Hi
I faced with an issue, I have installed last version of Nagios XI and I use passive check for monitoring.
according to log (snmptt.log), I have received a fault trap at Thu Jun 6 15:05:03 and also recovery trap for it at Thu Jun 6 16:36:31, I am able to see the recovery in service status on Nagios, but when I try to see service history, there was not any log related to that time.
It should be noted, I recently upgraded Nagios XI to version 5.6.2 and offloaded MySQL to a remote server.
And I have another question, when I check a service in service status, the status information of that service is completed but when I check it in service history, the status information of that service is not completed.
I would be apprecitaed if you could help me to solve the cases.
problem with service history
npolovenko
- Support Tech
Re: problem with service history
Hello, @parisa. Did the service history log stop catching entries for services after you upgraded XI? Can you confirm whether other(active) services are producing State History log entries during state changes?
If that is the case please read the following KB article, and especially this part:
https://support.nagios.com/kb/article.php?id=77
Did the XI service status turn red(critical) for the SNMP checks at some point of time? Or was the status message "green" the whole time?I am able to see the recovery in service status on Nagios
HOLD ON!!! Even though the Status Information says USERS WARNING the Status column is still OkCould you clarify what you mean by "not completed"? Can you show this on a screenshot?But when I check it in service history, the status information of that service is not completed.
Hello, @npolovenko
Thanks for your reply, this problem has been solved.
I only had a problem, after upgrading Nagios and DB and offloading DB, in (Reports -> Available Reports -> State History), there was not many records, it seemed that a lot of records was not created in the section. (it should be note that old records was existed in the section)
I modified size of "output" field in table:nagios_statehistory and problem was solved, it seems Nagios delete state history records if output field is more than 256 characters.( I didn't have this problem before, there was the record but only showed 256 characters.
I use passive check (SNMP Trap)Can you confirm whether other(active) services are producing State History log entries during state changes?
I don't have any problem with my hosts and my services, I get trap based on my configuration, the state of my services are changed correctly.Did the XI service status turn red(critical) for the SNMP checks at some point of time? Or was the status message "green" the whole time?
Actually I don't know how the problem was existed, but I didn't have the problem until I upgraded Nagios and offloaded DB, also I upgraded DB from MariaDB 5 to MariaDB 10.3.13 (I think, this problem maybe was related to upgrading MariaDB), I'm not sure.Did the service history log stop catching entries for services after you upgraded XI?
Glad it is resolved.
This was likely because of the version of mysql/mariadb on the offloaded DB
See this article
https://support.nagios.com/kb/article/n ... s-780.html
See this article
npolovenko
- Support Tech
@parisa, Thanks for sharing your solution, I'll keep this in mind if I come across similar cases.
I'll be closing the thread as resolved.