nagios.org/directory/P ... rd/details
Previous Nagios employee